    Question Pinholes in CU piping

    I had my home re-plumbed about 1988 in copper tubing. Type L was used. It has a circ. pump with expansion tank, check valves, and the WH is outside in a shack. Now that I am remodeling, and re-piping again, I am just curious. I had perhaps 20 pin holes develop and leak, mainly at fittings, from then until now. Anyone else have this/know the causation?

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    The pump was oversized and not throttled down to maintain a "safe" velocity in the piping. The excessive flow created turbulence at the fittings and eroded the tubing adjacent to them causing the leaks. It is a common problem when someone thinks that a "larger" pump will give better circulation.
    Licensed residential and commercial plumber

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,448

    Default

    About the max velocity you want in a pipe is around 5-6 feet/sec, and a recirculations sytem doesn't need to be anywhere near that max.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Interesting. It is the smallest pump I could find. How can I throttle the flow rate down without affecting flow when needed?

    It is a TACO 1/35 HP. Loop is probably around 120' of 3/4" cu on a horizontal plane, excepting the 5' of head for the WH.
    Last edited by big2bird; 09-30-2012 at 07:46 PM.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    You place a valve in the OUTLET pipe from the pump, NOT the inlet", and close it down until it just maintains the temperature in the pipe. 3/4" is much larger than a recirculation line has to be.
    Licensed residential and commercial plumber

  6. #6
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by hj View Post
    You place a valve in the OUTLET pipe from the pump, NOT the inlet", and close it down until it just maintains the temperature in the pipe. 3/4" is much larger than a recirculation line has to be.
    Okay, I installed a gate valve and throttled it down by half. I'll check later to see if it is too/not enough. Thank you.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    DId you put the valve on the outlet? IF not and you throttle the flow down you will destroy the pump. THere just has to be enough flow to maintain some temperature in the return line.
    Licensed residential and commercial plumber

  8. #8
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by hj View Post
    DId you put the valve on the outlet? IF not and you throttle the flow down you will destroy the pump. THere just has to be enough flow to maintain some temperature in the return line.
    Yes. That is where you said to install it.

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    I just wanted to be sure you read it properly. Sometimes all people see is "put in a valve" and then decide to put it in the easiest way, regardless of where they were told to put it, thinking it didn't make any difference, since a "valve is a valve".
    Licensed residential and commercial plumber

Similar Threads

  1. pinholes in copper
    By blacktop37 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 01-24-2009, 03:58 PM
  2. Pinholes in copper vent pipe
    By chel_in_IL in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 24
    Last Post: 11-24-2007, 06:02 PM
  3. Pinholes in copper pipes
    By jimmym in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 19
    Last Post: 12-26-2005, 08:22 AM
  4. pinholes
    By homedfrequentflyer in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 09-23-2005, 06:43 AM
  5. Pinholes in Hot Water Loop
    By 9000cs in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-17-2005, 09:38 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •