Page 2 of 2 FirstFirst 12
Results 16 to 29 of 29
Thread: Adding a Bath Electrical Circuit
  1. #16
    Jun 2007
    North Carolina
    Quote Originally Posted by diydude View Post
    Sure.
    Here's the owner's manual for the thermostat. I read the instructions a little closer, and they call for a 15-amp breaker max. at the panel to connect the thermostat for the size mat I'm using (10 sq ft). The mat instructions mention a 20-amp circuit - I'm guessing this is for headroom considerations: http://www.warmyourfloor.com/media/t..._500670-EN.pdf
    SunTouch 4' x 30" mat I plan on installing: http://www.warmwire.com/products/sun...-12000430.html
    When you open that link for the thermostat look at the left of the screen and read line 5
    Edited to add;
    Also look at the bottom of the first page at line 4
  2. #17
    DIY Member diydude's Avatar
    Jul 2012
    Seattle,WA
    Quote Originally Posted by jwelectric View Post
    Edited to add;
    Yes, those were the two bullets I noticed when I looked through the manual. I just reread it, and I've got it now. I've decided to stick with my plan to install the two 20-amp circuits:
    - Circuit #1: Two GFCIs
    - Circuit #2: Floor heat, downstairs bathroom fan and lights
  3. #18
    Jul 2012
    Seattle,WA
    Ok, I have a couple requests for confirmation. I'm running my wiring through the crawlspace. I was reading through Chapter 296-46(B) WAC as is referenced by my city's electrical code (fun reading - NOT!)
    Link to Chapter 296-46(B) WAC: http://apps.leg.wa.gov/wac/default.a...ue#296-46B-334
    (1) The "015 Exposed work" section mentions that the NEC protection standards for NM cable in crawlspaces do not apply in Washington; no need to bore holes in floor joists or use running boards when running cable perpendicular to floor joists. I just wanted to confirm and make sure I didn't miss something.
    (2) The other thing I read in section "015 Exposed work" was about a 2 1/2" requirement for cable protection. It appeared to not apply to installations being covered by drywall. The NEC 1 1/4" requirement would apply instead for drywall. Please confirm.
  4. #19
    Jun 2007
    North Carolina
    I think that the link you posted calls for a circuit no larger than 15 amps and for it to be all by itself if possible.
    Being that you are installing this new then it is possible for it to be on a deciated circuit
  5. #20
    Jul 2012
    Seattle,WA
    Yeah, the instructions seem ambiguous. The mat instructions mention the following:
    Maximum Circuit Overload Protection 20 A Breaker
    Maximum Circuit Load 15 Amps
    One other thing I saw, which led me to think that they were providing general NEC-type guidelines for residential circuit wiring, is step 1.2 of the mat instructions. Also, see page 19, which mentions a typical 20A circuit for one mat: http://www.warmwire.com/media/SunTou...urrent-WYF.pdf
    Also, why would you have a cap on the breaker size if everything is being wired in parallel?
  6. #21
    Jun 2007
    North Carolina
    The maximum circuit that can supply the mat regardless of the square feet being covered is 20 amp. The largest load the circuit of the mat can carry is 15 amps. All this is directed to the mat itself and has nothing to do with the controller that you posted.
    Should one to decide to use a larger mat then they would choose a larger controller that would match the square footage being installed.
    http://www.warmwire.com/products/con...hermostat.html
    The controller which is the weakest link in this circuit is what will mandate what is to be installed. It requires a 15 amp circuit and recommends a dictated circuit.
    As an electrical inspector I would not pass the installation should it not be as the controller states in its installation instructions.
    As to your cable installations question, I can’t address Washington but the here in NC we are not requiring anything special in the crawl space or any hole drilling.
    Each node of a parallel circuit will add current to the entire circuit. In the node for the heating mat the mat and its controller will be a series circuit of a predetermined resistance. This node will add to the other nodes of the circuits for a total amperage draw that the conductor must be capable of carrying.
    The total resistance of a parallel circuit will always be less than the lowest resistance of any single node. Should one of those nodes lose all resistance then the amperage draw will increase to the point that damage would occur to the insulation on the conductor. This is the job of the fuse or the circuit breaker. It will open in the event of a high current draw and protect the conductor.
    A GFCI device does not open in the event of an overcurrent event. All the GFCI device is looking for is a difference between two current carrying conductors of 4 to 6 milliamps.
    What the manufacturer of the GFCI device is saying is if more than 15 amps is allowed to flow through this device it could damage the integral wiring of the circuit board and render the device useless.
  7. #22
    Jul 2012
    Seattle,WA
    Ugh, ok. jwelectric, I'll take your suggestion. Please confirm this is what you stated:
    Circuit 1 (20 amps): GFCIs only
    Circuit 2 (15 amps): Floor thermostat and mat
    Circuit 3 (Existing 15-amp branch circuit): Add recessed light and sconces that are substituting for existing vanity lights
    Edit: My concern is overloading the 15-amp branch circuit. When I add up the wattage, including the new recessed light, I'm at 1575W. This would most likely not pass an inspection, correct?:
    Lights fixtures:
    - kitchen (2): 240W (4 - 60W bulbs)
    - chandelier (1): 360W (6 - 60W bulbs)
    - downstairs bathroom (1): 315W (Recessed light (75W), Sconces (4 - 60W bulbs))
    - deck (1): 180W (2 - 90W bulbs)
    - downstairs bedroom (2): 120W (2 - 60W bulbs)
    Outlets:
    - downstairs bathroom GFCI (1)
    - downstairs bedroom (1)
    - upstairs bathroom GFCI (1) - probably not necessary that it be GFCI, since it feeds off the downstairs GFCI. Anyway.
    - living room (1)
    Other:
    - downstairs bathroom fan (180W?)
    - kitchen range hood (180W?)
  8. #23
    Jun 2007
    North Carolina
    Are you planning on having all these light on at the same time?
    If it is a concern while the walls are open then install an addtional circuit
  9. #24
    Jul 2012
    Seattle,WA
    No, I wouldn't have all the lights on at the same time; there are only two of us in the house I remember reading something about a 3-hour continuous load, and only the deck light would be on continuously for 3+ hours. I believe I have 5 open slots in the panel (although, it's only a 60-amp panel - that's another issue I'll have to deal with later), so I could run three new circuits.
    I'd have to amend my electrical permit. Oh, boy. And yes, I was supposed to meet with an electrician this past Thursday before applying for a permit, but they never showed. So, I decided to move forward with getting permits before the weekend.
  10. #25
    Jun 2007
    North Carolina
    There is a difference between calculating a load for commercial and industrial than doing a dwelling unit calculation.
    In industrial and commercial we do a continuous calculation but for a dwelling we do the 3 watts per square foot and no continuous load for these circuits.
    Although it is a good idea to do the wattage per light fixture for branch circuits there is no need to do the continuous factor to the circuit. It is very unlikely that one would have 1400 watts of lights burning for a very long period of time let alone for three hours at a time. Should someone do this repeatedly the power company would invite them to the board of directors meeting as a stock holder.
  11. #26
    Jul 2012
    Seattle,WA
    LOL. Ok, thanks. So, I'll just add the recessed light to the existing 15-amp circuit and call it good. Thanks for the advice.
  12. #27
    Jul 2012
    Seattle,WA
    Ok, I have another question. I'm investigating another floor warming system by Warming Systems, Inc. The instructions mention that only a certified electrician can connect the floor heating mat (I'm actually going to be using the warming wire instead of the mat - don't think it matters). Do I need to worry about this mandate with regard to an inspection?
    http://www.warmingsystems.com/Cable%...structions.pdf
    Only a certified electrician who is familiar
    with electrical installation codes and
    practices can connect the floor heating mat.
    All wiring must comply with the
    specifications in the US National Electric
    Code and all local electrical regulations
    and standards.
  13. #28
    You may lose any warranty claim if not installed by a licensed electrician.
  14. #29
    Jul 2012
    Seattle,WA
    I can live with that. I'm just concerned about legal issues.
  1. adding a light switch to GFI protected circuit
    By Spook in forum Water Heater Forum, Tanks
    Last Post: 01-26-2012, 10:21 AM
  2. 1985 Electrical Code, Bathroom Circuit Amperage in Georgia
    By Dr.Lightning in forum Electrical Forum discussion & Blog
    Last Post: 10-19-2011, 04:14 PM
  3. Adding circuit in existing EMT?
    By cacher_chick in forum Electrical Forum discussion & Blog
    Last Post: 03-30-2011, 09:16 PM
  4. NC Electrical Code - 20A GFCI Circuit in bathroom
    By WalterHego in forum Electrical Forum discussion & Blog
    Last Post: 12-21-2009, 11:12 AM
  5. Adding 4-way switches to a 3-way lighting circuit
    By cej22 in forum Electrical Forum discussion & Blog
    Last Post: 11-14-2009, 07:39 PM