    Default GFCI blows on jacuzzi

    about a month ago the GFCI outlet tripped every time I tried to turn on the water jets in the bathtub.
    I opened up the access panel and ran an extension cord over from a non-GFCI outlet and it worked.

    Today I replaced the outlet.
    Same damn thing.

    I then ran an extension cord over to an outlet on a different circut with a GFCI. It blew that one also.
    (Should have tried that earlier and saved the $30 and time for replacing the outlet)

    Its a 15amp. should be more than enough. Plus, it has been working for 8 years.

    Any ideas?

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Its been working for 8 years and wore out

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    You have a problem with the tub and it may no longer be safe. I'd not run the jets until I figured out what was wrong - it's not the GFCI!

    A GFCI works by comparing the current that goes from the hot lead, through the load, and then back through the neutral. They should be equal. If they are not, some of the current is leaking, and going somewhere else (probably to ground, thus they call it a ground fault - error, problem). The problem is, that current might end up going through you along the way, and it doesn't take much to kill a person under the right circumstances, and adding in water makes that more likely. DON'T run it via a regular outlet if you value your life. Fix it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    331

    Default

    Nine times out of ten it's a heating element worn out. Nine hundred and ninety-nine times out of a thousand the GFCI is doing its job and protecting you.

  5. #5
    DIY Junior Member Carl Fredricksen's Avatar
    Join Date
    Aug 2012
    Location
    Illinois
    Posts
    2

    Default

    It has no heating element.

    My next step was going to be putting in a 20amp breaker.
    guess I should just call the bath guy.
    Anyone know of a good one in Chicago?

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    If it is tripping the GFCI installing a larger one will not fix the problem. Installing a larger breaker will only make things worse.

    The problem is that the tub is 8 years old and needs to be repaired.

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    While the GFCI might have current limiting, its primary purpose is to detect faults, and those can occur at ANY load. If it was exceeding max current, it would trip the breaker, not the unit itself. It only takes in the order of 5milliamps unbalance in the outgoing and incoming current to trip the unit. 10milliamps (that's 0.010A) applied just right can kill you. If the motor has brushes, it could be as simple as the conductive dust from them wearing down is providing a current path to ground. The thing is a safety device - a properly working appliance should NOT trip it. It is tripping, there is something wrong and applying a bigger hammer (circuit breaker) isn't the answer.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  8. #8

    Default

    Most jacuzzis have a heater,but if yours doesnt then it has to be the pump motor.Is the pump compartment wet at all? A wet motor will likely run but will trip a gfci
    Politicians are like diapers. You need to change them often……for the same reason.

  9. #9
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    time for a new pump. Save the other for some non life critical use.

  10. #10
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    GFI's don't trip from too much current being used so installing a larger breaker will not solve the problem.

    Have a repair company come out and service the tub.

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default

    GFCIs are NOT circuit breakers so using a 20 amp breaker will just waste money. The problem is in the motor.
    Licensed residential and commercial plumber

Similar Threads

  1. Takagai TM-1 blows fuse on circuit board
    By magconpres in forum Tankless Water Heater Forum
    Replies: 5
    Last Post: 04-20-2012, 02:39 PM
  2. New sink install, not draining, garburator blows water up the 2nd sink
    By aldous314 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 07-01-2011, 05:39 AM
  3. GFCI Breaker (no GFCI outlets) not working, but not tripped
    By dmotes in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 12-02-2010, 11:18 AM
  4. Cold air blows in with the heat through vents...
    By pestario76 in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 03-05-2010, 03:57 PM
  5. Pensotti blows out
    By Pensotti in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 08-26-2008, 04:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •