    Default Jet pump pressure

    I just replaced my 1/2hp jet pump with a1/2hp new pump, and the expansion/pressure tank (25gal) with similar size. I am drawing water, but only enough to run a single faucet and not enough to reach the second floor or power the first floor shower. The switch is set 20-40 as factory settings and the pressure tank is 25lbs. To increase my pressure is it simply increasing the switch settings to 40/60? That's where the trigger points were on the previous pump. My gauge is currently reading 25lbs.
    Thanks for your help

    Sam

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Yes all you need to do is increase the pressure switch setting. That is as long as your new pump can build that much pressure. You don't want to get close to the "max" pressure that pump can build.( check the pump specs) Depending on which 1/2 HP you have, the max pressure might only be 60 PSI. Which means you don't want to set the pump to shut off any higher than about 55 PSI.

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,679

    Default

    You will also have to increase the air precharge on the tank.

  4. #4
    DIY Junior Member Sam Downing's Avatar
    Join Date
    Nov 2012
    Location
    Maine
    Posts
    2

    Default

    Quote Originally Posted by valveman View Post
    Yes all you need to do is increase the pressure switch setting. That is as long as your new pump can build that much pressure. You don't want to get close to the "max" pressure that pump can build.( check the pump specs) Depending on which 1/2 HP you have, the max pressure might only be 60 PSI. Which means you don't want to set the pump to shut off any higher than about 55 PSI.
    I called the vet for a house call in the morning.
    I'll enjoy a cold beer with my feet up til then.

Similar Threads

  1. Low pressure, pump stays on - tank, pressure switch? Replace all?
    By applebach in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 04-17-2011, 04:51 AM
  2. I think pressure switch is not receiving pressure from pump.
    By jeremytl in forum Pumps and Tanks Well Forum & Blog
    Replies: 16
    Last Post: 04-04-2011, 06:26 AM
  3. 2 Houses, 2 Pressure Tanks, 1 pump, 1 controller, 1 pressure switch pro help needed!
    By betaman in forum Pumps and Tanks Well Forum & Blog
    Replies: 12
    Last Post: 05-05-2008, 05:07 AM
  4. Water in well, pump working, can't build up pressure, but doesn't lose pressure????
    By bgnotaplumber in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 08-20-2007, 10:32 AM
  5. ***Help***Pressure tank/pressure switch/pump
    By s4orce in forum Pumps and Tanks Well Forum & Blog
    Replies: 11
    Last Post: 02-28-2007, 02:11 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •