    Default Toilet Drain

    Which of these is the best configuration for a toilet drain ?

    Going to assume that C is incorrect because of no immediate vent pipe; that leaves A or B.
    Which one would be the best configuration ?

    Thanks,
    Arky


  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Deepending on the situation, all three can be correct, although "B" is the way it is usually done. It usually "boils down" to the logistics of the installion. The depth of the sewer and the direction from the toilet to the sewer connection, are two considerations which could change which one is "best" for a particular situation.
    Licensed residential and commercial plumber

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    In Washington State none of those would work. Since the toilet connects to a waste stack, it needs a vent between the waste stack and the toilet. That vent would then extend through the roof.


  4. #4
    DIY Member Arky217's Avatar
    Join Date
    Jan 2008
    Location
    Arkansas
    Posts
    40

    Default

    Quote Originally Posted by Terry View Post
    In Washington State none of those would work. Since the toilet connects to a waste stack, it needs a vent between the waste stack and the toilet. That vent would then extend through the roof.


    Sorry, I wasn't clear on the main stack; there is no upstairs, the main stack is the main vent.
    With that being the case, would A or B be the better configuration ?

    Thanks,
    Arky

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    I'd go with B, there would be easier air exchange with the stack. But, I'm not a plumber! This is the more commonly installed configuration and it hides more of the pipes, giving more room underneath the sink, if you need it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    quote; This is the more commonly installed configuration and it hides more of the pipes, giving more room underneath the sink, if you need it.

    This is a TOILET, and I hope you do NOT use your sink in place of a toilet. AIr is a gas, so it is not governed by the same rules of flow as water. At various times I have installed all three configurations and a couple you do not show.
    Licensed residential and commercial plumber

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Was thinking sink...given a choice and enough room for it, then A may work better with a toilet, but dont' think it makes a big difference.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    quote; then A may work better with a toilet, but dont' think it makes a big difference.

    They will all work exactly the same, with a slight caveat. Since a toilet is an "S" trap, the greater the drop out of the toilet before the vent connection, the more "suction" that will be created possibly helping the toilet flush better.
    Licensed residential and commercial plumber

  9. #9
    DIY Member Arky217's Avatar
    Join Date
    Jan 2008
    Location
    Arkansas
    Posts
    40

    Default

    In the following picture, assuming that the 'other drainage' pipe cannot be moved, which would be the better arrangement, A or B ?

    Thanks,
    Arky



  10. #10
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    I would use "A"
    B isn't vented.
    B would only work if it only included the same bathroom group (lav/shower) that the toilet is on and nothing else.

    Last edited by Terry; 10-15-2012 at 09:02 PM.

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    "A" always works. It would depend on what the "other drainage" is whether "B" would be acceptable. I had a customer once, where the "other drainage" was the discharge from a small sewer pump. Every time it operated it sucked all the water out of the toilet. The only cure would have been to break into the structure and relocate the connection.
    Licensed residential and commercial plumber

  12. #12
    DIY Member Arky217's Avatar
    Join Date
    Jan 2008
    Location
    Arkansas
    Posts
    40

    Default

    One last time on the toilet drain.
    Because of obstructions and space limitations, I need to have the toilet drain into the
    stack lower than the tub and sink.
    Would there be any potential problems with this arrangement, that is, having the sink and tub drain into the stack about a foot above the toilet inlet ?



    Thanks,
    Arky

Similar Threads

  1. Replies: 7
    Last Post: 08-21-2012, 12:11 PM
  2. Washer drain/toilet drain
    By Jeff Oosterhof in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 01-24-2012, 05:19 PM
  3. Toilet clogs - sewege ejector pump water level above the toilet drain
    By rgamett in forum Toilet Forum discussions
    Replies: 5
    Last Post: 08-01-2011, 12:10 PM
  4. shower drain to toilet drain rough in
    By baloonberry in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 10-26-2010, 03:41 PM
  5. Replies: 3
    Last Post: 02-17-2010, 07:23 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •