Thread: Venting basement DWV system

  1. #1
    DIY Junior Member FatsoPilot's Avatar
    Join Date
    Mar 2012
    Location
    WA State
    Posts
    18

    Default Venting basement DWV system

    I'm trying to figure out how to vent my basement bath and shower drains. In WA state code says you can't roll a vent more than 45 degrees until 6 inches above the flood line of the highest fixture? If I have a drain in the basement along an outside wall that I'm running straight down the middle of the bathroom (so there is no access to a wall to run a vent in any other place in the required distance) and I'm trying to vent along the wall back around the room to the vent, what kind of fittings would I use? Without running the line a few feet close to horizontal I'm not sure how it is physically possible. This is a mock up (a poor one), the wall the line crosses over is too far to meet code so I have to vent out the back. The drain for the bath is going to be a few feet from the wall at the bottom and the other drain is going to be a few feet from the wall on the left.

    Name:  Jay's Bathroom211.jpg
Views: 232
Size:  9.3 KB

    Thanks in advance for any advice (or even better a picture).

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default

    For starters, when the tub drains, unless there is a vent for both the shower and the tub, that are separate, the p-trap on the shower is going to siphon dry when the tub drains.

    Washington State UPC
    You can run a 2" trap arm 60" before the vent
    and for a 1.5" trap arm, 42" before the vent.
    The revents need to be 42" above the floor.
    In this case, the shower and the tub have vents that can be tied in together at 42" above the floor.

  3. #3
    DIY Junior Member FatsoPilot's Avatar
    Join Date
    Mar 2012
    Location
    WA State
    Posts
    18

    Default

    Thank you for reply. I was planning on venting them separately and tying them together eventually at least 42" above the floor. Is it possible to vent the tub on the back wall? And the shower on the left wall? If so, how is it possible without running the vent horizontal a short distance? What fittings would allow this to happen or how can I run the lines so I can stay in code when rolling the vent?

    Cheers.

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default

    Rolling would be wyes and 45's

Similar Threads

  1. basement venting
    By b-y in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 20
    Last Post: 02-19-2011, 08:56 AM
  2. Basement venting-Is this right?
    By littlebrook in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 13
    Last Post: 09-03-2008, 05:24 AM
  3. venting with ejector pit system in basement
    By jiggityjars in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 20
    Last Post: 04-24-2008, 01:29 PM
  4. Venting drainage system in cottage
    By lardlad in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 07-03-2007, 03:05 AM
  5. Adjusting AS Vent-Away toilet venting system
    By andy_levine in forum Toilet Forum discussions
    Replies: 4
    Last Post: 09-15-2005, 06:54 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •