That's my guess now as well. Have you actually watched the pressure gauge at the pressure tank while this is going on? Is there a solenoid valve in the geo lines anywhere to isolate all the geo plumbing from the rest of the world when the geo is off? I wonder if you need a check valve in the geo dump line pointing to the well.
The Heat pump generally has it's own pump which may be pulling through the softener when it runs and because it pulls a fairly high volume and water always follows the path of least resistance that path may be through the softner outlet.
No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license!
Is that the actual order from the pressure tank? Your description sounds like there is no pr. tank tee, just regular tubing. A pic of that would be nice.
What is a Taco valve?
What storage tank, and why do you have one, what is it used for?
Is it a pressurized tank or non pressurized?
Do you mean you have a stop valve or 3 valve manual by pass AND a Clack by pass valve too? A pic would be helpful.
When you say discharge do you mean from the time the pump turns off until it comes on again? And the charge is from the time the pump comes on until it shuts off?
If so that is way too little time for the pump to be off between starts and that is going to kill your pump fairly soon and it runs up your electric bill.
That is called short cycling and all pump manufacturers want the pump off at least 60 seconds for up to 2hp pumps. For 2hp and larger the time is longer.
That length of time is controlled by the size of the pressure tank and that and the psi range of the pump pressure switch controls the number of gallons the tank delivers between pump runs; those gallons are called draw down gallons.
992-770=222. 222gals/7hrs=31.714 gals per hr., or .5 gpm for all of 7 hrs. Since the geo doesn't run constantly the flow through the softener has to be higher than .5 gpm.
I can not believe or see how others here can believe that that much flow is due to expansion of PEX tubing a few seconds once every 30 seconds. Plus it would mean that the pump is not coming on before the pressure tank empties since there is no restriction to backflow meaning the pressure is always the same in the PEX as it is in the pressure tank. So to me there has to be another cause.
Plus there is the storage tank being dumped into the sump pump hole causing the same flow through the softener. Which makes me wonder why a storage tank dumping into a sump pump and where the drain line from the softener is going.
Click Here to learn how to correctly size or program a water softener.
Are you thinking that there is perhaps a siphon going on? I'd like to see pictures of the set up but that's a distinct possiblity. If the drain line is in the same hole as the geo, and the sump fills over the softener drain line it could possibly pull through that drain line when the geo is running. raising the drain line so there's an air gap will give him a quick answer.
No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license!
Where is the geo system getting its source water from? Another well, I presume? In any event, why would it dump into the domestic well's pump output line? I could understand using the domestic well as the dump (or the source, for that matter), but I'd rather see a separate dump line to the well, and not pressurize the line the well pump has to pump into.
Note -- I have no expertise in the area of open-loop geo systems. Maybe it shows.
Sorry been away from the computer.
Again, thanks for all the replies and help.
Problem is fixed, continue reading if you want to know.....
So, I decided to try and fix the short cycling of my pump. I turned my pump off and emptied my water lines, put in a new pressure gauge, and pressurized my pressure tank to the correct value. This solved 2 problems. My cycling went from about 48 seconds, to 2 minutes and 50 seconds. AND, my water softener quit flowing backwards!
My best guess is since my pressure tank wasn't working correctly, it was causing my water lines to charge and discharge to fast, causing the meter in my water softener to move.
Cheers!
Thanks for the follow up and I'm glad you found the cause and fixed it with more than a misapplied band aid like a check valve.
Click Here to learn how to correctly size or program a water softener.