Please, has anyone else had the same experience with the pilot light going out after holding it down for 60 seconds and then releasing it?
|
|
|
I replaced the thermocouple. It's installed correctly. I get a nice blue flame. No drafts. No water dripping on pilot light. When I go to light pilot light, I hold down the knob for 60 seconds, as soon as I let up on the knob the pilot goes out. Yes, the gas supply is turned on. Is this a faulty gas control valve? How do I test it? I had no trouble replacing the thermocouple so I may be able to replace the gas control valve?
Please, has anyone else had the same experience with the pilot light going out after holding it down for 60 seconds and then releasing it?
The position of the thermocouple can be critical to its proper operation. The pilot flame must intersect the thermocouple for it to genereate the signal to tell the gas valve it's okay to light. While it shouldn't be a problem with a new one, if it is all covered in soot, that can be an issue. You may need to bend the bracket slightly to reposition it.
Jim DeBruycker
Important note - I'm not a pro
Retired Defense Industry Engineer
To add to what I wrote earlier: the primary problem of many water heaters in recent years has been a failure in the gas control valve/thermostat--particularly those with Unitrol valves. For the Whirlpools (see sticky above) a primary culprit was an ECO device that would shut off the gas. If this goes you have to replace the gas control valve/thermostat. From what I've seen personally and other posts here, the replacements seem to be holding up.
About the only time this won't work is if there is a problem with the air supply (plugged flame arrestor screen) or vent stack (back pressure/back draft.) While these were posited as primary causes for many pages of the Whirlpool WH thread, these did not explain most of the problems. The gas control valve/thermostat issue did!
I replaced the gas valve assembly. I am back up and running. It was a fairly easy procedure.
I thought it was suspect how readily "State" was to send me the part (under warranty of course)...they must have had a lot of problems with their short-lived gas control valves.
Everyone seems to have had trouble with the the Unitrol gas valves for awhile (including Rheem and others...BW had the same set up for awhile, but they have far fewer installed.) At some point vendors became pliant to replacing parts when people called. Anyway, glad you could repair it--it is beyond the ability of some folks. Makes way more sense trying this than throwing out a good tank many years before it fails. For awhile there were several plumbers here recommending a new WH as the first response, which was just stupid and unnecessarily wasteful.
RWB- thanks, I watched this video over and over and just followed the steps closely.
http://hotwater101.com/video/gas-gas...placement.html