    Hi, so i finally got the remote for my T-K2. It does not show any trouble codes
    Any one have any other suggestions?
    I was thinking it must be a non sensor issue since it gets no codes. Perhaps the control valve is acting on it's own.
    Any help would be great.

  2. #17
    DIY Senior Member lifespeed's Avatar
    Join Date
    Apr 2007
    Location
    California
    Posts
    319

    Default

    Quote Originally Posted by sapo View Post
    Hi, so i finally got the remote for my T-K2. It does not show any trouble codes
    Any one have any other suggestions?
    I was thinking it must be a non sensor issue since it gets no codes. Perhaps the control valve is acting on it's own.
    Any help would be great.
    Did you ever measure the temperature of the hot water and compare it to the setpoint? You already know the heater is shutting down the flow rate, now you have to figure out why. If the temp is correct then perhaps it is incapable of putting out enough BTU, so it throttles the water flow to maintain temp.

    If you can't do the troubleshooting you're going to have to hire somebody who can, or buy a new heater.
    Lifespeed

  3. #18
    DIY Junior Member sapo's Avatar
    Join Date
    Oct 2012
    Location
    Felton, CA
    Posts
    11

    Default

    I checked the output temp with a thermometer at the faucet. It is the correct temp. The new remote also verified the set point and output temp as being accurate.
    When the problem started back in october the incoming water temp was warmer than it is now, yet the output temp and gpm has remained the same. This would suggest to me that the burner capacity is not taxed.
    I emailed the company, i guess i'll see what they have to say.
    At this point my wallet prevents me from hireing someone or buying a new unit.
    The control valve is only $90 so i might throw a new one at it and see if it sticks.

  4. #19
    DIY Senior Member lifespeed's Avatar
    Join Date
    Apr 2007
    Location
    California
    Posts
    319

    Default

    Quote Originally Posted by sapo View Post
    . . . yet the output temp and gpm has remained the same. This would suggest to me that the burner capacity is not taxed.
    I emailed the company, i guess i'll see what they have to say.
    Most tankless heaters will reduce the output flow, using their flow control valve, in order to maintain water temperature. Given your problem (reduced flow rate when the heater is plugged in and controlling output flow), it would appear that your burner is not being asked to produce maximum rated BTU. There is a possibility it is not capable of max BTU output, so the water heater throttles the flow to maintain temperature. So maybe a problem on the burner side, or it's gas valve and control.

    There is also the possibility your flow control valve won't open up all the way, so the brain throttles back the gas to avoid overtemp. But you said when unplugged the flow control valve opens up, right? So not a mechanical blockage, but possibly electrical control and or the servo within the valve itself?

    Talk to Takagi and see if there is a diagnostic mode available, where you can manually command the flow valve. You need to identify if the problem lies in the water control side, or the flame control side. Either one could potentially cut down your water flow.

    Unfortunately these water heaters are somewhat more complicated. Hopefully they have provided some helpful built-in diagnostics and manual controls to allow you to determine the problem without guessing and parts-swapping too much.

    Edit: Here's a test - turn the temperature up all the way, hopefully it will allow you to go up to 140F or so. See if the water flow rate is reduced. Then turn the temperature down to 110F. See if the water flow increases. This should tell you if the heater is limiting water flow based on limited burning capacity.
    Last edited by lifespeed; 02-02-2013 at 10:45 AM.
    Lifespeed

  5. #20
    DIY Junior Member sapo's Avatar
    Join Date
    Oct 2012
    Location
    Felton, CA
    Posts
    11

    Default

    Thank you, excellent idea. I will try it and see what we get.

Similar Threads

  1. water pressure drop?
    By djwehr in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-11-2012, 06:00 PM
  2. Drop in Water Pressure?
    By bperillo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 26
    Last Post: 11-09-2010, 01:28 PM
  3. Water pressure drop
    By kevin schuhl in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 12-12-2009, 01:52 PM
  4. Water Pressure Drop
    By Siegfried in forum Pumps and Tanks Well Forum & Blog
    Replies: 8
    Last Post: 07-03-2007, 06:45 AM
  5. Why Would Water Pressure Drop?
    By nipandgab in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 04-24-2006, 08:10 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •