I'm working on a new renovation with new wiring and access to the open framing. I would like to prevent air leakage around all electrical boxes.
One thought I have is to use expanding foam around the outside of the boxes. Is this OK?
Thanks in Advance,
Bill
Last edited by molo; 06-24-2012 at 09:18 PM.
"Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
Gore Vidal.
Depends on the foam
read the instructions
Google is your friend. Search for:
fireblock foam electrical
I talked to a rep. at Dow today. They said that their standard "great stuff" foam is OK around electrical boxes and insulated wires. However, it is not OK inside the box or in contact with bare copper.
"Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
Gore Vidal.
if i were you, i wouldn't use the normal great stuff. get the stuff for windows and doors. it does not expand as much and will not push your boxes out of square if you use too much. it will bow window frames if used incorretly, i've done it myself.
I doubt that fireblock caulk or foam is required. The OP is not sealing fire rated areas, except for maybe floor penetrations and that is only is the floor is a rated assembly.