Thread: Sanitary tee on back for venting toilet

  1. #1
    DIY Junior Member bandrewfox's Avatar
    Join Date
    Jul 2012
    Location
    Seattle
    Posts
    11

    Default Sanitary tee on back for venting toilet

    Hi, I'm a new member here and have been browsing the forum trying to get an answer to this question, but it seems like half the threads say it is ok to do this and half say it is not ok.

    My question is: can I use a 3" sanitary tee on its back with the 2" opening going straight up vertically (as a vent - with nothing draining into it) on a horizontal 3" drain directly from the toilet's floor flange (about 1 foot away from the san tee)?

    I certainly understand that san tees can only be used vertically for drainage, but is this considered drainage or venting? Toilets seem to be an exception to some rules because their trap is inside the fixture...

    If you say "no, san tee cannot be used in this situation", then I will have to use a wye for the 2" vent - but I can't use the wye with the 2" vertical since there is not enough room in my joist area for the extra street 45 fitting. In this case, my next question is, how much do I need to "roll" my wye. Does it have to be 45 degrees or is something like 10 degrees ok? I know it can't be flat.

    I am the homeowner doing the work and this is in Seattle - with King County doing the plumbing inspection.

    Thanks so much!
    Last edited by bandrewfox; 07-22-2012 at 05:15 PM. Reason: additional question

  2. #2
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    If the sanitary tee is down stream from the toilet it's OK.

    John
    Last edited by johnjh2o1; 07-22-2012 at 05:28 PM.

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,221
    Blog Entries
    1

    Default

    I am the homeowner doing the work and this is in Seattle - with King County doing the plumbing inspection.
    In Seattle, which uses UPC code, they will expect a combo or wye fitting if it's on it's back.
    You may need to drill a larger hole up through the floor. Or...........you can try the Santee and see if the inspector notices.

    Here is a nice link to Bert Polk's plumbing tips
    Last edited by Terry; 07-23-2012 at 07:06 AM.

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,946

    Default

    Downstream or there is waste upstream and the 2" straight up works for IPC
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

Similar Threads

  1. Sanitary Tee on it's back
    By edtuck in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 05-28-2012, 09:16 AM
  2. Combined Kitchen/Sanitary Venting in Chicago
    By emende in forum Plumbing Code Questions
    Replies: 1
    Last Post: 12-10-2010, 07:10 AM
  3. Sanitary Tee on its back...
    By zxed in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 33
    Last Post: 02-01-2009, 02:26 PM
  4. Sanitary Tee on Back in DWV
    By plumbnut in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 09-16-2007, 10:08 AM
  5. Venting Back to Back Baths
    By Rob F in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-29-2006, 08:24 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •