    To resurrect this, another property has the same situation, 2 hots and a neutral from the meter pole, with a driven ground rod there at the meter pole. Then three wires travel to the house subpanel with ONLY a ufer ground, no driven ground. Does that fly too?

  2. #17
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    Quote Originally Posted by ballvalve View Post
    To resurrect this, another property has the same situation, 2 hots and a neutral from the meter pole, with a driven ground rod there at the meter pole. Then three wires travel to the house subpanel with ONLY a ufer ground, no driven ground. Does that fly too?
    Yup. Pretty typical install.

    With a Ufer NO other grounding electrodes are required, unless of course they already exist (like a metallic underground water pipe).

  3. #18
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    328

    Default

    Agreed. Given the information as presented, there is no problem with the installation.

  4. #19
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,661

    Default

    Most installs around here have the meter mounted near the breaker panel, or it is a temporary install.

    Are you in a trailer court or what ?
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #20
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    In this mountain area, most bring in power early for a well. Lots are 5 acre minimum to many at thousands. So you set a overhead or underground service pole, and then PGE serves that, usually a small meter box with 6 to 12 spaces. From that you build the house, and then finally make a main run to the house 'subpanel'. Sometimes 20 or 30 years pass between the meter pole and the final living space or barn hookup.

    PGE, the utility MUST serve a well, but no other structure unless completed, so this is how the ones that know get power in early. I knew one creative guy that set up a fake well and house just to get the power in.

    I should post a photo of the feed to my house - PGE hung the high tension lines to monster pine trees down an inacessible canyon. Been working for 30 years after a few re-habs. And then we did a 800' undergound run down a rock cut into a 50 degree slope to the meter box.

    Hell, I have 6 tie backs for power poles that are drilled into the base of black oak trees! and you can still follow the phone lines in the pine trees for miles - when I moved here it was maintained by a group of local miners and we were on a 32 party line. And that was the 80's.

    Those same guys used to just go out and hook up their mines to the nearest pole and then call and ask the utility [ a drinking bud at a one man office] to set a meter for them. Thats when we had freedom and guys that worked like mules.
    Last edited by ballvalve; 09-04-2012 at 12:43 PM.

  6. #21
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,661

    Default

    Wow,

    Ground rods are not much good in terrain like that.

    That must be why they do it that way.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  7. #22
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    The ground rods usually get cut off after about half gets in and then pounded on to look like its in. But I lay them down in a trench now in hard stuff.

    I think the county got its building department in 1978. Now its filled with Berkely educated idiots. The BEST part was the planning commission pre 1970's. If you wanted to subdivide your 400 acres into 25x75' lots - or anything - a ruler and a few dimensions on the county maps was just enough to make your city for free.

    Once owned into a 1940's subdivision of 20x50 lots - hundreds on a hillside. You should see our Berkely planners now finding ways to make them worthless.

    But there is hope: go to Dyer Nevada, Esmerelda county. Beautiful ranches surrounded by snow capped peaks and NO building dept. Just start hammering!


    http://www.zillow.com/dyer-nv/
    Last edited by ballvalve; 09-05-2012 at 10:55 AM.

Similar Threads

  1. 4 Wire Cooktop and Oven to 3 Wire Sub Panel
    By TJanak in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 12-29-2011, 05:45 PM
  2. Service water line entrance "Split entrance" house, slab floor...
    By EltonT in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 06-13-2011, 07:22 AM
  3. Ground Bus in old panel?
    By Nate R in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 06-30-2008, 08:57 AM
  4. Placement Of Service Entrance Panel
    By toolguy504 in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 12-21-2007, 08:05 PM
  5. tip(s) for replacing a meter panel
    By rdtompki in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 12-12-2007, 08:11 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •