    Question well pump cutting on and off.

    So I have just finished installing and calibrating my do it yourself irrigation system. And after a few days of flawless performance, my pump is now acting up. Let me caveat with I have a digital timer and solenoid valves where I should be able to run this fully automatic. But I have a small leak in my manifold I haven't fixed yet so I have been operating it manually. I did not install the pump relay as I don't fully understand it and my thoughts were that when left in auto mode, the pressure switch on the well pump should turn the pump on and off as necessary. When all 3 valves are closed, pressure is maintained at 65 psi and will not run, when the system pressure drops below 20 psi, the pump will kick back on from the pressure switch. And it worked fine like this for about 3 days.

    However now my pump is kicking on and off repeatedly when trying to irrigate a zone. The gauge pressure jumps up to about 50psi, pump kicks of, pressure drops below 20psi, pump kicks on - and this repeated on and off cycle is in fractions of seconds. So the stream coming out of my heads is pulsating with the pump motor as it kicks on and off. And the worst part of troubleshooting, this doesn't happen every time. But right now it is about 50/50.

    Well pump is the Myers HJ100D and the timer is Rainbird SST-900i.

    I just put out 6 pallets of St. Augustine sod on Friday...please help if you can. Thank you in advance!!!

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,685

    Default

    What size pressure tank do you have? Try turning up the kick-out pressure to keep the pump running.

  3. #3
    DIY Junior Member rikmoor's Avatar
    Join Date
    Apr 2012
    Location
    Wilmington, NC
    Posts
    7

    Default

    Since this is purely to feed an irrigation system that is capable of delivering adeuate flow and pressure with a continuous running of the pump, I did not install a pressure tank. During irrigation, this tank would never fill to provide pressure. My zones are running at 10 gpm therefore this pressure tank would merely be a "flow-through" device. And if it did build pressure intermittently, I wouldn't want the pump cutting on and off that frequently. Because unless I had a huge pressure tank, the pump would kick on and off every minute or so. The cycling would be too rapid in my opinion.

    These are just my thoughts - I'm a civil engineer so I'm not totally uneducated in the logic of how these things should work, but I'm not a specialist in irrigation by any stretch. Feel free to correct me if my logic on the pressure tank is flawed.

    I may try what you said and increase the pressure on the switch to something higher than the current limit of 70psi and see if that makes a difference. Is there a max pressure that I should be using here? When I get this thing working in fully automatic mode, I hate to have it sitting idle between irrigating cycles at something like 100 psi.

    Thanks again for the help in these forums!

  4. #4
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Quote Originally Posted by rikmoor View Post
    Because unless I had a huge pressure tank, the pump would kick on and off every minute or so.
    And if you don't have a tank, the pump will kick on and off every second or so! Never use a pressure switch without a pressure tank. And no matter the size of the tank, every zone has to exactly match the outout of the pump or the pump will cycle itself to death. You have three choices....

    1) Add a pressure tank and make sure every zone matches the output of the pump.
    2) Add a small pressure tank and a CSV, then you can make the zones any size you want.
    3) Use a pump start relay from the irrigation controller instead of a pressure switch.

  5. #5
    DIY Junior Member rikmoor's Avatar
    Join Date
    Apr 2012
    Location
    Wilmington, NC
    Posts
    7

    Default

    10-4 valveman. Hear ya loud and clear. I am going to go the route of the pump start relay. So to disconnect the pressure switch, do I just need to remove the tube that connects it to the pressure regulator? And do I need to physically remove it from the pump? Best I can recall it was integral to the power supply connection to the pump itself. Also, is it safe to assume the pump start relay will come with a wiring diagram that shows how it connects to my power source and pump? I read a little on the Rainbird tech support for troubleshooting and have a basic understanding of how it will be installed, just want to make sure it is a DIY level project. I am using a 230V power source for my pump and will obviously turn the breaker off at the power panel and disconnect at the pump before working on any of this.

    As I understand it, this relay will ensure that the pump is not maintaining pressure in the lines unless their is a zone activated by the timer. This is by far the best route since I don't really want/need to have a pressurized line from the pump to the manifold. So I'm actually pretty excited about this addition anyway.

    Thanks again for the help.

  6. #6
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    You don't have to remove the pressure switch. Just move the wires from the pressure switch to the pump start relay. Also need a good pressure relief valve. Pump start relays will still start the pump, even if the varmints eat the wire going to the sprinklers. A pressure relief valve will help keep the pump from melting down when this happens.

Similar Threads

  1. Pump cutting on and off ever few seconds
    By Freddyk in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 06-07-2007, 12:52 PM
  2. Cutting gas line???
    By don metzinger in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 04-12-2007, 02:37 AM
  3. Cutting swanstone
    By shamrock_94 in forum Shower & bathtub Forum & Blog
    Replies: 4
    Last Post: 01-14-2007, 08:23 AM
  4. Cutting a new vanity top
    By TedL in forum Remodel Forum & Blog
    Replies: 5
    Last Post: 12-25-2006, 04:57 AM
  5. pvc cutting
    By Zaffee in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 06-21-2006, 07:42 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •