    Default Can anyone explain to me why a shower requires a 2" waste?

    I'm converting an OLD bathroom (cast iron claw foot tub - original) to a shower enclosure and find the waste line is 1 1/2". It's well vented, but, looking at the code, a Shower requires a 2" waste even though it's only rated at 2 DFUs. Can someone please explain this to me?

    To me, the shower has FAR less flow than a full bathtub with the plug pulled (especially given low flow rate shower heads). Why on earth does it require a 2" drain???

    Tom

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,146

    Default

    In Canada, a 1-1/2 is still ok.

    I see a lot of new showers with 6-10 spray heads.

    Low flow- HA!

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Most codes in the US like to see a 2" shower drain.
    Until the 50's, we used 1.5" for showers. I don't think it's a big deal either way. If I'm retrofitting a shower where a tub used to be, I go ahead and use the 1.5" waste line. If I can bump it to 2" easily, I do.

    New work, 2" every time.

  4. #4
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,968
    Blog Entries
    5

    Default

    I think in many cases a 1 1/2" drain line is fine. The size of the drain line is only one factor in the amount of water a shower's drain can handle.

    Weither or not the water drops straight down or slides out at an angle can affect flow rates.

    Also the shear drop into the drain as well.

    For Example:

    A 1 1/2" drain line with 7" off free fall will drain faster than a 1 1/2" drain that has 4" of fall and angles off at a 45 degree angle.

    I have measured in the field slower flow rates when fittings are slightly out of wack. My thought here is that little eddies are created slowing the flow or choking the air these drains need.

    Before getting to committed to your new drain line do a dry run. Test the drain and see if it can handle the flow rates. You do not want to start tiling and find out that the shower's drain is undersized.

    I have some of my favourite drains listed here in an Idea Book.

    http://www.houzz.com/ideabooks/36507...or-Your-Shower

    JW


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    A tub has an overflow, a shower has the curb and it flows out onto the floor. Plug the drain by dropping the washcloth over it, or standing on it, and the level could rise a bit before a big mess...a bigger drain can resolve the issue better. Cross section is 1.5^2 verses 2^2 or 4/2.25 the 2" drain is 1.77 times bigger...not inconsequential.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    You can fill the tub with water and let it drain as fast as it can. If it does not drain as fast as the shower fills it, then you shower in a pool of water. With a shower stall, you CANNOT fill it very much, and if it does not drain fast enough it will overflow onto the floor. THAT is the reason for a 2" drain, regardless of what the FU, (which is an arbitrary number with no relationship to the flow of the shower head), rating is.
    Licensed residential and commercial plumber

  7. #7

    Default

    Great info John . To summarize it " It isn't the size of Your drain, but how You use it " GOT IT !

  8. #8
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,968
    Blog Entries
    5

    Default

    Quote Originally Posted by Boston1 View Post
    Great info John . To summarize it " It isn't the size of Your drain, but how You use it " GOT IT !
    Boston1 I wish I had more data for you on this. This info was shared to me by one of my drain suppliers as he was skirting the issue for why his drain was air locking. I went home and tried to see if the drain would lock but could not create the same environment.

    I did find that the water level was higher in my clients home (where the 1 1/2" line angles off) vs my home's (my wife's laundry room aka mad lab) mock up.

    Often the 1 1/2" lines we work on are in condo's - there we have sometimes 7" - 10" of free fall before the P-Trap. Never once a problem with flow rates here.

    In the residential homes where we are building curbless showers often the free fall is 4" (2"x10" framing) and here you need to be very careful.

    I have started measuring this as we build and then going back and measure water flow with a timer and 5 gallon bucket. Hopefully in time some kind of useful formula shows it's self.

    In renovations that have multiple shower heads you really need to see how much water they can produce. When we pressure test the lines I ask my plumber to hook up two hose bibs and we simply fill a bucket. If the flow rate is in excess on 6-7 GPM then we send the water down the drain. Anything more than that should have a 2" line.

    All the new fixtures have restrictors build in so most times it is a non issue. But rumour has it clients hate these and call the plumber back to rip them out.

    JW
    Last edited by johnfrwhipple; 09-03-2012 at 08:46 AM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

Similar Threads

  1. Can someone suggest a good shower valve and explain pressure balance vs thermostatic
    By shadysprings in forum Shower & bathtub Forum & Blog
    Replies: 12
    Last Post: 04-23-2013, 11:27 AM
  2. Shower valve requires?
    By ditttohead in forum Plumbing Code Questions
    Replies: 11
    Last Post: 03-19-2012, 12:39 PM
  3. 1/2" Copper waste pipe in shower - how to cut??
    By cashman in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 01-16-2009, 07:51 PM
  4. turning off water requires careful "tuning" of the faucet
    By mckern in forum Shower & bathtub Forum & Blog
    Replies: 8
    Last Post: 11-24-2008, 05:38 PM
  5. 2" Waste and Overflow for shower/footbath?
    By mightyperl in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 10-12-2006, 08:39 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •