Thread: Necessity of Vacuum Relief Valve - Not Pressure Relief Valve

  1. #61
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    WH are tested for pressure. While they may test them for vacuum, I've never seen it listed. Get the right conditions, and you can get a vacuum in a WH. It doesn't take much to collapse or distort a vessel designed for pressure when you substitute vacuum - the tensile strength is generally a lot stronger than the crushing into a void.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  2. #62
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Default no big foot sightings on another thread

    thought I would let everyone know that no one over there at PZ has ever actually seen an imploded water heater...


    but some of them claim that they have seen big foot, and a couple of them claim that they have been abducted by aliens too...

    but no imploded heaters

    lots of them claim that they have to install the vrv valves on heaters in their area where the heater is above the fixtures on the first floor.....which was a suprise to me.....

    In this city and surrounding counties their are at least 150,000++ homes built since the mid 90s with heaters on the second floor and no vrv valves on anything.....but nothing has ever gone wrong that I have heard about.... basically no imploded heaters

    I suppose the inspectors in this State must think they are not necessary because of the hole in the dip tube and feel that its a complete waste of time and money.-

    or we are just a bunch of ass-backwards hicks living out in the sticks






  3. #63
    Master Plumber Caduceus's Avatar
    Join Date
    Oct 2013
    Location
    Pittsburgh, PA
    Posts
    99

    Default

    I think that you could find that hj and nhmaster3015 (he hasn't been on this forum for a couple of years) have already expressed that same concerns and situations for vacuums in hot water tanks on other plumbing forums and they also meet resistance from other plumbers.
    A common situation that simulates what can happen to a tank is this; A customer has a leaking hot water tank. They shut off the gas and the cold water supply and the tank is leaking onto the floor while they wait for a plumber. When the plumber arrives hours later or the next day, the homeowner explains that it wasn't leaking badly but then after several hours they heard a WHOOSH!! and the tank suddenly blew loose at the bottom and all of the water came dumping out. What happened was as the tank emptied there was a void created at the top and the water was cooling. Once the water got low enough and the air in the void cooled enough a vacuum occurred and compressed the remaining water finding the weakest spot on the tank (the leak) and blew the hole open wider forcing the water out. The nipples and sometimes even the pipes connecting are all bent up from the action. This same situation is created with homeowners who flush their tanks or plumber who do repairs on water piping. It's commonly mistaken as an exploded tank and some plumbers on other forums even blame it on thermal expansion. Tanks can over heat and blow the jacket of the tank wide open, but on imploded tanks there is usually little external evidence (the jacket appears to be normal) only showing the distorted nipples and pipes mentioned above.

  4. #64
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Default

    Quote Originally Posted by Caduceus View Post
    This same situation is created with homeowners who flush their tanks or plumber who do repairs on water piping. It's commonly mistaken as an exploded tank and some plumbers on other forums even blame it on thermal expansion. Tanks can over heat and blow the jacket of the tank wide open, but on imploded tanks there is usually little external evidence (the jacket appears to be normal) only showing the distorted nipples and pipes mentioned above.


    that sounds like a great theory, but I do not believe in big foot either...

    The picture of the unit I posted earlier was a tank about to explode....
    the nipples on top were crushed inwards because the tank itself had expanded
    outwards dramatically like a baloon....

    If a water heater was about to crush in on itself I would think
    that the nipples would be pointing outwards, of course we is getting
    into some grey area of thermo-dynamics here ....

    So The next time I see a heater with the nipples pointing outwards,
    I will cut the jacket off of it and see for myself....and I will post it here.

    this will probably happen some time after I post the picture of bigfoot
    walking across my back yard.....

    the pz site someone claims that a marathon plastic heater imploded
    and cracked the liner due to someone draining it and voided the warranty
    but no one has actually seen an imploded heater....

    I will see my Rheem salesman this morning and ask him about this whole thing
    I wonder if he is totally in the dark about this also...


    By what you claim, I actually ought to be at ground zero for imploded water heaters in INDY cause not one plumber in town has ever installed a vrv valve on heaters in tract homes on the second floor since at least 1990. I know that there are well over 150+++ heaters out there on second floors in this region....

    so BIG-Foot has to be out there just waiting for me to find him......and I am gonna get me a picture of one of these critters some day






    yea, uh-huh

  5. #65
    Master Plumber Caduceus's Avatar
    Join Date
    Oct 2013
    Location
    Pittsburgh, PA
    Posts
    99

    Default

    Name:  collapse 2.jpg
Views: 58
Size:  55.8 KBName:  collapse.jpg
Views: 49
Size:  43.2 KB


    This is what an imploded hot water heater looks like. Nipples and T&P valve bent inward. If you ever come across this, remove the jacket. It will appear to still be intact from the outside. Once removed you will easily see that it is not outward force, but inward. This happened suddenly to a member of another forum and this is a mild case of imploding tanks.
    If I find some with more detail or a jacket removed I will post them.
    This is the post from the thread describing the situation:

    "I seen a few things in my day but this one is a first for me. My daughter called to say she was worried about her hot water heater. I thought she was over reacting a bit and had just seen too many insurance commercials! You know, the hot water heater missile. She tried to convince me that her hot water heater's (that been known to drip a bit) down pipe had moved and was sticking out at an angle. I told her not to worry and I'd be over to look at it the next day. She did say as a bonus that the dripping had stopped though.

    Well, it appears that the hot water heater is quite literally collapsing from top. The metal of the hot water heater itself seems to sunken in. And when the metal top of the hot water heater sunk in it caused the pipes to move as well and they're now at strange angles.

    And, yes she right, because it's sunk, the down pipe is sticking out at quite an angle. See picture. This has happened at some point in the last week or so.

    She bought this small 1950's bungalow about 1.5 yrs. ago and it is a manufactured pre-fab home (National Homes) on a traditional block foundation.

    Has anyone ever encountered this before or have any idea why it would have done this. Suffice it to say we'll be replacing it very soon. "
    Last edited by Caduceus; 11-16-2013 at 11:47 AM.

  6. #66
    Master Plumber Caduceus's Avatar
    Join Date
    Oct 2013
    Location
    Pittsburgh, PA
    Posts
    99

    Default

    It's been almost 24 hours since I posted the pictures. Isn't somebody going to jump on this thread, breathe some life into it and tell me that the pictures that I posted are something other than what I stated? C'mon...it's not THAT challenging.

  7. #67
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    Okay. Let's assume it has imploded. If so, how could it be? It appears that the WH is in the basement. You won't siphon the water out of it (unless you turned off gravity and flipped it around). If everything was closed off and the WH was drained from the bottom, the most vacuum that could ever be generated would be something like the elevation head of the WH itself (maybe 1-2psi at best) without some active means. It also sounds like nothing out of the ordinary was taking place when this happened.

  8. #68
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    How about pulling the covering off and letting us see that picture?
    Please, the next time anyone sees that, can they pull the cover, make a picture anad post?

Similar Threads

  1. Pressure relief valve bad?
    By billy_pilgrim in forum Boiler Forum
    Replies: 3
    Last Post: 07-09-2009, 01:09 PM
  2. vACUUM RELIEF VALVE ON CLOSED LOOP SYSTEM?
    By CHRISUPNORTH in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 11-24-2008, 06:16 PM
  3. vacuum relief valve?
    By KKfromNJ in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 09-05-2008, 09:18 PM
  4. what is a vacuum relief valve for?
    By northman in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 05-15-2007, 06:27 AM
  5. pressure relief valve
    By ttlcm in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 11-16-2006, 09:03 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •