Thread: Using a HVAC Condensate Pump or Directly Connecting to Sewer Line w/trap

Hybrid View

  1. #1
    DIY Senior Member DanMcD's Avatar
    Join Date
    Jun 2005
    Location
    Dayton, OH
    Posts
    121

    Question Using a HVAC Condensate Pump or Directly Connecting to Sewer Line w/trap

    I like some advice on whether I should install a Condensate Pump for my HVAV or just have a plumber directly connect it to my sewer line and use a trap to prevent sewer gas from entering my furnace install. I am having my entire cast iron sewer lines replace with PVC, so I need to decide on how to do this correctly.

    Below is some background info on what I have now...

    My current furnace setup has the A/C & Humidifier draining directly into my 2 inch cast iron sewer line which is under my crawl space. It has been like that for 35 years and has always worked. When this was first installed, the HVAC person:
    (1) Connected the HVAC inch PVC to a inch piece of copper pipe.
    (2) He then bent the copper pipe to make a trap before it would enter my 2 inch cast iron sewer line. This 2 inch cast iron pipe is the drain for my laundry tub.
    (3) He then drilled a hole into the 2 inch cast pipe and connected the inch copper and added silicone caulk. FYI, the 2 inch cast iron pipe connects downstream to my 4 inch cast iron main sewer line.

    What is the best method/correct way to drain my HVAV?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,437

    Default

    All traps should be separately vented to prevent siphoning the trap dray. There is no guarantee that between the humidifer or a/c it will drain often enough to keep the trap that's there full.

    Most people either run it outside if there's no danger of freezing and it can be accommodated reasonably, or, dump it into something like the sump pump, or drain it into the top of the washing machine stand pipe.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default

    You can be ABSOLUTELY certain, that in the winter time, there will be ZERO condensation to keep the trap sealed, therefore the blower unit WILL suck sewer gases into the system and distribute them throughout the house. Either connect it to a fixture's trap connection or use a pump.
    Licensed residential and commercial plumber

Similar Threads

  1. Connecting 3.5" IPS to ABS for sewer line extension
    By MrsTiki in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 18
    Last Post: 01-20-2012, 07:18 PM
  2. HVAC Condensate Pump
    By mallengold in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 12-12-2010, 10:04 AM
  3. Condensate Line to Sewer Pipe, NSPC
    By PrezMFL in forum NSPC Plumbing Code Questions
    Replies: 12
    Last Post: 06-07-2010, 08:55 AM
  4. Condensate Line to Sewer Pipe, NSPC
    By PrezMFL in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 06-07-2010, 08:55 AM
  5. Condensate drain line as trap prime
    By michael-thomas in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 12-23-2005, 06:11 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •