Thread: water heater venting water outside from what I think is mixer valve

  1. #1
    DIY Junior Member montags's Avatar
    Join Date
    Sep 2012
    Location
    atlanta
    Posts
    3

    Default water heater venting water outside from what I think is mixer valve

    Hi,

    I have a gas powered water heater tank that is continually leaking hot water outside via what I think is an overfill pipe. Having looked at diagrams online, I think it is coming from what is called the mixer valve (please see photos below). I originally thought it was coming from the pressure relief valve (PRV), but that is a separate plastic pipe and is not leaking. Note that I have two vent pipes to outside, one from the PRV and a second from this "mixer valve" thing.

    I did test the pressure relief valve and it seems to be working fine. Flows when I open it and stops when closed. When I do operate the PRV, the venting of water from the "mixer valve" stops for a minute then starts dripping again. It is a vigorous drip, maybe a few gallons per day. We have no complaints about the volume or temperature of our hot water.

    The water heater is 13 years old and despite having the manual, I do not know what manufacturer it is. There is no ID on the manual, not even a name. We live in a soft water area and this heater is the original install on 1999 house. Note that there is a continual ssshhhh sound like a faucet is running and it is coming from this valve.

    I was hoping it was an issue with the PRV and maybe it is - I know little about water heaters.

    Thanks for any help.

    http://mcontact.bestmail.us/DSC_0475_new.jpg

    http://mcontact.bestmail.us/DSC_0471_new.jpg

    http://mcontact.bestmail.us/DSC_0474_new.jpg

    Valve in question:
    http://mcontact.bestmail.us/DSC_0478_new.jpg

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    The valve on the side tank is a T&P valve - the fact you can open it is no perfect indication that it's good.

    A mixing valve would require both the hot and cold to connect to it (it's called a tempering valve). I'm not sure, but I think it's a pressure relief valve (again, not a PRV). It could be defective, or could be doing its thing...it would normally be set lower than when the T&P opens. If you have an expansion tank, it could be shot. The city could have raised the supply pressure (new pump, or new water tower, for example).
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member montags's Avatar
    Join Date
    Sep 2012
    Location
    atlanta
    Posts
    3

    Default

    Thank you Jim. Those are all good, well thought out points. I can see you are an engineer, so that makes sense. I think you are right, it is a pressure relief valve. I am in two minds about just replacing it because as you hinted, there could be other problems and it's just a symptom.
    Last edited by montags; 09-30-2012 at 08:26 PM. Reason: missing word

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    I would investigate WHY someone, at some point, thought it necessary to install a seconday pressure relief valve. Check you system pressure both static ( no water running) and dynamic ( a faucet open)

  5. #5
    DIY Junior Member montags's Avatar
    Join Date
    Sep 2012
    Location
    atlanta
    Posts
    3

    Default

    Quote Originally Posted by jimbo View Post
    I would investigate WHY someone, at some point, thought it necessary to install a seconday pressure relief valve. Check you system pressure both static ( no water running) and dynamic ( a faucet open)
    Thanks Jimbo. Good points. I'll raise this when the plumber is looking at it.

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,192
    Blog Entries
    1

    Default

    It looks to be an extra valve there.
    Some areas required a relief line on the main piping, and none on the water heater. A dumb idea maybe, but that's what some inspectors wanted. Some were done because there was no way to drain a relief off the heater. We could position the relief high enough to get a good gravity drainage off the relief. Since the T&P is being drained outside, it would seem that the one higher up could be deleted.

Similar Threads

  1. Fuel Oil Water Heater Venting
    By Kielanders in forum Water Heater Forum, Tanks
    Replies: 0
    Last Post: 08-22-2011, 08:01 PM
  2. PVC venting for tankless water heater
    By RinconVTR in forum Tankless Water Heater Forum
    Replies: 4
    Last Post: 11-12-2010, 06:36 AM
  3. question on water heater venting (orphaned water heater)
    By harveymasons in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 08-23-2010, 06:11 AM
  4. Venting a gas water heater
    By zenn068 in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 08-02-2008, 09:43 AM
  5. water heater venting
    By perrycat in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 08-14-2007, 07:07 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •