Thread: Air Sealing Electrical Boxes (Expanding Foam.)

Hybrid View

  1. #1
    DIY Senior Member molo's Avatar
    Join Date
    Sep 2006
    Location
    cold new york
    Posts
    840

    Default Air Sealing Electrical Boxes (Expanding Foam.)

    Hello,

    I'm working on a new renovation with new wiring and access to the open framing. I would like to prevent air leakage around all electrical boxes.

    One thought I have is to use expanding foam around the outside of the boxes. Is this OK?

    Thanks in Advance,
    Bill
    Last edited by molo; 06-24-2012 at 09:18 PM.
    "Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
    Gore Vidal.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Depends on the foam
    read the instructions

  3. #3
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by molo View Post
    Hello,

    I'm working on a new renovation with new wiring and access to the open framing. I would like to prevent air leakage around all electrical boxes.

    One thought I have is to use expanding foam around the outside of the boxes. Is this OK?

    Thanks in Advance,
    Bill
    There are specific foams for closing holes drilled to chase NM thru framing. Look at some of that.

  4. #4

    Default

    Quote Originally Posted by Homeownerinburb View Post
    There are specific foams for closing holes drilled to chase NM thru framing. Look at some of that.
    Anyone know what this foam is and where it can be found?
    If I remember correctly, my memory is excellent, but my ability to access it is not.

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,687

    Default

    Google is your friend. Search for:

    fireblock foam electrical

  6. #6
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by LLigetfa View Post
    Google is your friend. Search for:

    fireblock foam electrical
    Amen.

    I saw rows and rows of it at Home Despot just yesterday.

  7. #7
    DIY Senior Member molo's Avatar
    Join Date
    Sep 2006
    Location
    cold new york
    Posts
    840

    Default

    I talked to a rep. at Dow today. They said that their standard "great stuff" foam is OK around electrical boxes and insulated wires. However, it is not OK inside the box or in contact with bare copper.
    "Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
    Gore Vidal.

Similar Threads

  1. Electrical Engineer allowed to do Electrical work?
    By willijimon in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 03-05-2009, 05:08 PM
  2. Hidden electrical boxes in ceiling.
    By ScottTENN in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 11-30-2008, 11:40 AM
  3. Connecting low-voltage conduit to electrical boxes
    By Taylor in forum Electrical Forum discussion & Blog
    Replies: 21
    Last Post: 06-24-2008, 04:02 PM
  4. ground electrical boxes
    By geandham in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 01-29-2008, 04:11 AM
  5. 1-1/2" deep multi-gang electrical boxes
    By Lakee911 in forum Electrical Forum discussion & Blog
    Replies: 39
    Last Post: 01-19-2008, 08:46 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •