    Exclamation Sewage and drainage lines planning

    Dear Sir,

    I need to install drainage line and sewage line for my 2 story home Ground floor and first floor. Ground floor has 4 bathrooms and one kitchen and the same in first floor. One Bath in the East, 3 baths in the south at the back side and kitchen in the West side.
    The line rout is 65 feet from North to south, turn to West and run 50 feet and the turn to North and run is 100 feet. the total
    length of each line is 215 feet. All pipe will run around the building. Kindly let me know the size I am thinking for 6 inches diameter.
    Also I need to know slope for each length. Do I need to make access point on the 100 feet side.

    With best regards,
    Shafeeq

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    That is a very large "U" shaped sewer system and usually there would be a more direct route. You do need cleanouts at 100' maximum, 75' is better, but since you also need them at each turn, that will take care of the 100' section. 6" is too large.
    Licensed residential and commercial plumber

  3. #3
    DIY Junior Member Shafeeq A Chaduhary's Avatar
    Join Date
    Nov 2012
    Location
    Islamabad
    Posts
    2

    Default

    Quote Originally Posted by hj View Post
    That is a very large "U" shaped sewer system and usually there would be a more direct route. You do need cleanouts at 100' maximum, 75' is better, but since you also need them at each turn, that will take care of the 100' section. 6" is too large.
    Hi HJ
    Thank you for your suggestions. If 6 inch dia. is too large what size you recommend. Please also give me slope for sewage and slope for drainage line.
    With best regards,
    Shafeeq

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    4" is large enough for 4 bathrooms. You need 1/4" per foot slope, which means your line needs to drop 4 1/2 feet over the length.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    4" can be installed with 1/8" slope so the minimum distance needed would be 26" for that distance. The actual amount you use can be anything over that depending on the parameters of your installation.
    Licensed residential and commercial plumber

Similar Threads

  1. PEX layout & planning
    By DavidTu in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 01-07-2011, 12:20 PM
  2. Planning new work
    By Jeff Haines in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 05-05-2009, 04:04 PM
  3. Geothermal/well planning
    By David G in forum Pumps and Tanks Well Forum & Blog
    Replies: 7
    Last Post: 11-05-2008, 06:19 AM
  4. DVW planning question
    By almostdone in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 06-28-2006, 10:11 PM
  5. Planning an addition
    By Lakee911 in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 12-01-2005, 05:09 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •