    Default Circulator pump location

    The boiler I'm working on has the circulator on the outlet of the boiler, essentially pushing the water through the heaters rather than pulling it.
    Is this ever legit?

    I've never seen it this way, but don't know why not.

  2. #2
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    It's totally legit (preferred, in fact), so long as the expansion tank & air scoop is between the boiler and the pump.



    Books have been written advocating that system architecture. It's nicer to the pump, and allows the air scoop to purge air somewhat better than some other configurations.

    On some low mass boilers (particularly those with higher head) it's sometimes better to pump toward the boiler making it the high-pressure point on the system to reduce flash-boil sizzle to not lose heat-transfer efficiency.

    More here.
    Last edited by Dana; 11-02-2012 at 03:22 PM.

  3. #3
    In the Trades dwindle's Avatar
    Join Date
    Nov 2012
    Location
    North East Pennsylvania
    Posts
    49

    Default

    Curious.
    Almost every one I've ever worked on had it as the very last thing in the line.
    I always assumed is was so in case of a break, it would suck in air rather than pump out water and run the boiler dry.

    Unfortunately, this one is before the expansion tank, so I suppose I'll be moving it.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    All boilers today have low pressure cutouts that shut them down with an uncompensated leak. A circulator run dry will fail fairly quickly, at least most of them use the water to lubricate their bearings. Having the expansion tank before the pump helps to ensure the pump stays full of water and not create microbubbles or water flashing to steam.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    Master Hot Water Mpls,MN BadgerBoilerMN's Avatar
    Join Date
    Mar 2011
    Location
    Minneapolis
    Posts
    285

    Default

    Nice drawing Dana! All low-mass boilers, including electric boilers, should be pumped-to for the reasons mentioned. It is the position of the expansion tank and air-eliminator that is most important, most properly, always on the low pressure side of the pump. This maintained the point of no pressure change.

Similar Threads

  1. Used hydronic circulator pump to transfer pump ??
    By Boston1 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 08-22-2012, 08:23 AM
  2. Boiler Circulator Pump Always Running
    By jdbs3 in forum Boiler Forum
    Replies: 4
    Last Post: 11-30-2011, 08:48 AM
  3. circulator pump question
    By shendog in forum Boiler Forum
    Replies: 3
    Last Post: 02-08-2010, 11:02 AM
  4. Circulator pump leak
    By petergunn in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 11-25-2007, 01:04 PM
  5. Circulator Pump Setting
    By shakedownstreet in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 11-12-2007, 07:41 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •