Dana
Burying a non-IC rated can light fixture in insulation is a code violation, but taping/caulking the holes isn't. The holes in fixtures are for convection cooling, and not a factor in the fire-ratings.
If you're installing a sub-15W LED assembly in there the fire risk is pretty close to zero even without a box-over. But if you have the space, taping up a cardboard box with housewrap tape (for longevity) that provides the code-prescribe 3" clearance, and air-sealing the box to the attic side of the gypsum with gypsum or can-foam would be code-complaint.
On any new fixtures, if they're not fully air-tight at the seams and gasketed it's OK (and desirable) to caulk them to be air tight for both space heating/cooling energy and moisture transfer reasons. A quarter of a square inch of air leakage at into an attic will move more moisture into the attic in winter than 2-sheets of vapor permeation through latex painted 4'x8' gypsum. With a 10W LED assembly in there, multiply that by more than 10 when the light's on. (With a 65W bulb it's much much higher still.) A typical non-air-tight can light will have about a square inch of leakage, even if you caulk the can to the gypsum under the trim (also recommended, even if it's a gasketed unit.)