    Default Double / Triple Security Measures running Gas Outdoors

    Maybe I'm overthinking this, but short of a shutoff valve indoors, what other security measures should I take into account if I was to have a gas pipe leadoff on the exterior of my home ?


    After Sandy, I plan to have natural gas as a fuel source for the generator.
    My neighbor has this for this grill already.

    I'm the latter and the thought of a *gas source* accessible is quite a thing.
    On the exterior, I am thiking a short stub with a ball valved (keyed/hole for padlock type) and then the quick disconnect right off that fitting.

    Any other safety precautions on the whole gasoline - exterior to be keen on

  2. #2
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Quote Originally Posted by chefwong View Post
    Maybe I'm overthinking this, but short of a shutoff valve indoors, what other security measures should I take into account if I was to have a gas pipe leadoff on the exterior of my home ?


    After Sandy, I plan to have natural gas as a fuel source for the generator.
    My neighbor has this for this grill already.

    I'm the latter and the thought of a *gas source* accessible is quite a thing.
    On the exterior, I am thiking a short stub with a ball valved (keyed/hole for padlock type) and then the quick disconnect right off that fitting.

    Any other safety precautions on the whole gasoline - exterior to be keen on

    The Gas feed connection for the generator should come off of the gas meter, and not from inside the house.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  3. #3
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    The Gas Meter is actually inside my house.
    The boiler room is my basement. That has a 1" or so + pipe there. That is where I was planning to have the plumber tap and then extend out.

  4. #4
    DIY Senior Member wjcandee's Avatar
    Join Date
    Apr 2012
    Location
    New York, NY
    Posts
    1,587

    Default

    Our generator just sits on a pad in a spot in the back that meets the requirements of the various applicable codes and the gas line to it and quarter-turn shutoff are right there next to the generator. It's all exposed and I suppose anyone could come by and tamper with it. But that's how most locations are. Drive behind any shopping center and the gas piping is all right there, sometimes with taps installed so that a trailer-mounted generator can be towed up and attached. (A lot of Walgreens and CVS Pharmacies appear to be designed to be trailer-generator-ready. That's why so many Walgreens and CVS Pharmacies were open right after the hurricane on Long Island blacked out the whole area. Near us, for days upon days, you would drive up the pitch-black main street with no streetlights or traffic lights working, past pitch-black shopping centers, and then you would come upon a Walgreens in the middle of this nothingness lit up bright as day, with everything working inside, as if nothing had happened. Good pharmacy chains take disaster recovery seriously, because people need their medicines. And then they also become suppliers of essentials, like this one did, with cold milk and frozen items readily-available, because they had brought a trailer generator of sufficient size to power the store at its normal electrical service level.)

    A friend of mine owns a hardware store. He has a 12kw Onan generator outside his store. He has built around it and the gas piping a very-attractive black wrought-iron cage, anchored into the concrete, that is locked and can be opened. It deters any tampering while still looking nice and not interfering with the operation of the generator, as there is probably 12" or more distance between the generator enclosure itself and this wrought-iron cage.

    I'm thinking that you may be required by code to have more fittings than you imagine at the generator location. There is a way to do it right and I'm not sure that you want to be reinventing the wheel on this. For example, most generators run a thick, flexible, not-quick-disconnect hose from the galvanized piping gas line to the generator, to absorb vibration, but it's a "permanent" hose (until you replace it, of course).
    Last edited by wjcandee; 11-14-2012 at 05:35 PM.

  5. #5
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Chef Wong, you have been around this forum for a long time. Surely you have noted that dealing with gas piping and related gas work is not something a DIY should be doing. Screw up a water line or drain and you have a problem, but screw up a gas installation and you could end up with a very large BOOM. My advice is hire a plumber licensed for gas work.

    He mentioned in his post that a plumber was doing the work
    Terry
    Last edited by Terry; 11-14-2012 at 06:05 PM.

  6. #6
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    It's not the fittings I'm worried about.
    I'm just not a fan of having a easily combustible source - accessible- .
    Even knowing I can control it with a shutoff inside, it's still not comfortable enough for my comfort factor.

    I dunno. Maybe I'm thinking-reading into this way too much to say Yes to the thought of it.

  7. #7
    DIY Senior Member bluebinky's Avatar
    Join Date
    Aug 2011
    Location
    Santa Clara, CA
    Posts
    354

    Default

    You might think about one of those square keyed fireplace-style shut-offs. At least then, someone would actually have to work at turning on the gas. If you are really paranoid, put the valve behind a small locked hasp or something.

    I would not bury the quick disconnect...

  8. #8
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    Why not just cap the line until your ready to hookup the generator.

    John

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    THere are some special flow detection shutoff valves for gas that close the line should it be broken or someone takes the hose off - it detects the high flow and shuts the gas flow off. No idea how well they work or if they might have nuisance shutoffs, but it might be something to look into.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Have a shutoff inside the house and then one outside....put a locking shutoff on the outside if you are worried. WHat is the issue? Are you concerned that someone will try stealing the natural gas or that someone may turn the valve on and the the gas flow without you knowing??
    Attached Images Attached Images  

  11. #11
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    People do crazy things. And I'm concerned about things going BOOM on someone trying to steal it....
    Whether it be during a circumstance like Sandy or just everyday normal looting/theft. Stuff happens.
    I don't need no idiot trying to fumble and attempt a theft, and me have a unsuspecting leak due to it, etc, etc.

    A perfect example would be my car. I had my track rat torn up to pieces as I was working on it so I had the other bay littered with parts.
    Park the daily driver on the street. Lo and behold, a couple days later, I noticed the trim below my headlight was looking a little *tweaked*. Inspect closer and I see scratches. I wash my cars religiously so I know every inch of things. Someone had attempted to steal my headlights.

    So yes, in a perfect world, no on would tamper with it. Just short of me building this hideous *steel/iron* box to house it.....just looking for ideas on how to at least put some measures in place.

  12. #12
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    Quote Originally Posted by chefwong View Post
    People do crazy things. And I'm concerned about things going BOOM on someone trying to steal it....
    Whether it be during a circumstance like Sandy or just everyday normal looting/theft. Stuff happens.
    I don't need no idiot trying to fumble and attempt a theft, and me have a unsuspecting leak due to it, etc, etc.

    A perfect example would be my car. I had my track rat torn up to pieces as I was working on it so I had the other bay littered with parts.
    Park the daily driver on the street. Lo and behold, a couple days later, I noticed the trim below my headlight was looking a little *tweaked*. Inspect closer and I see scratches. I wash my cars religiously so I know every inch of things. Someone had attempted to steal my headlights.

    So yes, in a perfect world, no on would tamper with it. Just short of me building this hideous *steel/iron* box to house it.....just looking for ideas on how to at least put some measures in place.
    Place a shutoff valve in the house and leave the valve closed unless you need the generator...this way if someone tampers with the outside pieces, at least no gas will be flowing. I dont know if you are more concerned with someone stealing the generator or the consequences of free flowing gas if someone steals the generator. If it is the later, the shut valve on the inside of the house will remedy that.

    As far as someone stealing the generator, if someone really wants it, they will get it.

  13. #13
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    Quote Originally Posted by jadnashua View Post
    THere are some special flow detection shutoff valves for gas that close the line should it be broken or someone takes the hose off - it detects the high flow and shuts the gas flow off. No idea how well they work or if they might have nuisance shutoffs, but it might be something to look into.
    Yeah, that was on my radar as well. I actually recall looking at one f those when we did my kitchen. Can't recall if the feedback was that it was more of a nuiscance than not.

  14. #14
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    Why are we making such a big deal out of this? Put your valve in and plug it. No matter what you do it would take just a pair of wrenches to steal it. Do you also lock you outside outlets and hose bib?

    John

  15. #15
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,625

    Default

    If someone wants to blow up your house, there is no way to prevent it unless you weld the pipes and valves together. A quick connect has an automatic valve inside of it, so even if the valve is turned on, gas will not leak out unless someone has the mating piece for it and pushes it into the connector. THis is a "gas" gas, not gasoline, so they cannot put into a gas can and "steal" it, unless they have a compressor to convert it into liquified natural gas, and if they can afford that, they don't have to steal your gas.
    Last edited by hj; 11-15-2012 at 06:55 AM.
    Licensed residential and commercial plumber

Similar Threads

  1. Sewer ejector basin outdoors - how far from house?
    By Seattle in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 07-11-2011, 05:38 AM
  2. Adding an outlet outdoors
    By Bubba25 in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 12-13-2009, 12:26 PM
  3. ceiling fan blades for outdoors
    By Lee Tanner in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 02-26-2009, 04:56 PM
  4. Grundfos CU 301 installed outdoors w/ no cover.
    By Singlecoil in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 10-22-2008, 11:57 AM
  5. HVLP Paint Sprayers - outdoors
    By rdtompki in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 12-11-2007, 09:28 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •