    Default Grounding electrode/bonding question

    Hi,
    I have recently installed two antenna's outside on my chimney on the second story of my house (one for OTA TV signal and one cellular antenna). I am attempting to ground these and have installed a new ground rod (8' long) at the chimney base, and will tie both antenna's to it with #10 solid copper grounding wire (per 2008 code).

    Now here's my dilemma. My main house electrical service grounding rod by my meter is about 50' away from my newly installed rod. I was planning on tieing these two rod electrodes together with #6 solid core copper wire (also per code). Unfortunately, I cannot find my main rod by the service to tie to. I have dug down about 3 ft following the main house ground conductor and am scared to go further lest I hit and damage that conductor while searching for the rod.

    So, I do believe that I could tie the secondary rod #6 bonding wire with the houses main wire by some means (vs directly to the rod) but am looking for opinion for best diy method outside of exothermic welding. My opinion on this is that this bonding wire's main purpose is to bleed off any differential in voltage and currents and not necessarily a primary path for a lighting strike, which is what the secondary rod is for, and subsequently I don't HAVE to tie directly to the main service rod. Is that line of thinking correct?

    If so, any suggestions on a good way to tie my #6 bond wire to that main ground wire would be appreciated.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Well, unless your house has a lot of fill around it, the ground rod should not be 3' deep. Are you sure you are not following the UFER wire which goes into your concrete footing? You will also NOT damage the conductor by digging next to it.
    Licensed residential and commercial plumber

  3. #3
    DIY Junior Member fotto's Avatar
    Join Date
    Oct 2012
    Location
    Ohio
    Posts
    4

    Default

    Quote Originally Posted by hj View Post
    Well, unless your house has a lot of fill around it, the ground rod should not be 3' deep. Are you sure you are not following the UFER wire which goes into your concrete footing? You will also NOT damage the conductor by digging next to it.
    hj,
    Attached are a couple of pics to help. House was built in 2000. Has underground electric and they had a pretty big trench open at outside service area. Wouldn't surprise me that they drove the rod into the trench bottom before backfill. The ground wire you see at the main service disconnect in my basement (my 200A inside panel is at opposite end of basement) is same that you see coming outside of house and running into the hole. There are no other ground wires anywhere else like at 200A panel or elsewhere, so I have to believe this is the one and the rod is just buried deep.

    After reading a bit more, I am coming to the conclusion to just clean up that wire and connect my #6 bond wire to it with a split nut. What do you think?
    Name:  service1.jpg
Views: 224
Size:  67.9 KBName:  disconnect1.jpg
Views: 179
Size:  51.6 KB

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Connect it to the conductor just before it enters the pipe using a split bolt

  5. #5
    DIY Junior Member fotto's Avatar
    Join Date
    Oct 2012
    Location
    Ohio
    Posts
    4

    Default

    Quote Originally Posted by jwelectric View Post
    Connect it to the conductor just before it enters the pipe using a split bolt
    Picture may be a little bad, but the conductor doesn't enter the pipe. If you look closely you can see it running down the side of it (it's a bit off colored due to weathering) at least to where I stopped digging. I guessing if I continued digging further it would at some point veer away from the house a bit to where it terminates to the buried rod.
    I was planning on connecting via split bolt just below ground level so you don't see it. Any issue with that

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    I don't buy it, that someone would install a ground rod at the bottom of the ditch and connect the ground wire. Was the pipe dug and installed AFTER the wiring was done or before it?
    Licensed residential and commercial plumber

  7. #7
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by hj View Post
    I don't buy it, that someone would install a ground rod at the bottom of the ditch and connect the ground wire. Was the pipe dug and installed AFTER the wiring was done or before it?
    I'll throw the ground rod in a ditch every chance I get. Too many rocks in the ground where I live to drive one with complete success each and every time.

  8. #8
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by fotto View Post
    I am attempting to ground these and have installed a new ground rod (8' long) at the chimney base, and will tie both antenna's to it with #10 solid copper grounding wire (per 2008 code).
    ...
    If so, any suggestions on a good way to tie my #6 bond wire to that main ground wire would be appreciated.
    Personally, I would go with at least #6 down from the mast. Actually, I prefer to run a bracketed tower up from the ground and let the tower be the grounding path. I have seen what lightning can do to a chimney.

    Quote Originally Posted by jwelectric View Post
    Connect it to the conductor just before it enters the pipe using a split bolt
    A split bolt would be fine. Exothermic welding is used on more elaborate ring ground systems around communication towers where the main objective is to save the electronics.

    http://en.wikipedia.org/wiki/Ring_ground

  9. #9
    DIY Junior Member fotto's Avatar
    Join Date
    Oct 2012
    Location
    Ohio
    Posts
    4

    Default

    Thanks for all the replies. I noticed that the telco ground (see top of disconnect pic where the red tag is) was bolted to the disconnect wire which gives me further confidence this is main service ground. Thur pm I ran my #10 down to second ground rod and then ran #6 over to the service #4 ground wire and connected with a split bolt. I may take the advice on running a heavier gauge down from the mast but next spring if so.

  10. #10
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by hj View Post
    I don't buy it, that someone would install a ground rod at the bottom of the ditch and connect the ground wire.
    It is common practice to simply lay the rod horizontally in the trench. I know a lot of installers that hate to drive ground rods and will often use a ground plate instead. We often used a jackhammer to drive them down.
    http://www.youtube.com/watch?v=vvCZvNj8H30

  11. #11
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,637

    Default

    What is the purpose for connecting into your power ground ?

    Connecting rods that far apart will do little good.

    #10 solid copper grounding wire is very little protection for a roof mount like yours. Even if some code says Yes. The Ground wire is to long for anything other than static discharge.

    Your Ground and signal wires should follow the same path and be grounded just before entering the dwelling at ground level.

    I personally would not waste the wire, and invest into some Good Antenna Coax protectors, Connected to their own Ground Rod at Ground Level. That would be the best protection for you and your home.


    You do not need to dig for the wire, You can connect it as JW suggested. Just do not cut and splice the original ground wire.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    quote; It is common practice to simply lay the rod horizontally in the trench

    How do you do it when you need two ground rods with separtion between them?
    Licensed residential and commercial plumber

  13. #13
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by hj View Post
    quote; It is common practice to simply lay the rod horizontally in the trench

    How do you do it when you need two ground rods with separtion between them?
    Point them in opposite directions.

  14. #14
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by LLigetfa View Post
    Point them in opposite directions.
    In two different ditches spaced correctly (6'?) apart...

Similar Threads

  1. Grounding or Bonding Jetted Bathtub
    By seegee in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 05-21-2012, 06:34 PM
  2. Copper pipe grounding/bonding - how to?
    By Copper Bahamas in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 12-31-2010, 08:56 AM
  3. bonding/grounding copper pipes
    By reed50 in forum Electrical Forum discussion & Blog
    Replies: 32
    Last Post: 11-24-2010, 10:31 AM
  4. bonding/grounding and pex
    By peltaz in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 10-23-2009, 05:39 AM