Ok so here is the story, the wife wanted a sink next to the washer.

So i did a rough-in and she ran the washer and once i got a little water backup (about 1 cup) into the sink drain.

Is this done correctly or what would you guys change?

I know it should be a 2'' abs tube but its a 1 1/2'' and everything was fine till i added sink.

I am thinking its because the drain for the sink is below the washer , but the reason i did it that way is cause if not the drain would be too high (18'' +) for the sink.

Any ideas ?

BTW where you see the orange wire it leads to a AAV and main drain is coming from the right side.

Thanks in advance !! wdrain.jpgwasherdrain.jpg
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If the connection to the sink was a wye rather than a sanitary T, it might work better. Or, maybe a double-wye to keep the overall length down. Wait for a pro to comment, as I probably am missing something...
 

Phantomvs

New Member
Messages
24
Reaction score
0
Points
1
Location
Quebec
You see my main problem is that i need to keep the height down.

If i put the sink above washer it will be too high. How can i have both on the main branch without raising sink level.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
Instead of trying to wet vent a washer over a sink, (which would never be allowed in any plumbing code, even if it had been run in 2")
Cut in a wye for the washer to the right, go up to a "Santee" for the trap arm.
For the sink, continue on from the wye horizontal and use a combo fitting for the vent on the trap arm. Now the two vents, the washer vent and the sink vent can tie together at 42" above the floor.

Running a washer past a sink drain is a problem.

Wet venting can only be done on bathroom groups.

Wet venting requires 2" or larger piping.

A wye fitting on the vertical on a trap arm, is an "S" vent. It will siphon the trap. A Santee should be on the vertical for a traparm.
 
Last edited:

Phantomvs

New Member
Messages
24
Reaction score
0
Points
1
Location
Quebec
Thanks Terry for the help.

Just 1 question, when you say the washer and sink vent can tie together do you mean i use only 1 vent (AAV) or tie together with no vent or double vent ?

Thanks !

Matt
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
A vent is always required.
You can tie vents together and use one AAV as long as you have an atmospheric vent somewhere on the system.
 