    Question Can I replace 120V Element with 240 to achieve half power?

    I am to install a point of use, 13 gallon Whirlpool electric hot water heater. The hot water heater claims to use up to 1750W, using a 1600W, 120V element. Is there any consiquence to replacting 120V element with a 240V element. From my understanding, it seems these are just resistive elements, and power/current should behave accurding to ohm law (V=IR, P=VI=V^2*R). Of course warm-up times will be doubled (or perhaps even x4).

    Thanks for any insight.

  2. #2
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,644

    Default

    Sounds like you have it correct.

    Recover time will be very slow, But the element will never burn open until it gets corroded from the outside in.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  3. #3
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    The power will be 1/4 with 1/2 the voltage. So, a 1600 W, 240v element would become a 400W element at 120v. Depending what elements will fit, you could go to a higher wattage 240v element to still have a decent recovery at 120v.

    What is the reason for going to a 240v element? Are you trying to tie the water heater to an existing kitchen (assuming this is going in the kitchen) circuit? If so, the problem is that maybe a future buyer could stick the 120v element back in and would overload that circuit. Best to run a dedicated line for it.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    IF you want slower hot water recovery, or less power draw, they do make 1000 and 1200 watt 120 elements, ( in fact, I have seen 850 watt ones but they are hard to find).
    Licensed residential and commercial plumber

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    FWIW, the power to heat the water will be the same, regardless of what element you use assuming the thermostat stays the same. It's just that the higher wattage stuff will get there faster. With an electric WH, there isn't a huge standby loss, so most of the energy is used to heat it in the first place, not reheat it after a long time of disuse.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    DIY Junior Member grimdestripador's Avatar
    Join Date
    Nov 2012
    Location
    Alaska
    Posts
    2

    Default

    For those concerned. I am not intending to use this as a perminante installation, but rather a semi-portable hotwater + generator combo. I have a 55 gallon rain barrel, with a RV type- pressure regulating pump (120V). I'm not concerend about recovery time and more concerened about power requirements (of generator vs 10guage extension cord).

    I see that home depot has replacement elements in stock for reasonable prices. I have been unable to find a supplier for these rare 750-1000w, 120V elements, but have been able to find lots of 240V elements for near $10. When I look at the elements, I can make guesses why they don't advertise a 1000W, 120V element as a capable 4000W, 240 element. But why can't a 240V, 3200W element run at half voltage to achieve quarter power.

    Resistance of a 3200W, 240V; P = V^2*R; R = P/V^2 = 3200/240^2 = 3200/57600 = 0.055555 [ohms]
    Resistance of a 1600W,120V; P = V^2*R; R = P/V^2 = 1600/120^2 = 1600/14400 = 0.11111111 [ohms]

    Power of a 3200W, 240V element running at 120V: Power = V^2 * R = 120^2*0.055555 = 800 watts (PERFECT).

    Other thoughts I've had, include... (1) using a power diode to rectify the wave. (2) using an variac (variable transformer). (3) using a stove top resister dial. But these seems risky because I don't know if the thermostat circuit requires exactally 120V or can run at arbitary values.
    Last edited by grimdestripador; 11-16-2012 at 01:57 PM.

  7. #7
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,644

    Default

    Quote Originally Posted by grimdestripador View Post
    Other thoughts I've had, include... (1) using a power diode to rectify the wave. (2) using an variac (variable transformer). (3) using a stove top resister dial. But these seems risky because I don't know if the thermostat circuit requires exactally 120V or can run at arbitary values.

    I would be careful using a diode. It would work but the thermostat may fail.

    Sometimes the DC can cause the thermostat to stick ON. They are normally AC rated.

    If you use a variac then you would have even more loss, but the thermostat should not care if it is switching less AC power.

    Propane or solar may be more cost affective for heating water in the sticks.

    Please post the outcome and let us know how you make it work.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. VERY odd problem... HALF a power outage??
    By TangoBravo in forum Electrical Forum discussion & Blog
    Replies: 19
    Last Post: 12-27-2012, 01:04 PM
  2. Thermostats : Dual Element in a Single Element Water Heater
    By Synicasm in forum Water Heater Forum, Tanks
    Replies: 4
    Last Post: 11-09-2009, 01:35 PM
  3. Lower Power element for small GE water heater?
    By sedin26 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 06-02-2008, 09:12 PM
  4. Replace heating element AO Smith ProMax
    By john_k9jgs in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 02-03-2005, 07:43 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •