Thread: Review Shower DWV Diagram Please - ready to install

  1. #1
    DIY Junior Member rafigso's Avatar
    Join Date
    Sep 2012
    Location
    Greensboro, NC
    Posts
    8

    Default Review Shower DWV Diagram Please - ready to install

    Good Evening,

    Thanks in advance!!

    I'd like to know if what I represented would work, here are some notes:

    1. ABS is 2"
    2. I'm going to remove the old P-trap from the vent and cap it in order to reutilize the vent for the new shower
    3. Can I utilize a 90 degree turn in the waste run from the p trap before the vent, did I say that correctly?
    4. Where the waste pipe meets the vent, do I need to use a T or a Y or does it matter?
    5. In order to get the slope I need, it seems to me that the pipe gets cemented in at a slight angle, is that correct?
    6. When installing the P-trap, does it rest on the drywall from the downstairs ceiling or is it slightly raised, not sure at what depth to seat the P-trap in relation to the joist and subfloor.
    7. What's best practice when installing the drain, do I cement a piece of pipe prior to subfloor install and cut after subfloor goes down or do I cement in drain pipe after subfloor.

    Here is a picture:

    Name:  showerDWVRoughIn.jpg
Views: 382
Size:  52.5 KB

    Thanks,
    Rafael

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    1. ABS is 2"
    2. I'm going to remove the old P-trap from the vent and cap it in order to reutilize the vent for the new shower
    3. Can I utilize a 90 degree turn in the waste run.

    You can have 135 degrees of change after the vent.

    4. Where the waste pipe meets the vent, do I need to use a T or a Y or does it matter?

    Most codes like a wye fitting in case someone tries to wet vent later on.

    5. In order to get the slope I need, it seems to me that the pipe gets cemented in at a slight angle, is that correct?

    Fittings are made with that angle built in. 2%

    6. When installing the P-trap, does it rest on the drywall from the downstairs ceiling or is it slightly raised, not sure at what depth to seat the P-trap in relation to the joist and subfloor.

    Once you have set the p-trap height, it drains down at a 2% slope toward the vent. No..........You can't monkey around with fittings and change that!

    7. What's best practice when installing the drain, do I cement a piece of pipe prior to subfloor install and cut after subfloor goes down or do I cement in drain pipe after subfloor.

    That depends on what you are using for a shower pan.

  3. #3
    DIY Junior Member rafigso's Avatar
    Join Date
    Sep 2012
    Location
    Greensboro, NC
    Posts
    8

    Default

    I have some follow up questions and have color coded them Green, thanks for the quick reply.
    Quote Originally Posted by Terry View Post
    1. ABS is 2"
    2. I'm going to remove the old P-trap from the vent and cap it in order to reutilize the vent for the new shower
    3. Can I utilize a 90 degree turn in the waste run.

    You can have 135 degrees of change after the vent.

    So is the 90 in the diagram before the vent allowed?

    4. Where the waste pipe meets the vent, do I need to use a T or a Y or does it matter?

    Most codes like a wye fitting in case someone tries to wet vent later on.

    5. In order to get the slope I need, it seems to me that the pipe gets cemented in at a slight angle, is that correct?

    Fittings are made with that angle built in. 2%

    6. When installing the P-trap, does it rest on the drywall from the downstairs ceiling or is it slightly raised, not sure at what depth to seat the P-trap in relation to the joist and subfloor.

    Once you have set the p-trap height, it drains down at a 2% slope toward the vent. No..........You can't monkey around with fittings and change that!


    Do I set the P-trap off the celing or rest it on the ceiling?
    7. What's best practice when installing the drain, do I cement a piece of pipe prior to subfloor install and cut after subfloor goes down or do I cement in drain pipe after subfloor.

    That depends on what you are using for a shower pan.
    I'm thinking of using pro-slope and then mud

Similar Threads

  1. Vent and Waste Diagram Review
    By rafigso in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 10-29-2012, 02:49 PM
  2. Need review of a rough plumbing diagram
    By ClevelandGuy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 07-16-2012, 07:16 AM
  3. Ready to install new bathtub - confused on a couple items.
    By zubz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 05-26-2010, 06:15 AM
  4. Getting ready to install new tub-questions
    By BJ James in forum Shower & bathtub Forum & Blog
    Replies: 6
    Last Post: 02-22-2010, 09:17 AM
  5. Ready to install flange but have question...
    By Geo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 09-10-2007, 07:24 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •