The boiler I'm working on has the circulator on the outlet of the boiler, essentially pushing the water through the heaters rather than pulling it.
Is this ever legit?

I've never seen it this way, but don't know why not.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
It's totally legit (preferred, in fact), so long as the expansion tank & air scoop is between the boiler and the pump.

0909pm-Sieg-fig1-lg.jpg


Books have been written advocating that system architecture. It's nicer to the pump, and allows the air scoop to purge air somewhat better than some other configurations.

On some low mass boilers (particularly those with higher head) it's sometimes better to pump toward the boiler making it the high-pressure point on the system to reduce flash-boil sizzle to not lose heat-transfer efficiency.

More here.
 
Last edited:

ShockHazard

New Member
Messages
50
Reaction score
0
Points
0
Location
North East Pennsylvania
Curious.
Almost every one I've ever worked on had it as the very last thing in the line.
I always assumed is was so in case of a break, it would suck in air rather than pump out water and run the boiler dry.

Unfortunately, this one is before the expansion tank, so I suppose I'll be moving it.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
All boilers today have low pressure cutouts that shut them down with an uncompensated leak. A circulator run dry will fail fairly quickly, at least most of them use the water to lubricate their bearings. Having the expansion tank before the pump helps to ensure the pump stays full of water and not create microbubbles or water flashing to steam.
 

BadgerBoilerMN

Hydronic Heating Designer
Messages
485
Reaction score
10
Points
18
Location
Minneapolis
Website
www.badgerboilerservice.com
Nice drawing Dana! All low-mass boilers, including electric boilers, should be pumped-to for the reasons mentioned. It is the position of the expansion tank and air-eliminator that is most important, most properly, always on the low pressure side of the pump. This maintained the point of no pressure change.
 