    Default Which States and Provinces require flood testing your next shower renovation?

    It seems the subject of flood testing showers is a very sensitive one online. Here in Vancouver, British Columbia all showers are required to be flood tested. That might be to general of a statement so to be more specific all showers that have a permit are required to be flood tested. So if you live in Vancouver and skip this step - is it wrong?

    I say yes. If you need to flood test your showers in a new home or commercial project you need to insist that this get done in a simple renovation.

    But what about other cities and in the states. I heard today that in Bridgton, Maine you are not required to preform them. I was called a "Lying Bastard" for even posting information about them. So who's right? Are flood tests required in Maine? Are they required in Vancouver.

    I'd like to hear from as many regulars as possible and would ask each of you to call your local building department and ask the question as to what the required steps are. If a permit is not needed to renovate a room and keep it the same ask them if they recommend that this step be done. Also ask about new construction for me please.

    Share your information here and perhaps we can get a state by state, province by province list going.

    Thanks for any and all help!

    JW
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  2. #2
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Does Laticrete promote flood testing in Maine? The answer is yes.

    If you are looking for more opinions on the subject of flood tests - perhaps consult the manufacture of the waterproofing products themselves.

    A company like Laticrete based out of Maine is a classic example. In their newsletter they not only recommend flood tests they go on to explain how they are done. Take a quick peak at this news letter from Laticrete.

    Flood Testing a Laticrete Hydro Ban installation.

    http://apps.laticrete.com/EmailImage...ewsletter.html

    Does the city of Portland require this step? Does the city of Bridgton require it? Not sure but the maker of the waterproofing product is recommending it - that should speak volumes to you.

    I find it surprising the huge resistance that I'm faced in promoting this silly little step. The plumbers in the group here would laugh I'm sure at the concept of skipping this step with a traditional PVC liner and clamping drain. I've seen young plumbers flood out offices before trying to figure out how to seam their membranes. The last big flood out was 12 years ago on Beach Avenue here in Vancouver. That was the last time I let a plumber use a rubber liner on my projects. I work with plumbers every week - not one of them misses doing these shower pans. Not one.

    I just emailed Dana and Bruce - both of which work for the government of Maine. I've asked fro some clarification to their plumbing codes and requirements. It seems that Maine follows the UPC and their most recent admendments do not remove the leak test from being preformed.



    JW
    Last edited by johnfrwhipple; 07-21-2012 at 12:03 PM.
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  3. #3
    DIY Junior Member AMartinez's Avatar
    Join Date
    Jul 2012
    Location
    Hutchinson, KS
    Posts
    1

    Default

    To my knowledge Kansas or at least my region does not require flood testing nor did Savannah GA when I Operated there for six years. Maybe stricter codes would help keep "fly by night" installers out of business! I still strongly believe in a pre slope underneath a shower pan liner with a mud bed on top. No styrofoam! I also like to waterproof the mud bed and my walls. There are so many extras you can do and techniques to ensure your installation is tighter than a bullfrogs butt! Unfortunately the basic knowledge of construction and water flow has seemed to bypass a huge chunk of our industry.

  4. #4
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Kentucky plumbing Code - Shower leak tests or shower flood tests

    A friend of mine online told me that Kentucky follows it's own plumbing code. I read through it quickly and the Kentucky Code book makes no reference to flood testing or leak testing it's showers.

    It does make note that no seams are allowed in the shower. This would rule out many of the smaller rolls of waterproofing products I imagine.

    Keep them coming!

    Kentucky Plumbing Code PDF


    Thanks guys.

    JW
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  5. #5
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default

    Quote Originally Posted by AMartinez View Post
    To my knowledge Kansas or at least my region does not require flood testing nor did Savannah GA when I Operated there for six years. Maybe stricter codes would help keep "fly by night" installers out of business! I still strongly believe in a pre slope underneath a shower pan liner with a mud bed on top. No styrofoam! I also like to waterproof the mud bed and my walls. There are so many extras you can do and techniques to ensure your installation is tighter than a bullfrogs butt! Unfortunately the basic knowledge of construction and water flow has seemed to bypass a huge chunk of our industry.
    Hi A Martinez. What plumbing code do your projects fall under? Are they a local or state requirement? Testing your work and informing potential clients that you do will separate you from every other Handy Andy that thinks our job is easy. I might suggest your try this approach going forward.

    JW
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  6. #6
    DIY Member jadziedzic's Avatar
    Join Date
    Aug 2006
    Location
    New Hampshire
    Posts
    72

    Default

    Nashua, NH: International Plumbing Code, shower line test was required (re: IPC 312.9). The inspector did remain on premises for the (minimum) 15 minutes required by the IPC, and observed the water drain when the test plug was removed. I actually filled the shower 24 hours prior to the test to be sure I didn't have any slow leaks.

  7. #7
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Kansas Plumbing requirements for shower receptors

    It appears that Kansas follows the IBC (International Plumbing Codes). The IBC requires that all shower receptors be built water tight and visually inspected.

    A little more research needs to be done here. Can you call on your local inspector and ask what's up?

    JW
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  8. #8
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Florida requirements for flood testing or leak testing showers

    Found this copy of the Florida plumbing code. Clear as day it requires that showers be flood or leak test and a visual inspection done for leaks.

    http://buildingofficial.com/2005code...l-Plumbing.pdf

    JW
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  9. #9
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Nashua, NH requires flood testing - IPC 312.9

    Quote Originally Posted by jadziedzic View Post
    Nashua, NH: International Plumbing Code, shower line test was required (re: IPC 312.9). The inspector did remain on premises for the (minimum) 15 minutes required by the IPC, and observed the water drain when the test plug was removed. I actually filled the shower 24 hours prior to the test to be sure I didn't have any slow leaks.
    Great work! A flood test is the easiest thing to do and shows your professionalism to this trade. I hope more people track you down.

    The NTCA is working on getting certifications done so that installers can choose their favourite method of waterproofing and get certified. The first step is becoming a 5 Star NTCA contractor and then later courses on Kerdi waterproofing, Mapei liquid membranes, Laticrete systems etc will be added. With any luck in a 5-10 year window showers will need a ticketed installer.

    I understand that Schluter Systems is working closely with the NTCA to develop the first course. I've already signed up for the 5 Star program and hope I make the grade! I'm not good at working under time line constraints and this 5 star NTCA program does have a time limit! That and I have to cut my own tile..... lol It will do me good to do a install start to finish on my own. I have grown accustomed to having my apprentice with me every day. I'm going to sign David up as well andwe are going to go head to head! I hope the student does not become the teacher.


    2009 International Plumbing Code (312.9) Shower flood test or leak tests.

    Now if your city follows the IPC or International Plumbing Code you are required to check that the shower is leak proof.

    JW
    Last edited by johnfrwhipple; 07-21-2012 at 11:29 AM.
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,560

    Default

    Common sense would dictate that if you construct a shower, with or without a permit, the only way to be sure it will NOT cause structural failure would be to "flood test" it. As far as I know, there is no code that does not require it, but have seen some "on grade" showers which would not have benefited from it, since they could not retain water.
    Licensed residential and commercial plumber

  11. #11
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default

    Quote Originally Posted by hj View Post
    Common sense would dictate that if you construct a shower, with or without a permit, the only way to be sure it will NOT cause structural failure would be to "flood test" it. As far as I know, there is no code that does not require it, but have seen some "on grade" showers which would not have benefited from it, since they could not retain water.
    HJ Common Sense goes out the window when builders are building on Spec and tile setters are in a rush to wrap up a new job. I spent the better part of 5 hours researching the subject more in depth today to find that much of the Universal Plumbing Codes position on the subject is no more than a 15 minute soak. Pretty sad that this is allowed.

    I can see it being to hard for the cities to inspect every job and every shower. If you are looking for an inspector to save your next shower you may be hoping for a miracle.

    I got an email from a friend in Maine who passed on a local inspectors phone number. This inspector should shed some more light onto the subject of flood test in Maine. I used his name and number to track down all the plumbing officials in Maine. I emailed ten people today and should have some information next week.

    Here in Vancouver if the shower is not flood tested properly it's a fail. If you use a product not familiar to the inspectors - its a fail. If the plug is not right - a fail. If the liner is not cut - it's a fail. More of the US should follow suit and more homeowners should demand that it gets done. This is on permitted projects only of course. Most of the bathroom renovations here in BC fly under the radar and no permit is ever issued. So with no inspectors and no safety net of self inspections who is surprised when it leaks? The builder - I bet. The client - More pissed off. The tile setter - Shocked for sure. If it is a huge repair - will your guy make it right? If you paid him cash, you are truly screwed as a client.

    I wonder how many showers would be saved from the landfill in one year if every new shower was flood tested? I'm thinking tens of thousands easy. I've heard that it is often the Home Builders Associations that offer up a lot of resistance to change. A flood test costs money for sure. Someone has to flood it. Some one needs to check it and someone needs to let the inspector in to see it. If your cutting costs on your renovation is this one step you think you can skip?

    JW
    Last edited by johnfrwhipple; 07-21-2012 at 11:06 PM.
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  12. #12
    DIY Junior Member Justadrip's Avatar
    Join Date
    Apr 2012
    Location
    New York
    Posts
    10

    Default

    Quote Originally Posted by John Whipple
    A company like Laticrete based out of Maine
    Laticrete is based out of Bethany CT.

    LATICRETE International, Inc.
    One LATICRETE Park North
    91 Amity Road
    Bethany, CT 06524-3423, USA

  13. #13
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Whoops - Bethany not Portland, Maine

    Quote Originally Posted by Justadrip View Post
    Laticrete is based out of Bethany CT.

    LATICRETE International, Inc.
    One LATICRETE Park North
    91 Amity Road
    Bethany, CT 06524-3423, USA
    Thanks for that.

    I received and email from someone in office in Maine and was told that the legislation around building codes removed all chapters on plumbing. In Maine I'm told that the Plumbers Examiner Board governs all work. I was pointed to this link for more information.

    http://www.maine.gov/pfr/professiona...bers/index.htm

    If you view the link you can see that Maine follows the Universal Plumbing Code and even includes a power point reviewing Maine's changes to it. Now where in this review does it remove the leak or flood test described in the Universal Plumbing Code. So has the Universal Plumbing Code dropped this step in the new 2012 version? My new PDF format won't load but in the earlier printings it's there.

    Any one have a current 2012 Universal Plumbing Code book?

    JW
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  14. #14
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Plumbing Inspection Process - 2012 Universal Plumbing Code (UPC)

    SECTION 107
    INSPECTIONS AND TESTING

    [A] 107.4 Testing. Plumbing work and systems shall be
    tested as required in Section 312 and in accordance with Sections
    107.4.1 through 107.4.3. Tests shall be made by the permit
    holder and observed by the code official.

    [A] 107.4.1 New, altered, extended or repaired systems.
    New plumbing systems and parts of existing systems that
    have been altered, extended or repaired shall be tested as
    prescribed herein to disclose leaks and defects, except that
    testing is not required in the following cases:
    1 In any case that does not include addition to,
    replacement, alteration or relocation of any water
    supply, drainage or vent piping.
    2. In any case where plumbing equipment is set up
    temporarily for exhibition purposes.

    [A] 107.4.2 Equipment, material and labor for tests. All
    equipment, material and labor required for testing a
    plumbing system or part thereof shall be furnished by the
    permit holder.

    312.9 Shower liner test. Where shower floors and receptors
    are made water-tight by the application of materials required
    by Section 417.5.2, the completed liner installation shall be
    tested. The pipe from the shower drain shall be plugged water
    tight for the test. The floor and receptor area shall be filled
    with potable water to a depth of not less than 2 inches (51
    mm) measured at the threshold. Where a threshold of at least
    2 inches (51 mm) high does not exist, a temporary threshold
    shall be constructed to retain the test water in the lined floor
    or receptor area to a level not less than 2 inches (51 mm) deep
    measured at the threshold. The water shall be retained for a
    test period of not less than 15 minutes, and there shall not be
    evidence of leakage


    And so it seems that if you are building a shower in Maine you do require a leak test of your shower. It is the responsibility of the permit holder to test it and to call for this inspection.

    I would go on to add a 15 minute test is worthless and would suggest you do a 24-72 hour flood test.

    Good luck.

    JW
    Last edited by johnfrwhipple; 07-24-2012 at 06:39 AM.
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

  15. #15
    Barrier Free Showers johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    1,581
    Blog Entries
    5

    Default Flood testing requirements for Bridgton, Maine - From the town managers office

    I received an email back from the mayor of Bridgton, Maine.

    Here is what was written.

    Good Morning Mr. Whipple,

    The Town of Bridgton follows the 2009 Uniform Plumbing Code and does inspect shower pans. In discussing this with our CEO, we may have missed one but that is the exception since we try to inspect all. The plumber sets up the feed line, we do not check for pressure. Robbie does a flood test of the pans.
    You will have to research construction elements in the codes or through manufacturers recommended installation manuals....

    Cordially,

    Mitchell A. Berkowitz
    Town Manager
    Bridgton, Maine 04009
    207-647-8786


    Mitchell Berkowitz <townmgr@bridgtonmaine.org>
    Non City Official Names edited out of email


    I was called a ______ Bastard for suggesting that this was required. It is staggering the amount of pros that have no clue how to do their job's properly. I hope this puts to bed the subject of flood testing showers in Maine for a while....


    UPDATE, August 2, 2012

    Good morning John,

    All shower, either pre fab or built on site shall be tested per the 2009 Uniform Plumbing Code. There are no exceptions to this rule. Showers shall also meet a minimum size requirement and if built on site they shall be constructed per the requirements in chapter four of the UPC. Too many times if they are not test a leak occurs and creates an insanitary condition where mold and bacteria can grow unstopped.

    The testing requirements are referenced in Chapter 4-411.8.1 and all other shower requirements are in 411.0 through 41.11.

    If I can be of any other assistance please feel free to contact me @ 207-624-8639.

    Dana C. Tuttle
    Senior Plumbing Inspector
    Dana.C.Tuttle@maine.gov



    JW
    Last edited by johnfrwhipple; 08-02-2012 at 05:58 AM.
    I'm a bathroom builder, a Houzz Contributor, a blogger, a linear drain salesman and "Coach" to about 24 North Shore Girls Soccer players. I live for snow days and love the work we do. My newest love is LED lighting and we are pushing the boundaries of what's possible in a high end shower! Proud member of the NKBA & TTMAC. Voting member ASTM

Similar Threads

  1. Choosing the best Grout for your shower renovation
    By johnfrwhipple in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: Today, 07:47 AM
  2. How much should the water level drop in a Kerdi Shower flood test?
    By johnfrwhipple in forum Shower & bathtub Forum & Blog
    Replies: 37
    Last Post: 10-05-2012, 06:55 AM
  3. Is shower stall ceiling lighting required in a new renovation shower?
    By GGB in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 05-07-2012, 05:13 PM
  4. Replies: 3
    Last Post: 01-17-2011, 01:45 AM
  5. This one may require an asprin
    By Mike_B in forum Plumbing Forum Discussion & Blog
    Replies: 5
    Last Post: 10-21-2006, 10:31 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •