Necessity of Vacuum Relief Valve - Not Pressure Relief Valve

Users who are viewing this thread

WillieK

New Member
Messages
12
Reaction score
0
Points
0
Location
Houston, TX
Hi everyone,

My new water heater states: "Install vacuum relief in cold water inlet line as required by local codes". My inspector says I need one. I read on one of the old posts that you only need one if your water heater is on an upper floor or in the attic. Mine is in the attic. What is the purpose of a vacuum relief valve? What could possibly happen if I didn't install one - other than the inspector killing me?

Thanks in advance for your help.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
It prevents siphoning of the water heater.
If the water main is shut off to the home, and then a faucet is opened, it will siphon the water heater. When that happens, the top element burns out in seconds. With a non-functioning top element, you now have no hot water.

watts-lfn36-instructions.jpg
 
Last edited:

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; Inside most heaters today there is a port hole on the
dip tube inlet at the top of the tank that prevents the
heater from siphoning....... a heater cannot siphon down

the valve they want you to install is not necessary


It is NOT to prevent siphoning. If the water supply to the building is turned off and the water is drained out, the tank will be subjected to "severe" negative pressure, i.e., a vacuum, and the amount of the negative pressure will be in direct corellation to how high the heater is above the drain point. The heater will withstand 300 psi of pressure but relatively LITTLE negative pressure so it will "collapse". If you have you ever seen a tanker truck that the driver opened the drain hose before he opened the lids, you have seen a collapsed tank and that was just the suction of a few feet between the truck and the ground. In Texas there was a city water storage tank that "imploded" and it was VERY impressive to see it look like an accordian. If you heater is in the attic, you DO need the vacuum relief valve, just as a safety measure.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Ja, hj has the right answer. A vessel designed only for pressure should not be exposed to a vacuum. There have been documented cases of various tanks collapsing from the improper implementation of a booster pump as well. Water softeners have also collapsed from an improper drain line installation.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
THey're required where I live, regardless of where it is installed, as is a tempering valve. Really pisses off uninformed people when it comes time to replace their WH (assuming they get a permit), as it can add some to the installed price.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; THey're required where I live

That is the problem with beaurocrats, a special interest tells them how to solve a certain "occassional problem" and they decide to make it a universal solution. We have the same thing here with pressure reducing valves. Most areas do not have the pressure that would require them, but since they do not want to address just the areas where a PRV is needed, they just passed an ordinance that EVERY house must have one.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
what????

HJ......

I dont have a clue as to what you guys are referring to
so please inform me as to what this is all about ...are you speaking about
residential or commercial systems actully imploding??

I have yet to see a water heater on the higher floors of any building
"implode" because they have drained down all the water....
Inside all heaters there is a dip tube with a anti siphon port hole
to keep this from happenning...... and I doubt it could

I would like to have an imploded heater for my store front window
if one actually exists..... that would be an extremely rare find.....


back a long time ago , this was something that was required on
drain down solar panels. I had to tangle with some "solar enjineers"
on this subject becasue they were so un-reliable that they would
leak and had to be changed out all the time due to any pressure fluctuations
in the system.......


this vaccuum relief valve will only cause troubles and probably leak all
over someones attic yearsdown the road when the system is turned off when
the poor plumber attempts to change out a ballcock or hose bib.......

this is just my humble opinion
 
Last edited:

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
If anyone has a water heater that has imploded or even a picture of one
I would really like to have a picture of it for my web site....

I feel like I am asking for a real picture of BIG FOOT

send me those pics..... I

am gonna Google imploded heaters and see what I can find


http://www.homeownershub.com/plumbing/imploding-hot-water-heater-2077-.htm


send me what you got HJ
 
Last edited:

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
tank

Not a water heater but the same thing happens on a smaller scale with a water heater, since it also does not have internal baffles, (which pressure vessels such as a sumbarine do have to resist collapse from exterior pressure), to strengthen it.
http://www.ebaumsworld.com/video/watch/344750/?autoplay=true

MPM, the "hole" is to prevent siphonage, NOT suction. Siphonage will only occur if a faucet is opened to let air into the system. Vacuum depends on the entire system being closed/sealed. In fact, if a faucet were opened so the hole stopped siphonage, it would ALSO break the suction and eliminate the need for a vacuum relief valve.
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
Mark,
Often when I'm draining down the house to do a pipe repair or to replace shutoffs, I loosen the flex connectors on the water heater to prevent the tank from siphoning. If it's electric, I just turn off the breakers at the panel so I don't let the water drop too low and burn out the top element.

Siphoning happens. We just take the right steps, knowing that.

In the city of Bellevue, if the electric heater is on the first floor, the vacuum breaker is not required, only if it's on a second or higher story.


Water heaters will siphon!
 
Last edited:

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Terry ...you have a firm grip on the obvious

Mark,
Often when I'm draining down the house to do a pipe repair or to replace shutoffs, I loosen the flex connectors on the water heater to prevent the tank from siphoning. If it's electric, I just turn off the breakers at the panel so I don't let the water drop too low and burn out the top element.

Siphoning happens. We just take the right steps, knowing that.

In the city of Bellevue, if the electric heater is on the first floor, the vacuum breaker is not required, only if it's on a second or higher story.


Water heaters will siphon!


Terry ...you have a firm grip on the obvious

I completely agree with you Terry..... yes they will siphon
till they hit the siphon hole on the dip tube in the heater..
and sometimes its not a bad idea to open the t+p valve
or something like you stated


YES a water heater will siphon,

but unless you put the heater to a test in an experiment
to see how much negative pressure you need to use to make it
implode..... the odds are it will never , ever implode. in a real world
situation.....,,,


I am gonna go get my power ball tickets now...
its up to 169 million and my odds are better to win
the power ball than see a water heater implode in my lifetime...



on another note..... how have you been doing lately???
feeling ok and all???.
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
I'm not worried about one imploding.
Hey, I like this big text.
:)

Feeling good. I spent a few days doing a repipe in a crawl. That gave my stomach muscles a workout. Just waiting for snow to fall so I can start using my skis.


 
Last edited:

Rap

New Member
Messages
63
Reaction score
0
Points
0
Location
california
Not sure if i grasp hj's argument, but for what it's worth:

1. the 1/8th hole near the top of the dip tube is called an anti-siphon hole ( for occasions of negative pressure ) and described as such by some mfr's of dip tubes and water heaters.

2. siphonage, as i understand it, is suction and gravity at work.

3. It's recommended ( can't remember by whom ) that bottom supplied water heaters ( which, obviously, have no installed dip tube ) have a vacuum-relief valve installed,no matter the location of the water heater.

4. A number of local codes in the Cal. Bay Area require vacuum-relief valves in attic installations - but i dont recall even ever seeing a vac. relief valve except in pics.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
WHere I live, if you want to pass code, you need a vacuum relief valve and a tempering valve on any new or replacement WH installation.
 

Rap

New Member
Messages
63
Reaction score
0
Points
0
Location
california
jadnashua, thank you for your post ref. New England code req's.
Do you have any diagrams or pics of approved N.E. installations with both fittings in place?
I ask because diagrams and pics on the web show all manner of confusing arrangements where tempering valves are installed in residential situations.
I'm going to post a new/separate message about this tempering valve business.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; siphonage, as i understand it, is suction and gravity at work

Suction is a function of gravity AND air pressure. Water falling down, in a closed space, creates a loss in pressure. If there is no way for air to get into the chamber, a negative pressure, aka a vacuum, occurs, but siphonage does NOT occur. If air can enter, then depending on the dynamics of the chamber, the liquid either drains, or if it is part of an inverted "U" shape then it is siphoned out until it reaches a level where air can enter and break the flow. This point is either the "anti siphon" hole or the bottom of the siphon tube. In all cases, air entry is required to enable the system to reach an equilibrium. The vacuum relief valve is installed at the highest point in the system. Tempering valves can be installed anywhere they are needed. Hot in on one side, cold in on the other, and the tempered water out of the center to the system. They are installed anywhere you have access to all three lines.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
jadnashua, thank you for your post ref. New England code req's.
Do you have any diagrams or pics of approved N.E. installations with both fittings in place?

I'm away for a couple of weeks, I can take a picture of mine when I return. Note that this is a CITY requirement, and maybe not a state one, as I understand it, but have not checked the state codes.
 

Nail24

New Member
Messages
6
Reaction score
0
Points
0
Location
Georgia
I just had a vacuum relief valve fail and allow water to flood the house. Has this happened before and if so what causes the failure?

wh-relief-valve.jpg
 
Last edited by a moderator: