    Renovating master bath on 2nd floor. Just ripped up a floor only to discover that the original shower drain is 1 1/2". House was built 1987.

    Question: Can I proceed to install shower with 1 1/2" drain? I always thought showers required 2" drains. Thoughts?

    Edit: Turns out OBC 1992 Table 7.4.9.3 permits 1 1/2" drains for showers with only 1 head. Am I reading this right?

    Thanks

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    If it is not being inspected, which I assume is the case, you can do anything you want to. And even if the code DOES permit it, that is a "minimum standard" and you may NOT be happy with the results some time in the near, or disant future.
    Licensed residential and commercial plumber

  3. #3
    Renovating Footman_75's Avatar
    Join Date
    Jul 2012
    Location
    Ontario, Canada
    Posts
    34

    Default

    Quote Originally Posted by hj View Post
    If it is not being inspected, which I assume is the case, you can do anything you want to. And even if the code DOES permit it, that is a "minimum standard" and you may NOT be happy with the results some time in the near, or disant future.
    Not interested in doing anything I want to. Am interested in doing good work, and understanding physics behind code. Thanks for your reply though.

    Did you read my original post? Original build has 1 1/2 shower drain. Was surprised to see this.

    Anyhow, I'll assume shower with 1 1/2 drain limits the number of shower heads, and lends itself more easily to clogs.

    Thanks
    Last edited by Footman_75; 07-12-2012 at 09:59 AM.

  4. #4
    DIY Junior Member centurion's Avatar
    Join Date
    Jan 2009
    Location
    New Jersey
    Posts
    10

    Default

    I can's speak for Canada, but here in NJ 1 1/2 is allowed if there is 1 shower head. I understand the concerns that some may have. However, it would seem to me that if it has worked OK for 25 years it should not be a problem.

  5. #5
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    As I understand the reasoning behind the 2" drain requirement is this lessens the chance of a clog which would result in an overflow. In my opinion, your drain falls in the grandfather clause, so I would leave it. New shower heads are supposed to be limited in gpm, so there is little chance of a problem. We got along with 1-1/2" shower drains for many years and mostly without problem.

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,403

    Default

    Code allows it in Canada, and there are millions of places with shower drains that size. It is much better to have a larger one, but people are generally happy with what they have. The reasoning for the larger drain is to ensure if you accidentally stand on the drain or drop the washcloth, you might notice it before it overflows the shower curb. It is also necessary if you have a high flow or multiple showerheads. Showerheads meeting current codes are pretty low-flow, much less than those of old which helps, too. Most tubs are 1.5", and many are used as showers, but they can hold a LOT more volume than a typical shower before overflow, AND they have a secondary, overflow path down the drain that usually works.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7

    Default

    1-1/2" is allowed in the OBC...with 1 shower head, and is common practice in Ontario

  8. #8
    Renovating Footman_75's Avatar
    Join Date
    Jul 2012
    Location
    Ontario, Canada
    Posts
    34

    Default

    1) Thanks to all for the input.

    2) Other option is to tie shower drain to toilet drain using a 3x3x2 low heel, or 3x3x2 side inlet. (See image below.) If I understand correctly, this complicates matters, as it will require a vent for the new shower drain (pls correct me if I am wrong). Further, the only feasible way to vent the shower drain would likely incur a downhill slope. Note that slopes are not to scale in the image.

    That said, the existing vent was formerly an LV drain and presently has no fixtures upstream from this diagram. So, worst case, backed-up shower vent would drain down the old LV drain. Still, it's ugly and likely not code. Pls comment on any other concerns over this option.

    Thanks again. Feedback is greatly appreciated.

    Name:  Drain 2.jpg
Views: 1514
Size:  21.0 KB

  9. #9
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    You can't vent using a down hill slope.
    If the shower vent was tied into a lav waste and vent, that would work. The lav would wet vent the shower. The lav piping needs to be 2" for it to work as a vent. And it has to grade up, not down.
    The drawing above wouldn't pass anywhere.

    If you go with a 1.5" shower drain and vent, you can't wet vent it.
    Last edited by Terry; 07-13-2012 at 10:27 AM.

  10. #10
    Renovating Footman_75's Avatar
    Join Date
    Jul 2012
    Location
    Ontario, Canada
    Posts
    34

    Default

    Thanks Terry.

  11. #11

    Default

    from your drawing, why not keep the new vent (yellow) sloped properly and tie into old lav vent above floor, or above FLR of lav if its still to be used for lav

  12. #12
    Renovating Footman_75's Avatar
    Join Date
    Jul 2012
    Location
    Ontario, Canada
    Posts
    34

    Default

    @mikeplummer

    Exactly what I was thinking. Trick will be making all this happen between joists. Right now, am planning for yellow vent to go right instead of left, through a joist bridge, then up a wall cavity about 8" away. From there, clear run to attic.

    I will follow up with diagram.

  13. #13
    Renovating Footman_75's Avatar
    Join Date
    Jul 2012
    Location
    Ontario, Canada
    Posts
    34

    Default

    ITEM A: Yellow vent drops into 2" shower drain from the top
    ITEM B: Run is 45 deg to shower drain

    Does this eliminate horizontal venting?

    Name:  Drain 3.jpg
Views: 1736
Size:  23.4 KB

    Name:  Drain 4.jpg
Views: 2391
Size:  29.2 KB
    Last edited by Footman_75; 07-13-2012 at 01:07 PM. Reason: added another angle of diagram.

Similar Threads

  1. Oatey "no-caulk" drain leaking in shower w/ acrylic pan
    By supermattthehero in forum Shower & bathtub Forum & Blog
    Replies: 12
    Last Post: 02-12-2012, 11:03 AM
  2. TOU Billing comes to Ontario
    By LLigetfa in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 03-25-2011, 09:58 AM
  3. Which cities in Canada have the "No Plastic" shower drain codes?
    By johnfrwhipple in forum Canadian Plumbing Code Questions
    Replies: 1
    Last Post: 01-07-2011, 11:02 PM
  4. how to connect plastic shower drain to 2" copper drain line?
    By showerpain in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 01-31-2007, 08:36 AM
  5. shower base with 1 1/2" drain or 2"?
    By Carpenter in forum Shower & bathtub Forum & Blog
    Replies: 6
    Last Post: 11-29-2005, 12:08 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •