    Default Toilet vent

    I have a toilet in the corner of the house, the vent is in the exterior wall and runs up to the attic area. Is it possible to attatch the vent after the combination why/tee turns horizontal? This would be at the top of the 3" horizontal pipe and vent up into the exterior wall. Or should I try to lower the height of the the horizontal pipe and try to vent it out the side of the vertical just below the toilet flange?

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,209
    Blog Entries
    1

    Default

    The vent can be within six feet of the floor flange on a toilet.
    Either at the same level as the trap arm, or lower with a wye fitting on the vertical.

    Since a toilet bowl is refilled after the flush, and the bowl is the trap, it's treated a little differently from the rest of the plumbing fixtures.

  3. #3
    DIY Junior Member KShirriff's Avatar
    Join Date
    Nov 2012
    Location
    Tuscaloosa, Al.
    Posts
    14

    Default

    Thanks Terry.

Similar Threads

  1. Connecting New PVC Pipe Vent to Existing Cast Iron Vent Pipe in a Wall for Toilet
    By DanMcD in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 21
    Last Post: 10-16-2012, 10:40 AM
  2. Can you tie lav drain into a toilet vent (wet vent)? W/SKETCH
    By kmuddzy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 01-27-2012, 10:15 AM
  3. New bathroom, new toilet, water in bowl dissapears - bad toilet or vent problem?
    By not in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 06-13-2011, 10:38 AM
  4. Can I install toilet vent in vertical section of pipe below toilet?
    By dayster in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 06-28-2008, 10:36 AM
  5. Inspector says: “The toilet-vent must be upstream of the toilet.”
    By lahabra in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 16
    Last Post: 02-13-2008, 04:26 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •