  1. #16
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,644

    Default

    Quote Originally Posted by chefwong View Post
    NO.
    Doubling up, does not make it *half* the wire rating.
    Just don't do it often enough to know.
    Found the answer - Two 14's = 11 AWG
    I thought you were talking about size ?

    Jim is correct it is double in size.

    The size of stranded wire is different than solid.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  2. #17
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by chefwong View Post
    Just making fancy speaker connections with my WBT crimp sleeves....

    Don't start the bare copper vs. connector debate ;-/
    Why would you want to parallel conductors for speakers? This is a very bad idea due to the resistance of the conductors that will have an effect on the amp.

    I always use stranded conductors for speakers due to eddie currents and would never for any reason install parallel conductors for any type of sound system.

    What size amp are you using? It must be big in order to use #14 AWG conductors.

  3. #18
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,259

    Default

    One may notice from that code quote on big conductors that a 50% increase in size brings only a 15% increase in conductivity. Is this the flow of electrons on the perimeter of the cable factor?

    Seems like the parallel cables would give more heat dispersing area...

  4. #19
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,644

    Default

    Quote Originally Posted by ballvalve View Post
    One may notice from that code quote on big conductors that a 50% increase in size brings only a 15% increase in conductivity. Is this the flow of electrons on the perimeter of the cable factor?

    Seems like the parallel cables would give more heat dispersing area...

    In theory X 2 or 100% increase would give the wire 1/2 of the resistance and 1/2 of the voltage drop for the same length wire run.

    1/2 of the voltage drop would produce less heat, but there are a lot of other factors that affect wire temperature.

    When it comes to Audio and Paralleling speaker wires, Phasing is important.

    1 speaker can cancel the sound of another if not properly phased.


    I guess chefwong is hanging speakers with this wire, as he said "This is not for electrical....."
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #20
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by ballvalve View Post
    For a guy with several miles of #6 and #10 wire, "doubling up" seems like a great use of material. I have done it on some wild mountain runs, and all works fine. Without any code babble, can you explain the practical danger inherent in parallel wires?
    When you use multiple runs to increase conductance, you must insure the impedence (total opposition to a/c current) is virtually identical. If they are not, you risk the overloading of the conductor with the least opposition to current flow.
    Therefore, a run of 1/0 minimum, identical length, identical connections is the minimum. It would be too difficult and unnecessary to ever do that for smaller circuits.
    When you get into kiloamps, it becomes necessary, as no practical cable is manufactured or easily installed.
    There are exceptions for voltage drop, such as high frequency applications, but the ampacity cannot be summed. I.E., you could parallel 14 gauge wire on a 400 cycle circuit to lower voltage drop, but it is still rated at 15 amperes maximum.
    I can rattle off more, or quote the exceptions if interested.

  6. #21
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by ballvalve View Post
    One may notice from that code quote on big conductors that a 50% increase in size brings only a 15% increase in conductivity. Is this the flow of electrons on the perimeter of the cable factor?

    Seems like the parallel cables would give more heat dispersing area...
    Skin effect has some factor. Basic rule of thumb. Copper is good for 1,000 amperes per 1" square cross section. Aluminum is 700 amperes per 1" cross section.

Similar Threads

  1. Converting to double sink-drain pipe too close to stud for double fixture fitting.
    By Finch85 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 04-11-2012, 06:04 PM
  2. Double Sink double dishwasher garbage disposal dilemma
    By Pettytalk in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-12-2012, 05:04 AM
  3. Wire gauge for new double-oven?
    By Artie in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 11-11-2010, 07:51 AM
  4. Double oven and cooktop wiring - connecting three #6 wires
    By jhodgens in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 11-06-2010, 02:19 PM
  5. Can someone double check my wiring diagram?
    By dizzo72 in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 04-11-2010, 11:14 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •