Is this done correctly? (Picture)

Users who are viewing this thread

PM5K

Member
Messages
151
Reaction score
0
Points
16
Location
San Antonio, TX
I'm just curious if the pressure relief valve can be run the way it's being run? I'm in TX if that helps, no idea what code we use here off hand :(

Just asking because I thought it had to be a rigid line.

4937.jpg
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
It would not pass inspection here because;
1. It is not rigid pipe
2. It has a "rise" between the valve and where it turns downward
3. It is NOT a full 3/4" i.d. as required by code.
4. If that is PVC pipe it is NOT permitted for "hot water" and if the valve ever discharged, the water would be beyond "hot", almost steaming, and if it is CPVC then it is also NOT full size i.d.
5. We cannot even use 3 /4" "flexible copper" connectors because the "ridges" reduce the i.d. to less than full size.
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
I think the simplest way to correct this is to use 2 pieces of 3/4" galvanized pipe and an elbow. Big Box stores have short lengths of pipe available, and exact lengths are not needed.
 