Thread: Backflow Valve Advice

  1. #16
    DIY Junior Member danny60632's Avatar
    Join Date
    Aug 2012
    Location
    Chicago, Il
    Posts
    7

    Default

    Update:

    Thanks to everyone that helped me out with my issue. There in fact was a Backflow valve which was deteriorated and stuck partially open. I was able to find the exact 6" cast iron valve and finally installed it 2 weeks ago. Just in time too because of all the flooding that the storms caused last week here in Illinois. All I have to do is install the new sump pump which I will do on my next day off.

  2. #17
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    Sorry I have not been around much. The backflow valve is right under the cover the 2" pipe ties into. This cover needs to be opened and the flapper serviced every year to ensure proper operation. The open pipe is an over flow tee, which is on the house side of the backflow valve. When the city sewer backs up and closes the flapper your water usage from the house over flows from the tee into the pump pit. The pump then pumps this water into the closed side of the valve. During the yearly service check to ensure the pump is working properly as well.

  3. #18
    DIY Junior Member danny60632's Avatar
    Join Date
    Aug 2012
    Location
    Chicago, Il
    Posts
    7

    Default

    Thanks! I did read some of your previous posts concerning these types of valves. Your posts were extremely helpful. It looks like the previous owner never did any maintenance at all, the flapper was detoriorated and stuck open, the screws were so brittle that they snapped off when i tried to clean them. Thanks again!

Similar Threads

  1. backflow valve but still flooding
    By s1156780 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 04-30-2012, 06:07 AM
  2. backflow/check valve code
    By benniebeeker in forum Illinois Plumbing Code Questions
    Replies: 9
    Last Post: 09-19-2011, 10:52 AM
  3. Backflow valve on water supply for cleanout
    By Cellomangler in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 11-18-2008, 06:19 AM
  4. how to retro fit an anti backflow valve?
    By Mrikert in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 05-29-2008, 06:23 PM
  5. Is a check valve sufficient for backflow prevention?
    By gonif in forum Irrigation / Sprinkler Forum
    Replies: 15
    Last Post: 07-08-2007, 09:09 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •