Replace all Wiring that was Stolen any great suggestion???????????

Users who are viewing this thread

Chad Schloss

Member
Messages
327
Reaction score
0
Points
16
Location
USA
"general purpose circuits are not being observed while I am at work or in bed asleep."

i would like to see ANY stats on home fires or any problems being caused by using 12ga vs 14ga. i really think that if this was as big of a problem as you propose, there would be a very rapid change in the code, requiring only 14ga wire to be used.

i really think that you should start lobbying lamp makers and extention cord makers to require OCP in their wire or device. I think you would be a great person to lead that fight. either that, or maybe lobby for 5 and 10a breakers on general purpose circuits.
 
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
why then are we required to wire not one, but two small appliance branches for kitchen appliances at 20a each for appliances that require 15a? how about the requirement for bathrooms to have a separate 20a GFCI circuit dedicated to just the bathroom, for a 1500w hairdryer that can run on 15a?
In my kitchen I have a 1.4kw coffee pot, 1kw crock pot, 1.1kw toaster, 1.2kw deep fryer, and the list goes on and on. Recon all this would run off of one 15 amp circuit? Should I have all of these going at one time the two 20 amp circuits would hold them either.
Your hair dryer exceeds what is allowed to be on a 15 amp circuit.
why then are 15 a recepts rated at 20a feed through?
It is permissible to wire the incoming cable to one end of a receptacle and the outgoing cable to the other end of the device. Should this method be used on a 20 amp circuit then the receptacle would need to be rated at the same as the overcurrent device protecting it.
This in no way means that the blade slots of a 15 amp receptacle is rated any more than 15 amps. The only part of a 15 amp receptacle that is rated at 20 amps is the fin tab between the two screws not the entire receptacle.

There is no one condemning your installation but I think you need to understand what a 20 amp circuit for general purpose circuits entails. The train of thought that a 20 amp circuit is better than a 15 amp circuit for general purpose receptacles has a flaw. All I have done is point out those flaws. I have also pointed out that most of the required 20 amp circuits while in use will be monitored while in use such as the bathroom receptacle unless someone knows how to blow dry their hair while asleep. The same is true for the laundry and small appliance circuits but the general purpose circuits are used while we are at work and asleep. These circuits are used more than those required by 210.11(C) for dwelling units.

Back in the late ‘60s and ‘70s many homes were wired using all 20 amp circuits. After many problems this practice fell by the way side except for those who were so closed minded to see the dangers. This lingers till this day with many who cannot see the nose on their face.

What is overlooked by most electricians and inspectors today is the two small appliance (210.11(C)(1)), the laundry (210.11(C)(2)), and the bath (210.11(C)(3)) circuits when used with a 15 amp receptacle (Table 210.21) is still no more than 12 amps for cord and plug appliances which leaves out the use of your 1500 watt hair dryer. 1500/120= 12.5
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
i would like to see ANY stats on home fires or any problems being caused by using 12ga vs 14ga. i really think that if this was as big of a problem as you propose, there would be a very rapid change in the code, requiring only 14ga wire to be used.

i really think that you should start lobbying lamp makers and extention cord makers to require OCP in their wire or device. I think you would be a great person to lead that fight. either that, or maybe lobby for 5 and 10a breakers on general purpose circuits.

Do an internet search of the Office of the State Fire Marshall in your state for the fire stats.

I have and still do work with the NFPA as well as with IEEE, IAEI, NEMA, NCDOI, and several others for safer electrical installations throughout our land.

Take a good look at the committees and officers of this web site for more information;
http://www.nciaei.org/

My name is Mike Whitt. The IAEI works with those mentioned above for safer electrical installations and as you can see I hold a couple of seats with the NCIAEI. Google search a few of the names that are beside of mine to see just who I work with daily.

Those things I have pointed out are facts that can be proven using math. I have not nor will I ever say that it is not code compliant but I have always said and will keep saying that the adage that 20 amp circuits are better is flawed. There is not one thing that can be said to make a 20 amp circuit safer than a 15 amp circuit no matter how one tries to put it into words.

Along with the committees and boards that I sit on I have over 44 years of experience in the field and more than 12 years in the classroom. I have dedicated my life to the electrical trade and the safety involved with the use and installation of electrical systems.
 

Chad Schloss

Member
Messages
327
Reaction score
0
Points
16
Location
USA
no, i wanted JW to answer, that's why I had quoted him. Nothing against you (or him) just wanted his answer.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
no, i wanted JW to answer, that's why I had quoted him. Nothing against you (or him) just wanted his answer.

And as you can see my answer is almost the same as Home's answer just used different words.
When someone asks a question and someone gives the answer most of the time I will remain silent and leave their answer alone but once in a while someone will take personal an answer thus a debate is started between two instead of the forum. I try to keep this from happening by not saying anything when someone else gives the answer therefore I didn't answer directly.

We need to remember that this is a “Do-it-Yourself” type of web site where for the most part the members have no experience or knowledge of electrical theory and installations. The knowledge that most have are old wives tales past down from one to another and in most cases these methods are wrong.

A good case in point is the installation of 20 amp general purpose circuits throughout a home is better than 15 amp circuits. Are these installations compliant? Yes. Are they safer? Not according to the math.
Another is to keep the lights and receptacles on two different circuits so in the event of a breaker tripping one won’t be left in the dark. In 60 years of living I have been left in the dark by a power failure 1000 times for every one time I was left in the dark over a tripped overcurrent device so there is a flaw in that thinking.

What I find most interesting is that when someone points out one of these flaws to the old wives tales most take it personally or as an attack instead of keeping an open mind to the points of views of others especially when the one giving that advice has credentials far above theirs.

As I have pointed out several times in this thread the installation of 20 amp general purpose receptacles is a compliant installation but to think that this circuit somehow gives me more amperage so I can vacuum while watching a DVD on the big screen through the sound around system has flaws.
I like the one where the 20 amp circuits were installed so portable electric heaters could be used. The 20 amp breaker and number 12 conductors in no way change the maximum load that that 15 amp duplex receptacle will handle.
It has been my experience over the years that the receptacle fails and all that wasted natural resource did nothing to prevent the failure.
Ever plug something into a receptacle and the cord cap just fall out? What did we do? Spread the prongs apart a little so it would stay in place?
The receptacle was loaded to the point that the spring metal in the slots have weakened to the point of no grip or the receptacle has failed. No amount of oversizing the conductors and overcurrent device will fix this problem. Upgrading the circuit to 20 amps only causes the failure to happen quicker as we can now put a larger load on that 15 amp receptacle.

This is the facts no matter what someone has told you. This is real world installations that through my career I have personally witnessed as well as many others that I have talked with through my years of experience in the electrical trade.

Then we have those who make the statement that a 15 amp receptacle is rated for 20 amps of feed through. This is true. The metal between the two screws is rated at 20 amps but should someone take the time to take a 15 and 20 amp receptacle apart it is easy to see that the blade slots of the two are a lot different. What we must know is that a 15 amp receptacle even on a 20 amp circuit is rated for 12 amps. The fact that it is on a 20 amp circuit does not change this nor does it change the cord we use to plug in our appliances. The cord is installed by the manufacturer and in most cases will handle a fraction of the amperage of the branch circuit. Up grading the amperage of the circuit then allows more current to flow through these cords. One does not need a formal education to know that the more heat energy allowed to flow through a conductor will allow it to break down faster.

Once again, is it compliant to install 15 amp receptacles on a 20 amp circuit? Yes. Is there more danger when doing this? Yes especially on the general purpose circuits that for the most part are overloaded in the first place.
It is better to install two 15 amp circuits than to install one 20 amp circuit.
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
I installed 20 amp receptacles in my house on 15 amp circuits and my plugs almost require pliers to remove. Seems like a safe investment. And the worst that happens is the tv goes off when you iron on the same circuit.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I installed 20 amp receptacles in my house on 15 amp circuits and my plugs almost require pliers to remove. Seems like a safe investment. And the worst that happens is the tv goes off when you iron on the same circuit.

Right in the middle of your favorite soap opera ?

I hate when that happens.

Why not upgrade to a 20 amp breaker ?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
The NEC mandates that in addition to other circuits required at least one 20 ampere “LAUNDRY” circuit is to be installed. See 210.11(C)(2)

I know that in this world that some think the codes says washing machine circuit but instead it says laundry. Ironing is part of doing laundry so guess which receptacle the electrician installed for the iron?

Should someone decide to do the ironing in the middle of the living room they would to let the electrician know before wiring the house that there needs to be a laundry receptacle installed at the place where the ironing is to take place.

Take a high end iron even a 20 amp receptacle and circuit is not big enough. Should that TV be plugged in the laundry receptacle then the iron would have the same effect. The receptacles in the living room for the TV and the receptacle installed for the washing machine for the iron. This is how the codes have it set up.

On a side note, when we did our room addition I plugged in the air compressor in the bed room receptacle. The air compressor draws 12.8 amps when running. The point here is we can plug in whatever we want where ever we decide to plug it in but if the installation is compliant the worst thing that can happen is the breaker trip.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
The NEC mandates that in addition to other circuits required at least one 20 ampere “LAUNDRY” circuit is to be installed. See 210.11(C)(2)

I know that in this world that some think the codes says washing machine circuit but instead it says laundry. Ironing is part of doing laundry so guess which receptacle the electrician installed for the iron?

That is pretty much useless for Ironing clothes and watching TV.

Most Utility or “LAUNDRY” Rooms do not have room for a Ironing board, or Wide screen TV.
Or a extra outlet for the Iron and TV, or a cable hookup.

And not many people Iron Clothes in their garage.

I thought every thing was perm press anyway.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
And as you can see my answer is almost the same as Home's answer just used different words.

One item that Chad seemed to need explained to him: why is it ok for the general purpose (lighting) circuits in the house to be 15 amp when the three or four circuits are specified at 20 amp?

You are much closer to this discussion than I will ever be, but it seems to me that the code is evolving to ensure that every component of the system is slightly under-utilized. That is, to have a fail-safe margin. Electricians can make poor joints when twisting wires together (not me), we can stress a conductor pulling it (OK, I know I have) and a dozen other factors can make a 12 ga conductor weak at 15 amps.

I would not be surprised if at some time the ratio of watts to sq ft in general purpose circuits changes to demand more circuits.

As a fully practical matter: to work with 14 ga is just faster and easier than 12 ga. Often one guy can do the first where using the 12 ga will demand a helper. And the material is profoundly more expensive for the 12 ga.

Instead of thinking "let's build in a big fat safety margin and wire it all at 20amps", I prefer to put in one more 15 amp circuit than is utterly needed. It really is hardly any more material, and it goes just as fast, and if one is half smart about how the house is split up, one does OK sharing the load among the circuits.

As for requiring 20 amp circuits in the kitchen etc, we go back to the matter of building in a margin. There are appliances used in kitchens and bathrooms and the laundry that will get past 80% of 15 amp on a regular basis.

Somebody asked why don't we require that the house be wired with 7 amp circuits, if higher ratings are so dangerous. I suppose that would be possible. Of course, it would be hideously inflexible compared to a 15 amp circuit, which could serve several rooms and not be stressed, where a 7 amp circuit could find itself loaded with an entertainment center and have no margin for a few lights and the proverbial vacuum.

The answer is that the line needs be drawn somewhere. Two common amperages to be found at classic Edison outlets, and the professional electrician knows which goes where, and the home owners concern themselves with paying the mortgage and getting the kid to earn decent grades.

15amp is safer, cheaper and easier. What is not to love? Where 20 amp is needed, put it in.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Guess I just don't get it.

I don't really see the big deal with having 20 amp circuits and why they are not safe.

It takes a lot less current to kill you so 15 amps is just as dangerous when it comes to electrical shock.

As long as the wiring is correct I do not see the big problem.

I would rather have larger wiring and less voltage drop. When voltage goes down current goes up.

My breaker panel does not have any 15 amp breakers, the 120V breakers are all 20A.

So does that make my house unsafe ?

All the houses around here were built by the same builder, so I would think that they are all wired the same.

Do we need a House oversize Wiring/Breaker Recall ?

Voltage drop is more of a problem for appliances than having to much current available than required to operate it.

What am I missing here ? Other than low voltage at my outlets when I plug in a heavy load.

To be totally safe you can always turn your Main Breaker off and deal with the candle fire damage.


Guess I just don't get it.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I don't really see the big deal with having 20 amp circuits and why they are not safe. It takes a lot less current to kill you so 15 amps is just as dangerous when it comes to electrical shock. As long as the wiring is correct I do not see the big problem.
I don’t believe that anyone has said that there is a problem installing 20 amp general purpose (those circuits in the bedrooms, living, outside, ect) or that they are dangerous.
If one would read this with an open mind one could see that there are draw backs to installing 20 amp general purpose circuits and the claim that 20 amp circuits are better than 15 amp circuits has flaws.

I would rather have larger wiring and less voltage drop. When voltage goes down current goes up.
unless you have circuits a thousand feet long in your home then VD is no problem. The voltage drop on the utility side can’t be fixed with oversized circuits. Case in point, At my house the voltage to ground at my service in off peak hours is ~ 127 but during peak hours can be down to ~115.



My breaker panel does not have any 15 amp breakers, the 120V breakers are all 20A. So does that make my house unsafe ?
Generally speaking no, but in some cases yes

Voltage drop is more of a problem for appliances than having to much current available than required to operate it.
this is untrue. If it were true then every time that your heat or AC unit started up your appliances would have a problem. I have seen my brothers voltage at his service as low as 107 volts with on problems.

What am I missing here ? Other than low voltage at my outlets when I plug in a heavy load.
You seem to be overlooking things such as extension cords, supply cords, plug strips, surge protectors that will have either 18 or 16 gauge conductors that are protected at 20 amps instead of 15 amps.

Guess I just don't get it.
The first part of getting it will be to open your mind. I didn’t get it either until I opened my mind to the words of others that had lot more experience than me in current flow.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Thank You Mike for breaking that all down for me so that I could understand it better.

Most if not all consumer products that are sold today have built in protection.

Even some of those Cheap if not All extension cords have a fuse link built into the Plug.
People think the plug is bad, when really the fuse link opened. They replace the plug and it works again, but now with no fuse link.

Most power strips have 10, 12 Amp or 15 Amp breakers built in.

A 1000 watt microwave will have a 15 Amp fuse on the input before the surge protector.

Most everything that connects to a AC outlet has built in protection of its own. Tell me what really don't ?


We are not flying a Shuttle here, and the Redundancy is more problem than worth worrying about.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Okay for the sake of argument let’s say that everything has built-in overcurrent protection of some sort

The laws of current flow say that current will stop flowing at the place where the overcurrent is located. So now please explain what is protecting the conductors from the male end of the cord to where this overcurrent is located?

If the insulation is cracked and is beginning to have a buildup of carbon in this crack to the point that it is conducting current what would role would internal overcurrent play for this situation. That built in overcurrent device would never see that current.

Ever see a picture of a conductor that was discolored due to a loose connection? Why didn’t the overcurrent device on that conductor open? I have seen the ends of cords both on appliances and extension cords that was disfigured due to heat. Why didn’t the internal overcurrent devices open?

When we up size from 15 to 20 amps we allow at the very least 600 watts (5 amps times 120 volts) more heat to flow across this continually and a surge up to 4000 more watts.
Again I am not saying that the use of 20 amp general purpose circuits is illegal in any way. What I am saying is that a 20 amp general purpose circuit has flaws so to say one is better is incorrect.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
Again I am not saying that the use of 20 amp general purpose circuits is illegal in any way. What I am saying is that a 20 amp general purpose circuit has flaws so to say one is better is incorrect.

I'll bang this drum one more time: for the contractor, installing 15 amp is better. It costs less in materials, and it goes in faster. It is a whole lot easier to stuff the wires into the boxes. I often can install 14ga by myself where I would need help with 12ga.

As there is no advantage to having the general purpose circuits set at 20 amp (that I can see) I am more than ready to say that one is better than the other. And now that I am thinking of the unnecessary extra current available to cook a deteriorating cord, I am even more adamant.

In some systems elsewhere in the world, plugs have replaceable fuses incorporated, and the fuse is rated to protect the device the plug is connected to. I know that this is practice in Britain, although I don't know if it is required of every item with a plug.

I suppose that Congress could pass a law requiring a similar system here: your clock radio protected at one amp, your blender at four, etc.

And then there would be all sorts of tiresome crying of the "Nanny State", from the same cretins who complain that 125 year old lighting technology should be abandoned for technology that is four or ten times as efficient.
 