Thread: 2nd floor powder room directly over exist. basement full bath

  1. #1
    DIY Junior Member baltimorecaesar's Avatar
    Join Date
    Jul 2012
    Location
    Baltimore, MD
    Posts
    4

    Default 2nd floor powder room directly over exist. basement full bath

    I'm in the process of installing a 2nd floor powder room directly over an existing full bath in my basement which I am also in the process of a gut/remodel as well. The powder room will take the place of an existing closet, so I need to run all new plumbing to service the toilet and sink. I sketched up a diagram of the waste-vent system in CAD to help illustrate what I'm trying to run. All horizontal drains & vents will be sloped at least 1/4" per. foot.

    Thoughts? Suggestions?

    Thanks in advance
    Name:  mPR-3D-ISO - Copy.jpg
Views: 574
Size:  46.4 KB
    Name:  mPR-3D-RT-ISO - Copy.jpg
Views: 177
Size:  46.1 KB

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    No vent can be less than 45 when below 42" above the floor. No inspector will allow a loop vent on that sink. You must tie a proper vent into the vent-to-roof.

    Basically, there is NOTHING in your diagram which will pass code.

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    Yep and furthermore that waste line needs to go all the way to the basement and tie in to the lateral there if the "stack" is the vent for the downstairs fixtures.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  4. #4
    DIY Junior Member baltimorecaesar's Avatar
    Join Date
    Jul 2012
    Location
    Baltimore, MD
    Posts
    4

    Default

    alright, how about this:
    Name:  mPR-3D-ISO.jpg
Views: 131
Size:  48.8 KB
    Name:  mPR-3D-RT-ISO.jpg
Views: 129
Size:  43.6 KB
    Also, there is a separate dry vent for the basement fixtures.

  5. #5
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    The lav is not vented
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  6. #6
    DIY Junior Member baltimorecaesar's Avatar
    Join Date
    Jul 2012
    Location
    Baltimore, MD
    Posts
    4

    Default

    Quote Originally Posted by Tom Sawyer View Post
    The lav is not vented
    The problem is that the wall that the sink is against is an exterior load bearing wall, so I wanted to avoid boring through the wall studs to get the sink vent to the existing vent stack. The only other solution I could come up with, would be to run the sink vent straight up the wall, go through the top plate, tear out the ceiling and T into the vent stack between the 2nd story ceiling and the 3rd story floor (See revised drawings).

    Name:  mPR-3D-ISO.jpg
Views: 219
Size:  41.0 KB
    Name:  mPR-3D-RT-ISO.jpg
Views: 136
Size:  40.9 KB

    Is this better?

    And thanks for the helpful advice all.

  7. #7
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    Yep, that be what you need to do to vent the sink properly
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  8. #8
    DIY Junior Member baltimorecaesar's Avatar
    Join Date
    Jul 2012
    Location
    Baltimore, MD
    Posts
    4

    Default

    Quote Originally Posted by Tom Sawyer View Post
    Yep, that be what you need to do to vent the sink properly
    Cool beans. Thanks again Tom and Jimbo.

Similar Threads

  1. Powder Room Toilet
    By DownTheDrain in forum Toilet Forum discussions
    Replies: 7
    Last Post: 05-31-2011, 10:54 PM
  2. Adding a full bath to basement
    By handyman7 in forum Remodel Forum & Blog
    Replies: 5
    Last Post: 09-23-2007, 08:40 AM
  3. Powder room plumbing
    By Zach in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 07-31-2007, 07:21 PM
  4. Powder Room Venting?
    By sandyman720 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-05-2007, 04:32 PM
  5. Powder Room SMELLS!
    By Sincraft in forum Toilet Forum discussions
    Replies: 7
    Last Post: 09-04-2006, 11:13 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •