    I am adding a new bathroom on the second floor. Can I tap into the vent from the first floor bath in the attic so to save from putting another vent through the roof? The horozontal distance is about 15'. If so, can I do it with 1 1/2" pipe (ABS)?

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    You can tap your 2nd floor vent into that. You can NOT put any WASTE into that vent line from the first floor. Your second floor vents cannot be horizontal ( less than 45 degrees) until 42" above the floor, and must ALWAYS have some minimum continuous slope back towards the drain, to avoid bellies which would fill up with rain water

  3. #3
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    see if this helps, what size is the vent going thru the roof? 3"?
    Attached Images Attached Images  

  4. #4
    DIY Junior Member bwc's Avatar
    Join Date
    Dec 2012
    Location
    NB
    Posts
    2

    Default

    Thanks. That is helpfull

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    If you are running a new vent through the roof you will also want to look at your local code. Many places will not allow a vent smaller than 3 or 4" to penetrate the roof due to the possibility of frost closure during the winter.

  6. #6
    In the Trades SacCity's Avatar
    Join Date
    Mar 2011
    Location
    Sacramento, CA
    Posts
    189

    Default

    If you are going to have a toilet in the bathroom, min vent size is 2 inch
    Michael
    Sac City Plumbing
    http://SacCityPlumbing.com

  7. #7
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,939

    Default

    Quote Originally Posted by SacCity View Post
    If you are going to have a toilet in the bathroom, min vent size is 2 inch


    Only if he's under the UPC. Under IPC it can be 1-1/2 and it doesn't even have to be in the same location as the WC
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    quote; Under IPC it can be 1-1/2 and it doesn't even have to be in the same location as the WC

    THe IPC would probably allow it to be in the house next door, if that was the cheapest way to install it.
    Licensed residential and commercial plumber

Similar Threads

  1. no bath venting?
    By marciaggg in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 09-04-2011, 12:29 PM
  2. Need advice on venting 2nd floor bath
    By adthern in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-02-2010, 10:08 AM
  3. Bath exhaust fan venting
    By dabiz7 in forum Remodel Forum & Blog
    Replies: 16
    Last Post: 10-04-2009, 02:42 AM
  4. Q re venting basement bath
    By Soke in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 20
    Last Post: 04-26-2007, 03:54 PM
  5. venting my new attic bath
    By Don in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 12-28-2004, 05:50 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •