    Default <8" Rough-in!?

    Needed to replace my toilet because the bolts that hold the tank to the bowl were corroded (cheap toilet and really hard water). However, when I measured the rough-in it was exactly 9". Knowing this was off, I decided to pull the toilet before I went to purchase a new one. Once I did, I found the scene pictured below -- even worse than I thought. An offset flange is already in place. The actual pipe center is less than 8" from the back wall and off-center to the right (12" from the right wall in the photo, 20" from the left).

    What do I do now? Call a plumber? Are they going to have to tear up my foundation to make this right so I can have a normal toilet that mounts correctly?
    Name:  IMG_2780s.jpg
Views: 319
Size:  30.2 KB
    Name:  IMG_2781s.jpg
Views: 285
Size:  50.6 KB
    Last edited by Rick Routh; 08-04-2012 at 06:09 PM.

  2. #2
    DIY Senior Member wjcandee's Avatar
    Join Date
    Apr 2012
    Location
    New York, NY
    Posts
    1,589

    Default

    Am I correct that the tank was sitting against the wall with the water supply sticking out of it?

    I don't know if this is viable or not, but let me mention this: The 12" rough-in Drake actually has 1-1/8" behind it, so you can get it in on an 11" rough-in, and, usually, on 10 7/8. This despite the fact that some of the spec sheets say 3/4" behind, and some say 1-1/8".

    The spec sheet for the 10" rough-in Drake says 3/4" behind. If, in fact, it has the full 1-1/8" that the regular Drake does, then you could get it in on a 9" rough-in. I just don't know the answer, though. Maybe someone who knows can champion or bludgeon my idea.

    You can get the Drake in with the water supply only a smidge to the left of center, but that looks maybe too tight; I'm thinking that you may need a 90 out of the wall. Certainly if the Drake idea is viable, we can measure and figure out the rest.

    The Drake is 19.5" wide, so you've got 2-1/4" on the one side. It'll fit; maybe not the most comfortable. I don't know about where you are but code is usually 15" from finished wall to center; I'm assuming this isn't somewhere where it needs to be inspected?

    EDIT: I guess I should point out that, as Jim notes below, the right (and, depending upon where you are probably the legal) thing to do is move the drain. My thought was "Poor guy, pulls up toilet and discovers horror. Maybe this could give him a quick and admittedly-dirty solution." What Jim says is correct, of course. Sorry you couldn't just reattach your tank with a decent set of tank-to-bowl hardware.
    Last edited by wjcandee; 08-04-2012 at 07:40 PM.

  3. #3

    Default

    Yes, You need a plumber

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    Okay, look at it this way...code says you need a minimum of 15" from the midline of the toilet to each wall, so given that and the fact you have a non-standard rough-in, you really should move the toilet flange. Now, depending on which way the drain line runs, you might not need to tear up too much. Unless this is a post-tensioned slab (more common in earthquake country), cutting a slab isn't normally as big a deal as most people think.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    In my opinion, the is not a DIY friendly job, especially for a novice. Off set flanges are junk and should never be used. Just because they are made and sold does not mean they are an acceptable fitting. As others have pointed out, there are some factors that we can not see and perhaps can not be seen until more demo is done. Again, in my opinion, a plumber, while not cheap, will likely be the least expensive way to get this done right. Lots of ways to do things wrong, usually only one or two ways to do it right.

  6. #6
    DIY Junior Member Rick Routh's Avatar
    Join Date
    Aug 2012
    Location
    Texas
    Posts
    10

    Default

    wjcandee,
    You are correct that the tank sits against the wall with the supply line. And the old (child-sized) toilet sat AGAINST the wall (the reason the rest of the wall is painted is because you literally could not touch the white part with a brush).

    Jim,
    I want to actually fix the problem, not just cover it up (again). The house is certainly not a post-tensioned slab. Built in the mid-90s in North Texas, they cut every corner possible. Every time I touch something I find that not only was it not done well, it was hardly done at all (no matter what "it" is).

    I had talked to a friend who suggested the offset flange route when we were discussing the 9" rough-in. At that point I was comfortable with widening the slab enough to get the extra clearance. But for this I'm looking at opening the slab AND new sewage plumbing, right?

    Another thought I just had was moving the wall(s)? Behind the wall to the left is the main intake for the AC which is extremely large (I can comfortably hang out in there, I think some of it was supposed to be closet space for the next room in the original blueprints). Behind the wall straight back (with the supply) is a hall closet which isn't used. And behind the wall to the right is a hollowed out area for a massive old-school entertainment center. We could easily ditch the ancient entertainment center, I just don't know what I'd be looking at as far as plumbing in that wall since the shower butts up against it.

    I've put in a call to the only local plumber I trust, but I'd like to do as much of this as I (legally) can.


    As an aside: I don't know how many of you are plumbers, but kudos to you. I grew up having to learn how to fix stuff that broke because we never had the money to pay someone else to do it, but of everything I can fix plumbing is the one thing that I just cannot find a way to enjoy. (I was also the kid who wouldn't play with finger paints, but have no problem swimming in transmission fluid, go figure.) So when it really hits the fan (like this) I am SO grateful that there are people who truly have a passion for it. To those of you who do, THANK YOU!

  7. #7
    DIY Senior Member wjcandee's Avatar
    Join Date
    Apr 2012
    Location
    New York, NY
    Posts
    1,589

    Default

    Rick: I'm one of those who is not a plumber. Spent a lot of time in apartment buildings as a young professional, and you called maintenance to fix stuff. So it was embarrassingly-recently that I learned how to fix a leaky toilet. I'm trying to make up for lots of lost time. But here's a story: I spent almost ten years in Dallas and Irving. Had a friend who coincidentally lived in my apartment building. Blonde, tan, fit, good-lookin'. Executive at a very popular nightclub. The kind of woman that where I'm from (NY): (a) would not be very nice and (b) would expect others to look after her. My friend was refreshingly not that way. She had me over one day. I realized that we had basically the same apartment. Except she had a ceiling fan, a really-nice chandelier in the dining area and a dimmer. "How'd you get them to put in a dimmer?" I asked. She looked at me like I was from Pluto. Or New York. "Sorry?" "The dimmer. I don't have one. Or a ceiling fan or a chandelier. I didn't know they'd do that for us." Long pause. "William, just 'cause I'm a girl doesn't mean I don't know how to do electrical." She was from East Texas. Of course she knew how to do electrical. And fix cars. And all the names of all the Cowboys. And which ones needed to be traded. Naturally, I was charmed.
    Last edited by wjcandee; 08-04-2012 at 08:52 PM.

  8. #8
    DIY Junior Member Rick Routh's Avatar
    Join Date
    Aug 2012
    Location
    Texas
    Posts
    10

    Default

    Haha! Yeah, I spent my summers growing up in a small town in western Nebraska. Not only did you learn how to fix stuff, you learned how to do it with whatever scraps you could find. There was a five-and-dime in town, but anything more specific than that was 19 miles away. I admit I have looked at people funny when they've complained about something like a toilet handle being broken. "Why don't you just fix it?" "You can DO that!?" Good times.

    Back on topic: And I don't mind if the answer is "wait for the plumber," but is there anything further that I can do to reduce my expense at this point? Should I go ahead and remove the offset flange and see which direction the drain line runs?

  9. #9
    DIY Senior Member wjcandee's Avatar
    Join Date
    Apr 2012
    Location
    New York, NY
    Posts
    1,589

    Default

    Good times, indeed!

    As to what you can do, I'm to a big extent not the person to ask, but I do remember seeing a few posts on here from the most experienced of the plumbers, that advised folks they were counseling not to "help" the plumber by, IIRC, pulling out the old flange, etc. It seemed like they wanted to see the old setup in all its demented glory, and perhaps feared removal of stuff that they might have wanted to keep. Assuming the guy you called is going to come over and give you an estimate before just getting down to work, I'm thinking he's the best guy to ask about that. But naturally I defer to the people that really know.

    When I first saw your photos, I actually thought, "Wonder what's on the other side of those walls." If the toilet is centered in that space, is it comfortable and inviting? Do you figure that on balance, it's not worth starting to rip out walls at this point?

  10. #10
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    As I noted, code requires at least 15" to either side of the toilet, and to make life easier for you, you want the flange 12" from the finished all. Now, if you can easily move the walls, and can do that yourself, that may end up less expensive than moving the flange. But, if you don't want to go to that effort, go for a plumber. An offset flange often isn't your friend, either so getting one that goes straight has advantages, too.

    When you look down the pipe, how far down does it go before it turns? Normally, you can see that and which direction it turns. If the turn is quite high or goes back towards the wall, you may need to tear up the wall to replace the flange. And, if it makes a turn immediately beneath the floor, depending on which way it turns, to maintain the proper slope, you may have problems. Drains really don't like to go uphill or even flat...they should slope down all the way out.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #11
    DIY Junior Member Rick Routh's Avatar
    Join Date
    Aug 2012
    Location
    Texas
    Posts
    10

    Default

    Quote Originally Posted by jadnashua View Post
    As I noted, code requires at least 15" to either side of the toilet, and to make life easier for you, you want the flange 12" from the finished all. Now, if you can easily move the walls, and can do that yourself, that may end up less expensive than moving the flange. But, if you don't want to go to that effort, go for a plumber. An offset flange often isn't your friend, either so getting one that goes straight has advantages, too.

    When you look down the pipe, how far down does it go before it turns? Normally, you can see that and which direction it turns. If the turn is quite high or goes back towards the wall, you may need to tear up the wall to replace the flange. And, if it makes a turn immediately beneath the floor, depending on which way it turns, to maintain the proper slope, you may have problems. Drains really don't like to go uphill or even flat...they should slope down all the way out.
    It goes down 12-18" (I think closer to 12, but it's hard to tell looking down through the gap between the drain and the offset flange) then turns directly toward the back right corner. I'm assuming it's heading toward the kitchen then down to the street. We live on the corner and that direction is the busier of the two streets. Since I want the toilet forward and right, am I looking at tearing up the slab, extending the current horizontal (I'm assuming slightly slanted toward the street) pipe then a new 90* and flange. That doesn't seem so bad. I'm assuming legally the plumber has to be the one to connect the pipes (I know legally only licensed irrigation techs can replace sprinkler heads in my town). As such I will still wait for my plumber before proceeding, but I think I'm feeling a little better about this after seeing the pipe seems to go the right direction down there.

  12. #12
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    I was worried that the pipe might be just beneath the slab, and that would mean extending it might bring it too high to easily make a connection. Sounds like that's not an issue. There's a limit on how many degrees the line can turn before a cleanout is required, but it sounds like that won't be an issue.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  13. #13
    DIY Junior Member Rick Routh's Avatar
    Join Date
    Aug 2012
    Location
    Texas
    Posts
    10

    Default

    Plumber is coming first thing Wednesday morning to take a look at the situation. Will update as soon as he gives his opinion.

  14. #14
    DIY Junior Member Rick Routh's Avatar
    Join Date
    Aug 2012
    Location
    Texas
    Posts
    10

    Default

    So the plumber gave me a quote to move the drain AND inlet (and in doing so also update the valve and change spiral hose to braided) which was within what I was hoping for AFTER I did some of the labor. So they did the jackhammering and plumbing.

    Name:  IMG_2794 (Medium).jpg
Views: 236
Size:  54.7 KBName:  IMG_2795 (Medium).jpg
Views: 236
Size:  72.7 KBName:  IMG_2796 (Medium).jpg
Views: 235
Size:  58.0 KBName:  IMG_2798 (Medium).jpg
Views: 240
Size:  71.6 KBName:  IMG_2799 (Medium).jpg
Views: 231
Size:  38.6 KB

    So then I had a patch of wet concrete, a third of the floor cut out, and access to the back wall. So my original valve replacement has now turned into...

  15. #15
    DIY Junior Member Rick Routh's Avatar
    Join Date
    Aug 2012
    Location
    Texas
    Posts
    10

    Default

    Name:  IMG_2801 (Medium).JPG
Views: 244
Size:  43.3 KBName:  IMG_2800 (Medium).JPG
Views: 234
Size:  44.9 KBName:  IMG_2803 (Medium).JPG
Views: 238
Size:  46.1 KB

    Mismatched paint (some flat, some textured, some faux finish), nasty 20-year old laminate sheet floor? Now's the time to change that!

    Name:  IMG_2807 (Medium).JPG
Views: 254
Size:  42.1 KBName:  IMG_2808 (Medium).JPG
Views: 233
Size:  52.0 KB

    The new yellow. Didn't look so... yellow when we picked it up, but I'm hoping the darker laminate tile and a dark-ish shower curtain will help tone it down. At this point we're in it to win it, and it will be easier to paint over this than the dark blue that was in here. 2nd coat and corners/edges are today, clean up the floor and put leveller down tonight, then I'll put the tiles down tomorrow night. Should have a toilet in by Friday! (You guys won't be happy with my toilet choice, but this project is already WAY overbudget from the original $20, so I'll omit details regarding the final purchase if you will forgive me and have some sympathy.)

Similar Threads

  1. Toto Aquia 10" rough - will it work with 10 7/8" CST412MF.10
    By bronsonb in forum Toilet Forum discussions
    Replies: 12
    Last Post: 01-18-2014, 09:13 PM
  2. 11 1/4" Toilet Rough-In: 10", 12", or custom order?
    By TJMagee in forum Toilet Forum discussions
    Replies: 13
    Last Post: 01-19-2011, 08:02 PM
  3. Best flushing toilet for 10" rough-in? TOTO 10" Drake
    By catorgs in forum Toilet Forum discussions
    Replies: 15
    Last Post: 11-01-2010, 12:12 AM
  4. Toto Ultramax 12" rough-in, but sits 2" out from the wall
    By pottynovice in forum Toilet Forum discussions
    Replies: 0
    Last Post: 10-24-2010, 02:18 PM
  5. Replies: 5
    Last Post: 09-18-2009, 06:58 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •