The 2011 cycle states that two rods must be installed unless the electrical contractor hires a Professional Engineer to perform the test.
The clamp on testers only read the ground loop between the grounding electrode on the premises wiring and the supplying transformer grounding electrode. This is not earth resistance.
I have been in the electrical field for more than 44 years and have never known an electrical inspector to perform any type of electrical test especially on the grounding system. The resistance of the grounding electrode will vary with weather conditions so a test done today will be different than one done tomorrow.
As an electrical inspector for NC should I come out and see only one rod at any location then the electrical contractor will have to produce a written report from a Professional Engineer and I will not accept the results of only one test.
EDITED TO ADD;
Here is the only test that counts
http://www.esgroundingsolutions.com/...tance-test.php