I am doing a school architecture project. The house being built is completely net zero. We need to know how warm the water temperature is inside of the tubes needs to be to achieve a certain air temperature.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Start by calculating the heat load of the room(s), then divide the total heat load by the floor area. The floor surface will deliver about 2BTU per degree F above the average room temp. The water temp required depends on the floor coverings and the heat-transfer plate types. Most radiant floor product manufacturers will give nomographs of average water temp in the tubing vs. BTU/ft^2 at different flooring-R. (From the nomograph it looks like with R0.5 thin wood or bamboo finish floor the WarmBoard product delivers 10BTU per square foot with 80F average water temps, but with an R2.5 rug flooring it would take 100F average water temps to deliver the same heat rate.)

Net-Zero homes typically have such low heat loads that the expense of hydronic floor heating is silly, with very little in the way of comfort as well. Using mini-split heat pumps for heating and cooling is often the most cost-effective approach, and is within the annualized output of rooftop photovoltaic arrays if you design & build air-tight with sufficiently low U-factors.
 
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks