Thread: Proper way to drain/vent dual vanities?

  1. #1
    DIY Junior Member nola mike's Avatar
    Join Date
    Nov 2012
    Location
    Richmond, VA
    Posts
    29

    Default Proper way to drain/vent dual vanities?

    I'm putting in double sinks in my new bathroom. Original plan was to plumb the drains and supplies through the floor, but it seems like the correct way to do this is to stub out through the wall. So I'm planning on installing 2 drains that will drop through the sill plate, wye into 1 pipe and then join the main 3" stack. I was originally under the impression that they didn't need to be individually vented (as long as there was a vent within 10 feet of the drains). Doesn't look like that's the case though, and that these sinks need their own vents (please correct me and make my life easier if I'm wrong on this). I could put AAVs on them I guess, but it doesn't look like it will be THAT much harder to do it right. Right now, there is a 1 1/2" vent from my shower that terminates in my attic, and the main 2" cast vent that goes through the roof. I have to relocate the 1.5" vent anyway. Here are the questions:
    1) Can the 2 sinks share 1 vent line? I think the answer is "yes", but the horizontal run needs to be 6 inches above the spill line for the sink. If that's the case, I'll have to cut through a couple of more studs, but save drilling through the sole plate--it's also easier to make those connections in the bathroom than attic.
    2) Can I tie this new vent into the existing shower vent? Is 1.5" the correct size?
    3) Should I then route this through the roof or tie it in to my existing cast vent? I think it would probably be easier to route it through the roof, but I'm not sure.

    Anything I'm missing?

  2. #2
    In the Trades SacCity's Avatar
    Join Date
    Mar 2011
    Location
    Sacramento, CA
    Posts
    189

    Default

    Yes tie the vents together, 1-1/2 is fine, yes vents are required
    Michael
    Sac City Plumbing
    http://SacCityPlumbing.com

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    A vent should never end in an attic, always must go through the roof.

  4. #4
    DIY Junior Member nola mike's Avatar
    Join Date
    Nov 2012
    Location
    Richmond, VA
    Posts
    29

    Default

    Quote Originally Posted by Gary Swart View Post
    A vent should never end in an attic, always must go through the roof.
    Yeah, so the plan is to have all 3 of those vents tie together (2 will join in the bathroom from the sinks, and then that vent will join the original from the shower) and then have that one vent exit the roof.

  5. #5
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    heres a good setup on how to drain/vent dual sinks
    Attached Images Attached Images  

  6. #6
    DIY Junior Member 41Fever's Avatar
    Join Date
    Feb 2007
    Location
    North Dakota
    Posts
    23

    Default

    You should consider using a double fixture tee...not a cross. Less fittings needed and only have to penetrate sill plate once. You will be fine connecting to existing venting as long as you are 6"above flood rim of highest served fixture.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    4Tfever has the correct solution, as long as you use the back to back fixture fitting, (and NOT a cross, and NOT a doulbe combo), with a cleanout tee below it. Bring it up between the two sinks then use two 1 1/2" horizontal "arms" to run to the sink locations.
    Licensed residential and commercial plumber

  8. #8
    DIY Junior Member nola mike's Avatar
    Join Date
    Nov 2012
    Location
    Richmond, VA
    Posts
    29

    Default

    Quote Originally Posted by hj View Post
    4Tfever has the correct solution, as long as you use the back to back fixture fitting, (and NOT a cross, and NOT a doulbe combo), with a cleanout tee below it. Bring it up between the two sinks then use two 1 1/2" horizontal "arms" to run to the sink locations.
    So, is this what you're talking about?
    And this is the fixture fitting?

  9. #9
    DIY Junior Member 41Fever's Avatar
    Join Date
    Feb 2007
    Location
    North Dakota
    Posts
    23

    Default

    Yes and Yes.

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    #1. Yes, but add a cleanout unless the pipe drops directly into the main line.
    #2. Yes.
    Licensed residential and commercial plumber

  11. #11
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    Quote Originally Posted by nola mike View Post
    3) Should I then route this through the roof or tie it in to my existing cast vent? I think it would probably be easier to route it through the roof, but I'm not sure.

    Either will work, but I'm a fan of having the fewest possible roof penetrations (especially when one isn't reroofing soon or at the same time). Tying into cast stack in the roof might mean having to redo its roof pentration so it's perhaps half of one to 6 dozen of the other...or something like that.

  12. #12
    DIY Senior Member bluebinky's Avatar
    Join Date
    Aug 2011
    Location
    Santa Clara, CA
    Posts
    356

    Default

    I think you mean "six and a half of one and a dozen of the other".

  13. #13
    I&C Engineer (mostly WWTP) Lakee911's Avatar
    Join Date
    Aug 2005
    Location
    Columbus, OH
    Posts
    1,328

    Default

    Just maybe ... note the smiley! :P

Similar Threads

  1. Proper Loop Vent?
    By jalloken in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 19
    Last Post: 12-24-2011, 09:25 AM
  2. Proper drain and vent help needed
    By papisox in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 11-01-2010, 08:02 PM
  3. Proper Drain / vent setup for Dish Washer
    By jamiedolan in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 03-09-2009, 08:49 AM
  4. Bathroom Vanities?
    By palbarian in forum Remodel Forum & Blog
    Replies: 5
    Last Post: 06-08-2006, 05:49 PM
  5. Proper Shower Drain & Vent Design?
    By jpb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-23-2006, 02:52 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •