    Default Toilet Drain/Joist Clearance

    Is there a minimum clearance requirement between a joist and a toilet drain opening? I read something about, I think, 3" from the center of the drain to a joist. I'd like to sister the bad joist in the attached pic. If my calculations are correct, doing this will leave me about 1/2" from the edge of a properly-centered 5" drain hole in the subfloor to the new sister.

    Thanks.
    Attached Images Attached Images  

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,403

    Default

    From a practical viewpoint, most toilet flanges are a cone, so they flare out from the pipe. Thus, if the joist was right next to the pipe, you may not be able to slide the flange on while gluing it in place - at least you may not be able to slide it all the way in. Now, this is often more of an issue with a 3" pipe than a 4" pipe where you could use an internal flange.

    Don't know if there's an actual code issue here, but more of a practical issue on what will fit.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I don't see much joist left in that photo, I hope it wasn't you who went crazy with a sawzall.

  4. #4
    DIY Member diydude's Avatar
    Join Date
    Jul 2012
    Location
    Seattle,WA
    Posts
    62

    Default

    Quote Originally Posted by dlarrivee View Post
    I don't see much joist left in that photo, I hope it wasn't you who went crazy with a sawzall.
    No, it wasn't me who hacked together that mess. I just happen to be the beneficiary . I've since corrected that issue: Name:  Floor 005.jpg
Views: 229
Size:  83.9 KB

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    I would pull the shutoffs at this time and stub out copper.

    You should go with a new pressure balance valve for the tub there.
    There is a drain for one in the corner, right?
    You will need space for the waste and overflow that will be lower than the floor there. Looks kind of tight right now. Normally the drain is about 10" from the wall at the end.

    I will say the framing looks new and solid.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default joists

    I would say that "triple" joists are an "overkill".
    Licensed residential and commercial plumber

  7. #7
    DIY Member jadziedzic's Avatar
    Join Date
    Aug 2006
    Location
    New Hampshire
    Posts
    86

    Default

    I don't know about your jurisdiction, but here they would require EITHER some of the foam "gasket" material between the new joists and the concrete (or block) wall, OR have the new joists rest on a pressure-treated plate. It's generally frowned upon to have non-pressure treated wood in direct contact with concrete.

  8. #8
    DIY Member diydude's Avatar
    Join Date
    Jul 2012
    Location
    Seattle,WA
    Posts
    62

    Default

    Quote Originally Posted by jadziedzic View Post
    I don't know about your jurisdiction, but here they would require EITHER some of the foam "gasket" material between the new joists and the concrete (or block) wall, OR have the new joists rest on a pressure-treated plate. It's generally frowned upon to have non-pressure treated wood in direct contact with concrete.
    I have building paper under the joists; it's not easy to see in the picture. I confirmed with the city that this is ok.

  9. #9
    DIY Member diydude's Avatar
    Join Date
    Jul 2012
    Location
    Seattle,WA
    Posts
    62

    Default

    Quote Originally Posted by hj View Post
    I would say that "triple" joists are an "overkill".
    Thanks Seriously, I wanted to flatten the floor from below before I attached the subfloor, so I added a second sister to the second joist from the wall to make the joist heights even across the floor. The first joist nearest the wall was an absolute mess, so I patched it and sistered on both sides.

    Quote Originally Posted by jadziedzic View Post
    I don't know about your jurisdiction, but here they would require EITHER some of the foam "gasket" material between the new joists and the concrete (or block) wall, OR have the new joists rest on a pressure-treated plate. It's generally frowned upon to have non-pressure treated wood in direct contact with concrete.
    I have building paper under the joists now. I confirmed with the city that this is ok. I got a lecture about that when I took some pictures to City Hall to ask about boxing in the drain. Is that a newer code standard? Most or all of the floor joists on the first floor are resting on the foundation. The house was built in 1976.

    Quote Originally Posted by Terry View Post
    I would pull the shutoffs at this time and stub out copper.

    You should go with a new pressure balance valve for the tub there.
    There is a drain for one in the corner, right?
    You will need space for the waste and overflow that will be lower than the floor there. Looks kind of tight right now. Normally the drain is about 10" from the wall at the end.

    I will say the framing looks new and solid.
    Sorry, the picture doesn't show that I'm actually boxing in the tub drain. I'll have to read up on pressure balance valves. Thanks for the suggestion.
    Last edited by diydude; 05-27-2013 at 10:25 AM.

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    quote; I'll have to read up on pressure balance valves Not really, because that is probably the only thing you will be able to find for your installation.
    Licensed residential and commercial plumber

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,403

    Default

    For a number of years, ALL legal shower valves sold in the USA have anti-scald technology. The most common way to do this is with a pressure balance valve although some thermostatically controlled valves are fast reacting enough to qualify without some additional internal controls. Some places still sell valves that do not meet this requirement, but that doesn't mean they are legal to use (seems like they'd be required to only sell legal, code-compliant devices, but that isn't the case). The most common ones are a single handle that does not have a volume control...they're either all on or all off. There are some that still have a volume control, if that is important to you, but none I'm aware of still have separate hot and cold valves you control separately, only temperature control.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12
    DIY Member diydude's Avatar
    Join Date
    Jul 2012
    Location
    Seattle,WA
    Posts
    62

    Default

    Quote Originally Posted by jadnashua View Post
    For a number of years, ALL legal shower valves sold in the USA have anti-scald technology. The most common way to do this is with a pressure balance valve although some thermostatically controlled valves are fast reacting enough to qualify without some additional internal controls. Some places still sell valves that do not meet this requirement, but that doesn't mean they are legal to use (seems like they'd be required to only sell legal, code-compliant devices, but that isn't the case). The most common ones are a single handle that does not have a volume control...they're either all on or all off. There are some that still have a volume control, if that is important to you, but none I'm aware of still have separate hot and cold valves you control separately, only temperature control.
    Ah, those valves. Ok, thanks.

  13. #13
    DIY Member diydude's Avatar
    Join Date
    Jul 2012
    Location
    Seattle,WA
    Posts
    62

    Default

    When I was looking to remove the subfloor, I took a semi-crude route for removing the outside-fitting flange; used a drill, screwdriver, and mini-hacksaw. This left the collar of the flange still attached to the pipe, and the ABS cement is solid as a rock (the pipe is not damaged). Now that I have the floor open and I have a much better view, I want to clean up the sewer pipe before I reinstall the subfloor. I thought about cutting the pipe after the elbow when I initially looked at removing the flange, but there isn't much pipe after the elbow. Now, I was thinking of replacing the elbow and adding a section of pipe for the new flange if I can't somehow remove the remaining portion of the existing flange. Thoughts?
    Attached Images Attached Images   
    Last edited by diydude; 07-07-2013 at 11:07 AM.

  14. #14
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Quit your thinking so much.
    Run down and pick up either a long turn 90, or a medium and a coupling.
    Wack off what you have and start over. (with a saw or cutter)

    You could also drill out the pipe from the fitting, but it's cheaper and quicker to just pick up new fittings.

  15. #15
    DIY Member diydude's Avatar
    Join Date
    Jul 2012
    Location
    Seattle,WA
    Posts
    62

    Default

    Quote Originally Posted by Terry View Post
    Quit your thinking so much.
    Run down and pick up either a long turn 90, or a medium and a coupling.
    Wack off what you have and start over. (with a saw or cutter)

    You could also drill out the pipe from the fitting, but it's cheaper and quicker to just pick up new fittings.
    Thanks, Terry - needed that Moving on now...

Similar Threads

  1. Stumped - How to Replace Tub Waste/Overflow w/ Very Tight Clearance to I-Joist
    By m42stanle in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 07-06-2012, 10:55 AM
  2. Toilet drain clearance
    By rcoatsie in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 10-03-2011, 03:59 PM
  3. Tub Drain/Joist In The Way
    By akmacs in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 12-24-2009, 07:55 AM
  4. Moving tub drain (through joist)
    By hans_idle in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 12-13-2007, 02:41 PM
  5. Joist meets Drain - now what?
    By lhartl in forum Shower & bathtub Forum & Blog
    Replies: 49
    Last Post: 02-12-2007, 06:14 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •