    Default Slowing a Capacitor-Start pump motor

    I bet someone here knows how to do this:

    Picture a water transfer pump, a Tsurumi LB480, submersible, 2/3hp, 230v, 1ph, 60 hz, capcitor-start...I want to slow the GPM it delivers and I am thinking that slowing the frequency will slow the motor and slow the GPM flow rate.

    I have checked around with my friend Google, but after writing the manufacturer reps, I am told they don't have a device. I asked at Davis for AC Drive / Frequency Inverter, 200-240 VAC single or three phase input with 3 phase output, 2.4 max. ; not suitable, 3 ph out..
    Well, I do agree that slowing down the frequency of the power will slow down the pump. I know that can be a problem when running 60hz equipment (like fans) internationally because they often only have 50Hz. But I don't have the right equipment to offer to do that with the pump you have
    Tsurumi says it is possible and OK to use a VFD on the pump, just not above 60hz. The VFD's I reviewed are not suitable for the capacitor-start.

    The motor has blk, wht, green wires, to be used in the US, 110/220/1ph,60hz.

    b

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    Install a valve on the DISCHARGE pipe from the pump and you can throttle it to any GPM you want. It would not work on the inlet to a pump, even if there were a way to do it.
    Licensed residential and commercial plumber

  3. #3
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    It would need to be a permanent,split, capacitor motor to be slowed down. Cap start and other single phase motors need to reach full speed quite soon or the starting winding will fail.

    Hj has a good idea. An added benefit of clamping down on the water is the extra back pressure will be easier on the motor.

  4. #4
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,675

    Default

    Quote Originally Posted by hj View Post
    Install a valve on the DISCHARGE pipe...
    +1
    A dole valve is a common and acceptable way to reduce the GPM output. Did you want to reduce the GPM or vary the GPM and why?

  5. #5
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by hj View Post
    Install a valve on the DISCHARGE pipe from the pump and you can throttle it to any GPM you want. It would not work on the inlet to a pump, even if there were a way to do it.
    As long as it is a centrifugal pump, that would be fine. That could even reduce the current the motor will draw; less GPM transferred means more water just spiining around inside the pump body, using less work to get stationary water in motion.
    I am definitely not a pro plumber, but I am a pro crastinator

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    As long as there is some flow. Completely stopping the flow would cause the water to heat up and turn to steam, then cavitation would damage the impellers.
    Licensed residential and commercial plumber

  7. #7
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by hj View Post
    As long as there is some flow. Completely stopping the flow would cause the water to heat up and turn to steam, then cavitation would damage the impellers.
    That makes for a really bad day.

Similar Threads

  1. start capacitor size
    By dragnuts in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 01-24-2012, 10:04 AM
  2. Heat Pump Capacitor
    By sir_belrak in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 10-07-2011, 01:32 PM
  3. Capacitor for 1hp submersible pump
    By jk76 in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 07-02-2011, 03:24 PM
  4. 1994 Furnace won't start up - bad induction draft fan motor?
    By completelyhis in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 10-11-2010, 11:09 AM
  5. Flush force slowing
    By jaybird in forum Toilet Forum discussions
    Replies: 5
    Last Post: 05-01-2006, 06:17 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •