    Default Water softener VS air injector

    I need advice. I had my well water tested and here is what I got :

    PH : 8
    Total hardness : 7
    Iron : 0.4

    I’m also having some sulfur odour in the shower only (hot water), nowhere else except for some occasional and almost unnoticeable occurrence in both hot and cold water in other faucets. But I’m worried to see this odor getting worst.

    We are 4 people living in a 2 bathroom house (1 showers, 1 bath). My pump is rated at 12GPM and I get about 10 GPM at the pressure tank.

    For this year I would like to spend around 1000$, I see two options :

    Option 1
    - Install a 1.5pounds water softener to get rid of hardness and iron ( which is staining overtime).
    - Change the water heater anode for an aluminum one for the odor in hot water.
    - Install a carbon filter (20” big blue) for the slight odor in cold water and hope for the best.

    Option 2
    -Install an air injector system (Terminator)with a mixing tank and iron filter for both Iron and sulfur.
    -Install a water softener next year ( Since the air injector set-up is around 1000$).

    Thank you for your help and sorry for my poor English skills (I’m French Canadian)

    Martin

  2. #2
    DIY Senior Member mialynette2003's Avatar
    Join Date
    Nov 2010
    Location
    Ocala, Florida
    Posts
    664

    Default

    If the sulfur is slight, I would go with option# 1. Your iron is not bad enough to use the air injection. I'm not fond of the air injection systems. I've seen ones that cause a back pressure on the well pump enough to pop the pressure relief valve. You could also try raising the temperture of the heater to see if the odor goes away.

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,679

    Default

    Quote Originally Posted by mialynette2003 View Post
    You could also try raising the temperture of the heater to see if the odor goes away.
    +1 on raising the temperature.

    It sounds like the smell is not from the well so I doubt aeration would help.

  4. #4
    DIY Junior Member Martin35's Avatar
    Join Date
    Jul 2013
    Location
    Québec, Canada
    Posts
    12

    Default

    Thanks for the input

    I wonder if adding a mediaguard with KDF85 media in the water softener may be a alternative to the carbon filter ? I'm also wondreing if it's restricting the flow thru the water softener?

    Thanks

  5. #5
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,707
    Blog Entries
    1

    Default

    We do a lot of media guards with KDF55 and 85. They work well, but it is critical the backwash flow control be set correctly. In most applications, a 4.5 GPM DLFC button works best. The flow will be reduced with the media guard but most people will not notice. Depending on several variables, you can expect good flow, up to 8-10 GPM without a problem through the media-guard.

  6. #6
    DIY Junior Member Martin35's Avatar
    Join Date
    Jul 2013
    Location
    Québec, Canada
    Posts
    12

    Default

    Quote Originally Posted by ditttohead View Post
    We do a lot of media guards with KDF55 and 85. They work well, but it is critical the backwash flow control be set correctly. In most applications, a 4.5 GPM DLFC button works best. The flow will be reduced with the media guard but most people will not notice. Depending on several variables, you can expect good flow, up to 8-10 GPM without a problem through the media-guard.
    Are you talking about a separate filter unit or something added to the softener like that :

    http://www.qualitywatertreatment.com...000SXT.htm#kdf

    And if it's what your talking about, is this addition affect the softener sizing ?

  7. #7
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,707
    Blog Entries
    1

    Default

    Name:  mediaguard1.jpg
Views: 183
Size:  14.0 KB

    The media guard goes inside the tank and does not affect capacity, the only change is in the DLFC rate. it is critical for the media guard to last that it be backwashed at 4-5 GPM.

    We only recommend it for 2 bathroom houses and smaller due to its flow restriction potential.

  8. #8
    DIY Junior Member Martin35's Avatar
    Join Date
    Jul 2013
    Location
    Québec, Canada
    Posts
    12

    Default

    I'm poosibly looking to buy online a Fleck 7000SXT 40000 grains (if I go the water softener way). If I understand well the DLFC is a kind of orifice flow control (the bigger the hole the bigger the flow). Is different capacity
    DFLC are available ?

    Thanks

    Martin
    Last edited by Martin35; 07-26-2013 at 11:31 AM.

  9. #9
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    The Media Guard is not a good thing and especially for your water quality issues, and it is expensive to buy and maintain.

    Raise the temp on your water heater to 140f, don't use hot water for a couple hours and then reset it to what it was. That will kill the harmless reducing type bacteria (IRB and/or SRB) responsible for hot water only odor creation. Replacingthe anode rod with a different type metal one may not cure the problem. Especially if you scrape off any of the old rod as you remove it and the material falls down into the tank. I've never seen a tank type water heater that will allow you to totally drain all the water out to flush off the bottom of the tank.... The drain valve is up on the side allowing a couple inches of gunk to stay in the tank after draining the tank.

    The DLFC controls the gpm of the discharge water flow during regeneration. It is part of the control valve and its size is determined by the type and cuft volume of the resin in the resin tank. The flow controls are usually added to the control valve by the dealer's distributor or the dealer as they build the softener. Same for the BLFC.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  10. #10
    DIY Junior Member Martin35's Avatar
    Join Date
    Jul 2013
    Location
    Québec, Canada
    Posts
    12

    Default

    Thank you for the advices.

    As my plan don’t seems to make consensus, what about start from scratch ?

    For you guys what would be the ideal set-up (equipment) for my water properties ?

    Thanks again

    Martin

  11. #11
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,707
    Blog Entries
    1

    Default

    I am not a big fan of the Media Gurds, but the companies that sell them and that know how to work with them swear by them. I have installed a few in my relatives houses to reduce the Chlorine and it is highly effective for that. For other treatment methods, it is very hit and miss.

    You need to start with turning your water heater up to the max for a few hours, using extreme caution that no kids or elderly have access to the hot water as extreme burns can occur almost instantly at these elevated temperatures. Once this is done, see if the Sulfur smell returns. If it is only on the hot water side, it is unlikely that you will need much water treatment.

    If it is on the cold and hot water side, their are many options available to you. Lets start with the heating of the water to see if this takes care of the problem temporarily. If the smell returns only on the hot water side, it is probably coming from your sacraficial anode and that should be replaced with a different type.

    The DLFC is determined by the media type, water temperature, and tank dimension, as well as a few special factors that need to be considered seperately. Turbulators and media Guards are the most common reasons to use a flow control that ignore the normal rules of Flow control sizing.
    Last edited by ditttohead; 07-29-2013 at 09:12 AM.

  12. #12
    DIY Junior Member Martin35's Avatar
    Join Date
    Jul 2013
    Location
    Québec, Canada
    Posts
    12

    Default

    Thanks

    I will try the water heater temp raise and see what happened. On the other hand I think I will need something to get rid of Iron, but let's try one thing at a time.

    Martin

  13. #13
    DIY Junior Member Martin35's Avatar
    Join Date
    Jul 2013
    Location
    Québec, Canada
    Posts
    12

    Default

    Guys

    Yesterday I’ve raised my water heater temp to the maximum (150F)for the whole night (at least 8hrs) and I did not see any improvement this morning. I will describe the situation more in detail to give you a better picture :

    -I have odor only in the shower which is the last faucets on my main line. I have odor only for the first shower of the day for about 30 seconds, as soon as the water is hot the odor goes away.

    I’ve also take a water sample directly from the water heater (thru the relief valve) and there is no odor. It looks like the odor is coming from cooled down hot water in the end of the main line. BTW my plumbing network is two main (hot and cold) with branch to different faucets (see sketch).

    Like I said earlier I also have slight odor in cold water occasionally (last week I had some, this week nothing).

    Thank you again

    Martin
    Attached Images Attached Images  

  14. #14
    DIY Senior Member mialynette2003's Avatar
    Join Date
    Nov 2010
    Location
    Ocala, Florida
    Posts
    664

    Default

    The odor could be coming from the drain. Try pouring some chlorine down the drain to see if it kills the smell.

  15. #15
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    Otherwise raising the temp of the heater (disinfecting it which ) killed the bacteria and you have flushed out the hot water line to the shower of viable bacteria and hence now no more odor.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

Similar Threads

  1. How to empty water softener? (Kenmore deluxe demand water softener 625)
    By birkoff in forum Water Softener Forum, problems, installation and reviews
    Replies: 1
    Last Post: 01-22-2013, 08:56 PM
  2. Spray vs Air Injector for Aeration
    By Matt Helm in forum Water Softener Forum, problems, installation and reviews
    Replies: 10
    Last Post: 10-06-2011, 06:37 AM
  3. Air Injector question again vs Mazzi Injector
    By K Paterson in forum Water Softener Forum, problems, installation and reviews
    Replies: 9
    Last Post: 02-10-2010, 08:04 AM
  4. Air Injector problem
    By K Paterson in forum Water Softener Forum, problems, installation and reviews
    Replies: 3
    Last Post: 01-03-2010, 04:32 PM
  5. Air Injector Maintenance
    By joejvj in forum Pumps and Tanks Well Forum & Blog
    Replies: 11
    Last Post: 07-07-2009, 04:54 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •