    Backround:
    100 year old house with 90% new / newer wiring, New panel installed 18months ago, service and meter and weather head from ~60's.

    About a month ago i noticed some of my lights flickering. I shrugged it off until i saw it happening more consistently. The circuits i was seeing the flickering on were both old and new. I went outside and my meter base is looking a bit weathered and it is rusting at the bottom. I then popped the cover off my panel.

    As you can see the electrician used these splices. The red one seems to have failed or at least the outer insulation has failed. The circuits that are flickering are on this leg.

    My questions are:
    1) what kind of splice is this?
    2) why did it fail?
    3) At 18 months out should i expect a warrante repair?

    Thanks
    markName:  DSC00917.jpg
Views: 253
Size:  84.5 KB

  2. #2
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    272

    Default

    I would call it an insulated, compression, butt splice. It is a legitimate way to splice wires.

    What went wrong? I don't know. I can't tell from the photo. It does look like a bad splice and needs to be fixed and soon.

    Warranty? Unless you are upset with whomever did the work I would him first. If he is a stand-up guy and made a goof he will fix it. If the problem is caused by something not related to the work he did then their will be another charge. If you decide to call someone else then find an electrician with good references, get it fixed, write the cheque, and move on.

  3. #3
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    922

    Default

    WHY in the world they have changed the panel and leave a '60's vintage service entrance????

  4. #4
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Hack job. You do not splice in a panel.

  5. #5
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by Speedy Petey View Post
    WHY in the world they have changed the panel and leave a '60's vintage service entrance????
    Agreed. The best way would have been to rewire the whole house at once. I sense the entire house is full of skeletons such as this. Expensive, but a good piece of mind. When I see something like this that is visible, I get very concerned about the hidden you cannot see.

  6. #6
    DIY Junior Member mhmmofro's Avatar
    Join Date
    Sep 2011
    Location
    staten island
    Posts
    14

    Default

    Thanks for the answers guys. I left it original to the panel to save money and because the sparkies who checked it out told me i would be fine for at least 10 years. In terms of the splice in the panel i was told it was fine I dunno. Clearly you can see why one would not want a splice in the line - crap like this happens.

  7. #7
    DIY Junior Member mhmmofro's Avatar
    Join Date
    Sep 2011
    Location
    staten island
    Posts
    14

    Default

    The guy who did the work is supposed to come check it out on Monday. Could poor balancing of the phases cause this? I mean could having to many high current items on this phase cause the splice to fail even if it was installed correctly?

  8. #8
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    287

    Default

    Quote Originally Posted by mhmmofro View Post
    Could poor balancing of the phases cause this? I mean could having to many high current items on this phase cause the splice to fail even if it was installed correctly?
    That should not be a valid cause, if the crimp was rated.

    Assume it is a 100 amp service. This cable should be able to pass 100 amp without trouble. The crimp likewise.

    And the main breaker should trip if this leg of the service sees more than 100 amp for more than a moment or two. The crimp should endure that without issue.

    I doubt that you stressed the one side so much more than the other that you cooked this crimp.

    I think the crimp was just not executed well enough, and is of itself a point of resistance, at probably half the amperage that the panel is rated to.

Similar Threads

  1. Flickering lights on circuit with low voltage and line voltage bulbs
    By davidwie in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 04-18-2011, 07:34 AM
  2. New splice fitting
    By thezster in forum Plumbing Forum Discussion & Blog
    Replies: 1
    Last Post: 02-15-2009, 04:59 PM
  3. Connecting a 3/0 Splice
    By JoeyC in forum Electrical Forum discussion & Blog
    Replies: 21
    Last Post: 12-31-2008, 07:36 AM
  4. Flickering lights
    By jparrie in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 11-19-2008, 12:22 PM
  5. Splice sprinkler cable?
    By mntentman in forum Irrigation / Sprinkler Forum
    Replies: 5
    Last Post: 08-04-2008, 06:35 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •