Thread: Water softner flowing backwards.

  1. #1
    DIY Junior Member chachie's Avatar
    Join Date
    Oct 2012
    Location
    Greentown, IL
    Posts
    6

    Default Water softner flowing backwards.

    I have a clack ws-1 type water softener. Had the water softener installed at a different time from the rest of my plumbing and my Geothermal unit.

    My geothermal is open loop aka pump and dump.

    With Geo turned off and no one using water in the house, everything is fine. When the Geothermal system kicks on and no other source of water is being used, I'm getting a small amount of usage on my clack water softener. It is approximately about .5 gallons a minute WHILE the geo is on. When the Geo is off, there is no water usage.

    So....Some how my geothermal unit is leeching a small amount of water through my water softener. At this time, neither the plumber/geo, or the water softener people are owning up to any problem. I'm hoping that some how there is a bad seal in the water softener that is allowing a reverse flow of water through the softener. Does anyone have an idea and what I might do to fix this?

    Thanks

    Chachie

  2. #2
    In the Trades Akpsdvan's Avatar
    Join Date
    Dec 2009
    Location
    Alaska
    Posts
    1,471

    Default

    Back flow/check valve on the in coming side of the softener so that the water can only go one way through the media.
    Now this is only an idea if there is truly a back flow through the softener.

  3. #3
    DIY Junior Member chachie's Avatar
    Join Date
    Oct 2012
    Location
    Greentown, IL
    Posts
    6

    Default

    That was my first thought...to add a check valve in front of the inlet to the water softener. But I couldn't find anyone else who had to add a check valve in front of their water softener, which leads me to believe there is a bigger issue. I have scoured the internet trying to find something on this problem I have, and was surprised there is nothing out there.

    Does anyone have an idea what would cause a clack valve to allow a reverse flow of water? Or if that isn't the case, why the meter runs when no soften water is used, but when the geothermal unit(which is in front of the inlet) runs and the water pump cycles?
    Last edited by chachie; 10-28-2012 at 11:02 PM. Reason: clarity

  4. #4
    In the Trades Akpsdvan's Avatar
    Join Date
    Dec 2009
    Location
    Alaska
    Posts
    1,471

    Default

    I was just working on a system that has a water line tee out in the drive way with two pressure tanks and of the tanks has the well control and the pressure switch.
    There is now a back flow check valve between the pressure tank and the softener in each house, as each house's pressure tank feeds the other house and to keep the water from flowing back even a little through the softener there is the back flow check valve.

    This set up is working great.

  5. #5
    DIY Junior Member chachie's Avatar
    Join Date
    Oct 2012
    Location
    Greentown, IL
    Posts
    6

    Default

    Thanks for the replies. I guess I will be installing a back flow check valve between the inlet and the geo. The geothermal is stealing about 800 gallons a day from my water softener, it would seem that if this was normal and a check valve should be part of the installation process I would of read about it somewhere. But I can't find anyone else having this problem.

    Cheers!

  6. #6
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    My guess (and it's only a guess) is that while the geo is running the pump pressure is fluctuating up and down causing water to move back and forth across the meter. For it to do that, there has to be some room for expansion on the soft side, perhaps an expansion tank for the hot water or lots of PEX lines.

    Monitor the pressure while the geo is running to see if it is fluctuating.

    If you put in a checkvalve then you need to have an expansion tank after it.

  7. #7
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,796

    Default

    Quote Originally Posted by chachie View Post
    That was my first thought...to add a check valve in front of the inlet to the water softener. But I couldn't find anyone else who had to add a check valve in front of their water softener, which leads me to believe there is a bigger issue. I have scoured the internet trying to find something on this problem I have, and was surprised there is nothing out there.

    Does anyone have an idea what would cause a clack valve to allow a reverse flow of water? Or if that isn't the case, why the meter runs when no soften water is used, but when the geothermal unit(which is in front of the inlet) runs and the water pump cycles?
    Five gpm is not a small amount. And if I'm right, a backflow through the softener is not going to add to the gallons used. BTW, a backflow that causes a vacuum can bust the resin tank real easy.

    All control valves will allow backflow.

    I think you have a plumbing problem past the softener that is allowing geo water flow through the softener/house out to the well or wherever it goes. I had a softener service call on a softener I didn't sell or install with that problem many years ago and found the problem after the geo and softener guys said all was fine with their side of things. It was a 'cross connection' between the geo and potable water systems which was expensive and difficult to fix.

    I doubt you have a large enough expansion tank etc. to provide a 5 gpm flow against an open discharge geo pump.

    If you shut off the inlet side of the Clack by pass valve you shut off water to, through and past the softener. You might want to do that for a few seconds while the geo is running and see if the metered flow stops and then open it. I wouldn't close it for more than a few seconds if your geo doesn't have a pressure switch to turn off its pump or you could over pressurize and bust things.

    If closing the inlet by pass valve stops the metered flow through the softener, the cross connection is somewhere past the softener.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  8. #8
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    Quote Originally Posted by Gary Slusser View Post
    I doubt you have a large enough expansion tank etc. to provide a 5 gpm flow against an open discharge geo pump.
    I very much doubt that 5 gallons is all moving in the one direction. More than likely a much smaller amount is moving back and forth repeatedly as the pressure fluctuates.

  9. #9
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,711
    Blog Entries
    1

    Default

    I agree with LLigetfa, I would start with a check valve to try to stop the water fluctuating. The turbine inside the WS1 is highly sensitive to any water flow and will indicate flow regardless of flow direction. Dont forget about thermal expansion if you install a check valve.

  10. #10
    DIY Junior Member chachie's Avatar
    Join Date
    Oct 2012
    Location
    Greentown, IL
    Posts
    6

    Default

    Thank you for the replies.

    It's actually only 1/2 a gallon per minute(I wrote .5) sorry for the mix up. I was able to talk a "represenative" of the manufacturer of the water softener(a retired plumber of 32 years) and he gave me a few options. 1st, to install a check valve at softener inlet AND the thermal expansion tank at the water heater inlet.

    2nd, replace my water pump with a constant pressure one.

    3rd basicially disable the metered operation by lowering my hardness down to 5 and force my softener to regenerate every 3 days.

    I did look over all of my plumbing and did quite a bit of testing.(I will not go into great detail here) But there is no cross connection any where. the reps opinion is: water is flowing back and forth through the softener causing the meter to change. He doesn't think the geothermal is actually pulling in any softened water because of the distant of the geo to the softener and the amount the meter is moving.

    I have went with option 3 as of right now, since it was the quickest option. I am thinking about possibly getting a small inline constant water booster if I can find one and install it after my storage tank and Geo but in front of my water softener. I'm guess I will need to install a thermal expansion tank with this set up as well, but it might give me the best overall water experience at my faucets and hopefully not to much of a dent in my billfold.

    Thank you all for the replies

  11. #11
    In the Trades Akpsdvan's Avatar
    Join Date
    Dec 2009
    Location
    Alaska
    Posts
    1,471

    Default

    By not stopping the back flow through the softener you stand to lose resin, that is unless there is an upper basket under the valve body.
    Also by not stopping the back flow through the softener the resin is getting unpacked and repacked each time there is back flow and then you turn on water inside the house.
    Neither is good for the system ..

  12. #12
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,796

    Default

    Quote Originally Posted by LLigetfa View Post
    I very much doubt that 5 gallons is all moving in the one direction. More than likely a much smaller amount is moving back and forth repeatedly as the pressure fluctuates.
    I don't know what you base that on but most open loop geo systems that I've seen move 5 gpm + and are open discharge (hence open loop); next to no pressure builds up while the pump discharges the water down the well to below the water level.

    The pump isn't constantly turning on and off during the heat cycle run like a short cycling well pump does. And especially every minute which you are saying his has to be doing. And if it did, the pump wouldn't last long.

    I didn't see the latest reply until after posting the above. I see now it is point 5 gpm.
    Last edited by Gary Slusser; 10-29-2012 at 09:21 PM.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  13. #13
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,687

    Default

    Could he run a line bypassing the softener with a check valve pointing toward the well, as well as the check valve at the softener inlet pointing toward the house? That would allow the geothermal pump to continue to dump into the well, and prevent reverse flow through the softener. How does the well pump handle forced reverse flow?

  14. #14
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,690

    Default

    I doubt there are any reverse flows large enough to carry resin out but the upsetting of the pack is a possibility. Personally, I would have gone with a checkvalve and expansion tank (option 1).

  15. #15
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,796

    Default

    Quote Originally Posted by chachie View Post
    Thank you for the replies.

    It's actually only 1/2 a gallon per minute(I wrote .5) sorry for the mix up. I was able to talk a "represenative" of the manufacturer of the water softener(a retired plumber of 32 years) and he gave me a few options. 1st, to install a check valve at softener inlet AND the thermal expansion tank at the water heater inlet.

    2nd, replace my water pump with a constant pressure one.

    3rd basicially disable the metered operation by lowering my hardness down to 5 and force my softener to regenerate every 3 days.

    I did look over all of my plumbing and did quite a bit of testing.(I will not go into great detail here) But there is no cross connection any where. the reps opinion is: water is flowing back and forth through the softener causing the meter to change. He doesn't think the geothermal is actually pulling in any softened water because of the distant of the geo to the softener and the amount the meter is moving.

    I have went with option 3 as of right now, since it was the quickest option. I am thinking about possibly getting a small inline constant water booster if I can find one and install it after my storage tank and Geo but in front of my water softener. I'm guess I will need to install a thermal expansion tank with this set up as well, but it might give me the best overall water experience at my faucets and hopefully not to much of a dent in my billfold.

    Thank you all for the replies
    Since you say you have to add an expansion tank, I take that to mean you don't have one now.

    If that's true, have the guys suggesting you have back flow and a that a band aid sol;ution check valve is needed explain how you get back flow through the softener constantly while the geo is running. If a check valve is needed, why wasn't it installed with the geo system?

    IIRC I tested the Clack meter to see if it would register a back flow by blowing on the back side of the turbine and it didn't but I could be wrong but I can say it's not easy to get a fan blade to rotate backwards, and the meter 'blade' in a Clack is a turbine type, not a paddle/water wheel type like some Fleck meters use.

    The reason you haven't heard of other open loop geo systems requiring a check valve to be added after installation is because all others didn't need one or... already had one installed as part of the geo's installation or... they simply use a solenoid valve to dump the geo when its pump comes on.

    I think you are getting some bad advice from guys that don't know open loop geo very well.

    The constant flow/variable speed pump is an expensive and dumb idea; they don't last very long without having problems. If you want to go that route, use a Cycle Stop Valve but, that too is not going to stop back flow when the geo is dumping water back down the well. And if someone thinks the check valve will cure the problem, why are they suggesting other more expensive and intrusive solutions?

    Also, you don't just change the hardness gpg to get the softener to regenerate sooner. You have to change the K of capacity (and salt dose) and/or the gallons between regenerations. And if the problem is a missing check valve why screw around with the softener regeneration schedule and use more water and salt at your expense?

    You said you didn't want to get into the testing you did to see if there was a cross connection, so how about describing your set up (pics would help) and how the storage tank you mention is being used? Or by storage tank do you mean your well pump pressure tank?

    You say your geo system comes off before the softener inlet... How is the geo system kept separate from the house potable water system?
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

Similar Threads

  1. PVC Cement on pipe with flowing water
    By mwolf00 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 21
    Last Post: 03-30-2012, 04:37 AM
  2. Replies: 6
    Last Post: 01-11-2010, 07:09 PM
  3. Culligan mark 100 water softner water flowing to brine line all the time
    By seahawk99ca in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 08-27-2007, 09:35 AM
  4. Low flowing water
    By Frank in forum Pumps and Tanks Well Forum & Blog
    Replies: 12
    Last Post: 12-14-2005, 01:02 PM
  5. water flowing from faucets in bursts
    By nflguy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 05-31-2005, 12:24 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •