    Can anyone tell me the equivelent length of a 3" PVC short and long 90 on a 90% furnace exaust vent.

    I am being asked to lengthen the pipe by 7' and add 1 / 90 on the exterior of the house because it is dumping out next to a new hot tub.

    The max length of the run can be 70'.

    There is 31' of pipe 2 / 90s and 1 / 45 right now.

    Thanks

  2. #2
    Plumber/Gasfitter dubldare's Avatar
    Join Date
    Sep 2005
    Location
    MN/ND
    Posts
    286

    Default

    As far as I know, there is no generic standard for venting of 90+ furnaces. There are limitations on where intakes and vents terminate which are prescribed by code, and are standard. The actual sizing of vents and the equivalent losses for fittings varies by the manufacturer. When dealing with venting of these appliances, nearly all codes digress to 'installed per manufacturers specifications'.

    Hope the customer has the literature/installation manual for the furnace.

    That being said, I do know that you will not find an equivalent for a short sweep 90. I've yet to see or hear of a manufacturer allowing them.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    Depends on the specific restrictions on that particular brand. Just looked at a Weil-Mclain vent install manual...max of 2 elbows allowed. On the particular one I looked at (Ultra-80), the max length of straight pipe was 100', so that shouldn't be a problem with the added length (again, though it is up to the specific unit you have). They specify long-radius elbows to keep the back pressure down.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    Trane XL 90 Mod.# TVC120c96 o or 0 B6
    Last edited by Cass; 01-05-2006 at 06:47 PM.