Lavatory Drain

Users who are viewing this thread

JB412

New Member
Messages
24
Reaction score
0
Points
1
I am helping my son in law install a bathroom in his basement that was plumbed with drain and water lines when the house was built 2 years ago. The toilet and tub were no problem. Where I do have a problem is with the drain for the lavatory. The floor drain is centered between the water lines. Because they went with a 48" lavatory, it puts the center of the lavatory drain about 18" from the floor drain pipe. What is the correct way to deal with this? Do I put the trap directly under the lavatory drain then run a horizontal pipe over to the floor drain and elbow it down at that point, or do I com down from the lavatory draw, install an elbow and run horizontally over to a trap and striaght down to the floor drain? Any help would be appreciated.

Jerry
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Actually NEITHER, without a vent the drain will NEVER operate properly. Whoever installed the drain, (and, the trap should be under the sink, NOT be under the floor), should have put it in the wall with a vent going upward, OR it was installed that way, but you moved the wall so the pipes are under the sink and could not continue the vent the way it was designed.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks