Thread: Newbie seeks advice on simple-looking leak

  1. #1

    Default Newbie seeks advice on simple-looking leak

    Found a leak under my bathroom sink. I think it is a simple one to fix, but would like some backup as I am a newbie at this.

    There was no moisture above the joint pictured (see below). You can see a water drop at the right hand side of a threaded section of pipe by a shutoff valve -- the handle is just out of the frame, but you can see the flexible supply line connection nut. Ignore the tilt of the picture -- it's the best I could do in a tight space.

    Anyway, it appears as though this is just a simple threaded joint. I removed the supply line and tried to tighten the (Brass Craft) valve onto the short stub of copper pipe, but I couldn't get it to budge. I was using a super short wrench, and I was kind of nervous to apply too much torque since I don't know what the h*ll I am doing -- it took several minutes for me just to figure out what kind of joint I was looking at. It seems as though I could just:

    - shut off the water supply to the house
    - open a hose spigot, which is lower than the joint in question
    - remove the supply line from the valve
    - remove the valve from the copper stub
    - clean the threads
    - apply a generous amount of pipe dope (maybe an insufficient amount was used originally?)
    - tighten the valve on again
    - close the valve
    - reattach supply line
    - close hose spigot
    - turn on water supply to the house
    - open up valve, try faucet & inspect the joint

    Is that right? what tools will I need? That is a super short stub of copper pipe to work with! Will I hurt the joint on the left where the copper stub goes into the 90-degree elbow when I do this?

    Any other advice is appreciated.

    Name:  leak.jpg
Views: 161
Size:  33.8 KB

  2. #2
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    Replace the galvanized nipple with brass. You have a galvanized nipple between a brass valve and a brass fitting.

    John

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,673

    Default

    That is NOT a "copper stub", it is steel nipple. Remove it and replace it with a brass one. I didn't realize there were so many steps to take in order to remove it. We just usually turn off the water, remove the valve, and replace it.
    Licensed residential and commercial plumber

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    For now, you could remove the line up to the faucet, and turn the valve another 1/2 turn onto the nipple. That might fix your leak.

  5. #5

    Default

    Quote Originally Posted by jimbo View Post
    For now, you could remove the line up to the faucet, and turn the valve another 1/2 turn onto the nipple. That might fix your leak.
    Oh, I didn't know if it's OK to just tighten it more or if it breaks the seal that the pipe dope is (supposed to be) making.

    And of course the other responders were right that it is galvanized steel and not copper -- I had forgotten that I put a magnet to the nipple to determine that, duh.

    Are brass nipples like that a standard thing I could just walk into a hardware store and buy? Are they generally about that length? Why should I use brass?

    Is a pipe wrench the right tool to use to tighten the nipple (and to hold it motionless when tightening the valve on it)?

    Seriously, guys, I appreciate any detail you can give (hence my "long list" of steps).

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,209
    Blog Entries
    1

    Default

    You can use pliers or pipe wrenches. I do almost everything with pliers. I get a kick out of movies that show plumbers with giant pipe wrenches working on small fittings. sometimes on the wrong side of the fixture, the side with no plumbing.

    Brass is permanent. Galvanized steel will close up over time with rust. And placing steel between copper and brass just speeds up that process.
    Years ago I asked a plumber why the shop used galvanized.
    "It's a bit cheaper. Don't worry about it, it's a guaranteed service call later on."
    That was almost forty years ago.
    Last edited by Terry; 12-11-2012 at 08:52 PM.

  7. #7
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by larryleveen View Post
    Are brass nipples like that a standard thing I could just walk into a hardware store and buy? Are they generally about that length?
    A "close nipple" is the shortest, and some will have flats for applying a wrench between the threaded ends. Wherever possible, it can be best to use a nipple you can tighten into one fitting before attaching the next rather than just putting all three together and tightening both connections from one end. And along with that, using a nipple with some "grip room" in the center can help make it possible to later remove that nipple without damaging its threads.
    Last edited by leejosepho; 12-11-2012 at 10:30 AM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  8. #8
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    That shutoff valve looks suspiciously thin where the female pipe threads are supposed to be. I wouldn't trust a valve like that not to split when tightened down.
    For sure, I would remove the valve, clean the threads thoroughly, and inspect closely.

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,673

    Default

    You do NOT tighten the nipple into the valve. You apply sealing compoud to both threads then screw it slightly into the elbow, then screw the valve onto the nipple, THEN tighten the valve which will also tighten the nipple into the elbow. Pipe wrench, adjustable "Crescent" wrench, or pliers, whichever you have the strength to use will do the tightening. The nipple you have is 1 1/2" long, also called a "shoulder nipple" and they will have a brass one the same length. Oh, I, and many if not most, plumbers would change the other one at the same time.
    Last edited by hj; 12-12-2012 at 02:30 PM.
    Licensed residential and commercial plumber

  10. #10
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    You do not really want any steel/iron in your supply lines. You may have used it because you were scared to try to solder things, but there are other choices that are essentially permanent, iron/steel is not. And, eventually when it starts to rust, you'll have rust streams in the sink or wherever that supply runs to.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #11

    Default

    Well, I took the stop off and cleaned the threads of the steel nipple and wrapped them with teflon tape. When I looked in the female threaded end of the stop I saw some debris, which I realized was the end of the nipple that had crumbled. I hadn't noticed when I was cleaning and taping -- or maybe it was "wishful non-seeing" it. I put the stop back on anyway, and the supply line, but it leaks still -- possibly slightly more now. Looks like I have to replace the nipple. Name:  photo-1.jpg
Views: 105
Size:  48.6 KB

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,673

    Default

    quote; Looks like I have to replace the nipple.

    That is what we told you to do from the start, but you may also have to replace the valve. I would NEVER remove one of those valves and then actually reuse it. That would usually be a waste of time.
    Licensed residential and commercial plumber

  13. #13
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    I just don't understand why people take the time to find and post a question on forums and then don't take the advice they spent the time looking for.

    John

  14. #14

    Default

    Whoa there, guys. Don't jump down my throat here -- there's no call to be rude.

    I was advised by someone in the thread that I could just try to tighten the fitting. I figured that removing the pipe dope and teflon taping would be important. Nobody ever advised that the valve should be replaced before HJ _just_ mentioned it -- what's the problem with reuse or a brass valve, BTW? I am genuinely curious.

    My slow exploratory work was to "get the lay of the land" with something I am completely unfamiliar with. The fact that I didn't _yet_ replace the nipple doesn't mean I am ignoring advice. Also, not everyone has a work schedule or transportation situation that allows them to hit a hardware store after work. I'd never criticize you for proceeding slowly on a repair related to my field of expertise. Please don't take my slow pace as disrespect, and please be kind and patient with others. Thanks to all who have provided help. I truly appreciate it.

  15. #15
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by larryleveen View Post
    Well, I took the stop off and cleaned the threads of the steel nipple and wrapped them with teflon tape ... but it leaks still -- possibly slightly more now. Looks like I have to replace the nipple.
    The brass one should do better, but there can be complications even there. Not all manufacturers use the same process for making all the parts, and I have had times when one brand of nipple and another brand of fitting just did not fit together well at all. Also, pipe dope and teflon tape are actually more for reduction of friction during assembly so the parts can mate well than for sealing...and the same principle appears in electrical and electronics work where wire nuts and solder merely maintain a solid mechanical connection. So, always only use plumbing parts that fit well, and then use something slippery while fitting them well!
    Last edited by leejosepho; 12-13-2012 at 02:05 PM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

Similar Threads

  1. Advice for Newbie
    By cycler in forum Boiler Forum
    Replies: 10
    Last Post: 10-13-2009, 07:56 PM
  2. Newbie: Simple Question on Shower Handles
    By don't_know_how in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 04-27-2009, 05:13 PM
  3. Well Newbie - Need some advice
    By ljvanbo in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 07-14-2007, 06:24 AM
  4. Plumbing newb seeks advice on rough-in
    By ktulu in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 09-06-2006, 06:16 AM
  5. Inspection Please - Novice seeks your expert advice
    By AMorey in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-27-2006, 02:07 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •