    I'm replacing a sewage ejector pump and installing a "Zoeller Tri-check" at the same time.

    The tri-check is a union check valve and ball valve in one unit, and is made of PVC.

    The pump is cast iron, the main line I'm tying into is 3" ABS.

    PVC for DWV is very uncommon here, but I'm required to have the ball-valve etc. due to local code.

    The ejector is right below the 3" abs line, so I will be dumping into the top of the line w/ a wye and 1/8th bend.

    There are female threads on the pump, and 2 sockets, one on either end of the tri-check.

    Where would the best place to transition from PVC to ABS be? I'm not planning on using transition glue, I was thinking female PVC adapter to male ABS adapter right after the ball valve before the 1/8th bend and wye...

    Is this threaded connection trustworthy?
    Attached Images Attached Images  
    Last edited by Terry; 10-29-2012 at 09:28 PM.

  2. #2
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    Why not a shielded neoprene coupling? Much handier when (not if) the time comes to dissassemble/reassemble
    the works.

  3. #3
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I have a Proflex 3000-22, I wasn't sure if these were meant for discharge on pumps though?

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,199
    Blog Entries
    1

    Default

    The best place to transition from PVC to ABS is with a shielded coupling. That's a plus 1

  5. #5
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Great thanks guys, I've got the coupling already but was second guessing and thought I would check in here.

Similar Threads

  1. pex to fixture transition
    By joatmoo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-14-2010, 02:15 PM
  2. Transition cement
    By ilya in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 01-11-2010, 06:29 PM
  3. ABS transition cement?
    By MikeVila in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 15
    Last Post: 11-10-2008, 11:31 AM
  4. PCV transition
    By Rancher in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 01-01-2008, 12:47 PM
  5. cast to pvc transition
    By buddyluv in forum Toilet Forum discussions
    Replies: 2
    Last Post: 04-08-2005, 10:08 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •